14 gauge in this example might technically meet the ampacity requirement of the Code, but also the voltage drop must be considered. For example, a receptacle that's only 10 ft from the breaker would have very little voltage drop, but a receptacle 150 ft away likely would have excessive voltage drop, in which case the wire size should be increased (say from 12 ga to 10 ga). There are calculators online that will calculate the acceptable voltage drops for different combinations of lengths, current, and wire size.
 
   / welder #12  
I don't have my NEC book right now, but I believe that Article 630 of the NEC allows circuit wiring dedicated for welders to be derated. That is that you can put a 20a breaker on #14 wire and be legal (and safe). The down side to this is that the circuit MUST be dedicated to the welder with NO other outlets on the circuit. The second downside is that you probably will not own the property forever and if the following owner plugs in a 2,400 watt load and burns down the structure, he may coming looking for you with his attorney.

Is it legal? Probably. Would I do it, no.

Article 630 is a mess.
 
   / welder #13  
This may be off subject, but there is a paragraph, Other Possibilities for Power Distribution
This paragraph show how the voltage drops in different segments in the wiring.


Groundloop information pages
 

Tractor & Equipment Auctions

New/Unused Quick Coupler (A57454)
New/Unused Quick...
DEUTZ MARATHON 60KW GENERATOR (A58214)
DEUTZ MARATHON...
2-Row Peanut Inverter (Chain Drive, PTO, 3-Point Hitch) (A56436)
2-Row Peanut...
2014 INTERNATIONAL  DURASTAR 26FT BOX TRUCK (A58017)
2014 INTERNATIONAL...
2007 Reitnouer 40 Ton T/A Heavy Haul Flatbed Trailer (A55973)
2007 Reitnouer 40...
LOT: Clevis Hook, Snatch Block (A59076)
LOT: Clevis Hook...
 
Top