Voltage drop and wire size

/ Voltage drop and wire size #1  

n8586m

Member
Joined
Jan 17, 2008
Messages
45
Location
Stanwood Mi
Tractor
Kubota B2620 w/FEL
While I am just sitting here waiting for spring so that I can empty out my storage building which will allow me to take delivery of the new tractor I have picked out, I have seen several threads asking about wire size to run for added circuits. It appears that there is some confusion on just how to arrive at the correct wire size. Maybe I can shed some light on how to find the right wire size.

We will use the following formula:
This method is a bit more involved that the Ohms Law method, but the big advantage is you can use it for three-phase or single-phase. Here are some additional items to observe:

* Single-phase VD = 2 x K x I x D/CM.
* Three-phase VD = 1.732 x K x I x D/CM. The difference between this and the single phase formula is you replace the 2 with 1.732.
* K = Direct-Current Constant. K represents the dc resistance for a 1,000-circular mils conductor that is 1,000 ft long, at an operating temperature of 75コC. K is 12.9 ohms for copper and 21.2 ohms for aluminum.
* I = Amperes: The load in amperes at 100% (not at 125% for motors or continuous loads).
* D = Distance: The distance the load is from the power supply. When calculating conductor distance, use the length of the conductor溶ot the distance between the equipment connected by the conductor. To arrive at this length, add distance along the raceway route to the amount of wire sticking out at each end. An approximation is good enough. Where we specify distances here, we are referring to the conductor length.
* CM = Circular-Mils: The circular mils of the circuit conductor as listed in NEC Chapter 9, Table 8. I will include some standard sizes later.

Now we all remember 8th grade algebra so we can cross multply the formula and solve for the CM or wire size by picking the voltage drop we can stand for the application, usually not more than 5%.

CM= 2 x K x I x D/VD single phase, CM= 1.732 x K x I x D/VD three phase
(continued)
 
/ Voltage drop and wire size
  • Thread Starter
#2  
Here are some of the most common wire sizes in circular mills (CM):

Wire Cir.Mills
Size
12 6530
10 10380
8 16510
6 26240
4 41740
3 52620
2 66360
1 83690
1/0 105600
2/0 133100
3/0 167800
4/0 211600

Recently someone wanted to know what wire size to run for four lights at a distance of about 300 feet, the total amp load was about 4. So let's do the math. Since he was using 120 volts, let's allow a voltage drop of 5% or 6 volts. The lights will run just fine on 114 volts.

CM= 2 x 12,9 x 4 x 300/6= 5,160 From the table, a #12 wire will be just fine.

If you got any questions, I will try to answer them. Hope this helps.
 
/ Voltage drop and wire size #3  
Actual conductor length is twice the distance from source to load. Im guessing that is accounted for by the "2" and the "3^1/2" for the 2 and 3 phase formulae?
larry
 
/ Voltage drop and wire size #4  
Eeesh. I have a degree in electronics and you guys lost me. Actually I can comprehend it, but it's easier to look in a book.
 
/ Voltage drop and wire size
  • Thread Starter
#5  
SPYDERLK

It's not do to the length out and back but I will have to look into it, the 1.732 is the square root of three which comes from the three phase. I'll get back to you on where the 2 comes from.
Doug
 
/ Voltage drop and wire size
  • Thread Starter
#6  
SPYDERLK

OK, you are correct, it is the hot going out and the neutral coming back. On the three phase it is the the square root of the three hot wires only.
Doug
 
/ Voltage drop and wire size #7  
It really boils down to how much drop is acceptable. Is the person willing to accept a 5% drop or a 6 or more percent drop? NEC suggests a 5% or less drop, and that is a good rule of thumb. I have found that in some cases a drop larger than 5% can produce acceptable results.
 
/ Voltage drop and wire size #8  
So does that mean in your example the 300 should have been 600? (double the length of the distance due to "out and back" wires? That makes a substantial difference in the results.
 
/ Voltage drop and wire size #9  
I attempted to attached a searchable NEC 2002 electrical code book, but it exceeds the file size. Unless you are running your feeders excessive distances or powering sensitive equipment the voltage drop shouldn't be a problem. It would certainly help to get a little back round on what you are doing, like the distance of your feeders and the devices you are delivering power too.
 
/ Voltage drop and wire size
  • Thread Starter
#10  
westbrooklawn

No, the "D" is the one way distance, the "2" in the equation takes care of the "in and out" distance. Note only does the NEC not require a consideration for voltage drop, they don't require a change in wire size because of it. That is somewhat of a surprise as the NEC normally over engineers everything.
Doug
 
/ Voltage drop and wire size #12  
I'm new,
and I have to disagree with "n8586m's" recommended wire size of #12 for a 300' run.

And I'll tell you why,

300' from the house someone is going to need a drill, saw, battery charger or something that draws higher current than those 4 lights, it's just going to be handy there, so Bob (or who ever is you favorite name for these people that takes things on thereselves) sorry Bob) desides to put a recepticle in. Bob always does this.
And Bob is everywhere. May not be today or tomorrow but
it will happen.

Run #10 and give him 4 lights and a recepticle and he will be happy.

Again, sorry Bob
 
/ Voltage drop and wire size #13  
one should also note that some state's requirements are more restrictive towards drop than NEC standards. check your local codes
 
/ Voltage drop and wire size #14  
ray66v said:
It really boils down to how much drop is acceptable. Is the person willing to accept a 5% drop or a 6 or more percent drop? NEC suggests a 5% or less drop, and that is a good rule of thumb. I have found that in some cases a drop larger than 5% can produce acceptable results.

There is actually quite a bit more involved in conductor selection that just voltage drop. Anytime you have a drop you also have heat generated. This raises the temp of both the conductor and insulation. Deponding on the type of insulation and how it is used even a modest voltage drop can overheat a conductor and it's insulation. A conductor in free air behaves quite differently than one in romex, or one in various sizes of conduit, etc.

Andy (an EE who's designed in lot's of conductors)
 
/ Voltage drop and wire size #15  
AndyMA said:
There is actually quite a bit more involved in conductor selection that just voltage drop. Anytime you have a drop you also have heat generated. This raises the temp of both the conductor and insulation. Deponding on the type of insulation and how it is used even a modest voltage drop can overheat a conductor and it's insulation. A conductor in free air behaves quite differently than one in romex, or one in various sizes of conduit, etc.

Andy (an EE who's designed in lot's of conductors)

Yes Andy, I am aware that a drop can reach a point of overheat. And then of course that would be unacceptable.
I believe the fact that the codes allow for some flexibility on these matters is because each situation is different. (Point I was trying to make).
I prefer to do things to a point that I can be confident there will be not problems. However, out here in the country, I have seen things done that I would not do, and they have worked fine.
I wish we could all have the benefit of an EE to evaluate our particular situation. Although, I have found that asking one of the many different engineers I know, a simple question, usually results in an answer that would make a Politician proud.
 
/ Voltage drop and wire size
  • Thread Starter
#16  
If you are going to change the load by adding a receptacle, then you have to re-do the calculations. If you are going to add a 15 amp circuit at the end of the 300 foot run, the circular mill calculation comes out to 19,350 at a 5% voltage drop. No. 8 wire is 16,510 which would be too small, so you would need No. 6, which is 26,240. The point is, you just can't make a guess and hope to be right, you have to do the actual calculations.

The run will probably be under ground either as direct burial or in conduit. In either case, the ambient temperature will not exceed 60 degrees C, so no consideration for insulation other than standard thhn or romex will be required.
 
/ Voltage drop and wire size #17  
n8586m said:
If you are going to change the load by adding a receptacle, then you have to re-do the calculations. If you are going to add a 15 amp circuit at the end of the 300 foot run, the circular mill calculation comes out to 19,350 at a 5% voltage drop. No. 8 wire is 16,510 which would be too small, so you would need No. 6, which is 26,240.

The price difference between the #12 that will work for lighting, from the original calculation. and the #6 that you would need to have the 15 amp receptacle? #6 is approximately 4.5 times as expensive. Multiplied over 300", plus the larger conduit, equals a lot of money. Like around $500 more, better be sure you want that outlet.
 
/ Voltage drop and wire size #18  
What a lot of people don't consider, engineers included, is when determining voltage drop you need to know what the voltage is, under load, at the tap especially when supplying motors.

Don't assume that because you're tapping from your panel box that you're guaranteed 120/240 volts at your starting point. Too many times I have seen a 3000 sq.ft house with a 200 amp service being fed with a 100 ft. drop of #1 aluminum wire from the POCO. The transformer that feeds your house is the starting point.
 
/ Voltage drop and wire size #19  
Also, when supplying a motor that comes from the factory set at 120, convert it to 240 if possible, keeps the voltage drop down and the motor runs cooler. Most well pumps are multi-tapped.
 
 
Top