Surge Protection Install Ques

   / Surge Protection Install Ques #21  
Which rating are you talking about?

- The Nominal Discharge Current (In) – the peak value of current, through the surge protective device (SPD) remains functional after 15 surges.

- The Short Circuit Current Rating - the amount of “available” current that the SPD can be subjected to and safely disconnect from the power source under short circuit conditions.

- something else?

The Generac SPD my standby generator installer installed as a NDC rating of 20kA and a SCCR rating of 200kA.
 
   / Surge Protection Install Ques #22  
Mine is just down stream of the main service entrance breaker, And I believe it is only good for one lightning strike. We had a big strike, and all the circuits were protected, but the surge protector sacrificed itself I think. Had to get a new one.

Meanwhile, the neighbors had damage to their standby generators and their electronic equipment. I guess they didn’t have surge protectors! I suppose I you spellI guess they didn’t have surge protectors! I suppose I should ask them one day.
 
   / Surge Protection Install Ques
  • Thread Starter
#23  
I’m going to go w the F140 and install on the inside of main 200amp panel. Thank you very much for all the suggestions.
 
   / Surge Protection Install Ques #24  
I put my arrestor at the main breaker on the pole
where the power lines are just have the 200 amp
breaker and the arrestor.

willy
 

Tractor & Equipment Auctions

2013 Cadillac SRX SUV (A53424)
2013 Cadillac SRX...
2025 Swict 84in Bucket Skid Steer Attachment (A53421)
2025 Swict 84in...
Toro Cart Run and Drive (A50324)
Toro Cart Run and...
2013 Ford Fusion SE Sedan (A55853)
2013 Ford Fusion...
Wooden Rocking Chair (A55853)
Wooden Rocking...
66'' root grapple (A53421)
66'' root grapple...
 
Top