Surge Protection Install Ques

   / Surge Protection Install Ques #21  
Which rating are you talking about?

- The Nominal Discharge Current (In) – the peak value of current, through the surge protective device (SPD) remains functional after 15 surges.

- The Short Circuit Current Rating - the amount of “available” current that the SPD can be subjected to and safely disconnect from the power source under short circuit conditions.

- something else?

The Generac SPD my standby generator installer installed as a NDC rating of 20kA and a SCCR rating of 200kA.
 
   / Surge Protection Install Ques #22  
Mine is just down stream of the main service entrance breaker, And I believe it is only good for one lightning strike. We had a big strike, and all the circuits were protected, but the surge protector sacrificed itself I think. Had to get a new one.

Meanwhile, the neighbors had damage to their standby generators and their electronic equipment. I guess they didn’t have surge protectors! I suppose I you spellI guess they didn’t have surge protectors! I suppose I should ask them one day.
 
   / Surge Protection Install Ques
  • Thread Starter
#23  
I’m going to go w the F140 and install on the inside of main 200amp panel. Thank you very much for all the suggestions.
 
   / Surge Protection Install Ques #24  
I put my arrestor at the main breaker on the pole
where the power lines are just have the 200 amp
breaker and the arrestor.

willy
 

Tractor & Equipment Auctions

PALLET TOTE OF MISC PARTS (A58374)
PALLET TOTE OF...
2019 CATERPILLAR 326FL EXCAVATOR (A52709)
2019 CATERPILLAR...
2013 FREIGHTLINER CASCADIA (A58214)
2013 FREIGHTLINER...
Poly Bristle Sweep, 78" x 8" (A59076)
Poly Bristle...
2016 FORD F-250 SUPER DUTY (A58214)
2016 FORD F-250...
New Wolverine 78in Skid Steer Land Leveler (A59000)
New Wolverine 78in...
 
Top