Sub panel wiring?

   / Sub panel wiring? #1  

ELMO67

Silver Member
Joined
Jul 23, 2002
Messages
216
Location
CT.
Tractor
KUBOTA L3010
I have just added an attached garage, and now need to add electricity to it. I have a 125 amp subpanel mounted in the basement of the garage, it is approximately 40-45 feet from the main panel. My question is - what size cable do I need to run from panel to panel. I'd prefer to use copper, and does the subpanel need it's own ground cable/ ground rod? I hope this was the correct forum to post this question to ,I apologize if it isn't.
 
   / Sub panel wiring? #2  
Is the garange a detached building or in the same building as the main panel?
 
   / Sub panel wiring? #3  
Attached garage does not need a ground rod, but yes needs a grounding conductor from the main panel. Decide if you want 125A, 100A, 90A....then make your wire selection . (We'll help) /forums/images/graemlins/grin.gif
 
   / Sub panel wiring?
  • Thread Starter
#4  
Thanks for the replies, so far! The garage is attached to the house by way of a 10'x 12' mudroom. The house, mudroom and garage all have basements, which is where the main panel ( house), and subpanel (garage) are located. The subpanel I have mounted in the garage basement is rated at 125 amp capacity; I would like to have that full capacity available. I think that the most I'll be drawing at one time would be 60 amps, but that may not allow for a start up draw.
 
   / Sub panel wiring? #5  
<font color="blue"> (We'll help) </font>

You just did /forums/images/graemlins/smile.gif I have had the ground rod on my to-do list for 5 years. Amazing how time solves problems, thanks
 
   / Sub panel wiring? #6  
For 125A feed to the garage, you’ll need to keep the following in mind.
Assuming all your terminations are rated at 75°C, you can use #2AWG Cu to feed the sub-panel. The #2 is rated at 115A at 75°C, but then you can “round up” to the next standard fuse size, which is 125A.
Run 3-#2Cu, one of them being marked white in some fashion. AND include a #6 bare or green for the grounding conductor.

The above is all based the premise you want to run Copper, sizes must be changed accordingly if you use Aluminum.

Jerry
 
   / Sub panel wiring?
  • Thread Starter
#7  
Thanks for the info, guys, now when I get the wiring done I won't have to keep dragging an extension cord all over the place!
 
   / Sub panel wiring? #8  
Remember to keep the neutral bar isolated from the panel and keep all neutral (white) wires on it and add a ground bar and put all the ground (bare or green) wires on it and bond (connect the ground bar to the metal breaker box
 
   / Sub panel wiring? #9  
BKY-

I was told by an electrical engineer and a electrical inspector that you only use the bonding screw to bond the main box and not the sub box.

Please verify.

Thanks

Yooper Dave
 
   / Sub panel wiring? #10  
yes true ion your main pannel. but in the sub pannel you have to bond the ground bar not the nuteral bar
 

Tractor & Equipment Auctions

Takeuchi Skid Steer (A49461)
Takeuchi Skid...
2015 FREIGHTLINER CASCADIA TANDEM AXLE DAY CAB (A52141)
2015 FREIGHTLINER...
IF YOU BID ON AN ITEM YOU MUST PAY FOR IT!! NO BACKING OUT AFTER IT IS SOLD!! (A50775)
IF YOU BID ON AN...
(4) 20.5R25 13 WHEEL LOADER TIRES & WHEELS (A51244)
(4) 20.5R25 13...
2017 CATERPILLAR 336FL EXCAVATOR (A51242)
2017 CATERPILLAR...
2016 BOBCAT MT55 STAND ON SKID STEER (A51242)
2016 BOBCAT MT55...
 
Top