Sizing bridge beams

/ Sizing bridge beams #41  
You make my point by missing the point...!
You were talking about built up headers and beams...I remarked about the strength of structural plywood etc...and used TJIs as an example...you said they used OSB because it was cheap...That is not the primary reason...the main reason is it is stronger than typical lumber..and much less (thinner) material is required to achieve the same strength...to use regular lumber it would have to be structural grade lumber with very minimal knots etc. (clear) it the strength of plywood etc. that makes it viable...

On beams etc...to add strength to a built up beam using plywood "flitch" members...requires engineered fastening along with effective adhesive...not as strong as a beam with steel flitch plates but significantly stronger than just 2x's nailed together...
That is NOT where the strength comes from.

Again, you can achieve the same strength with a floor "truss", which DOES use dimensional lumber as well as alot of "air" between the top and bottom members.

You can take a 4-ply built up header.......with OSB or plywood in between each of the boards. This header beam will be 7.5" thick...(4 dimensional boards at 1.5" and 3 plys of 1/2" plywood).

You can simply OMIT the 3 plys of plywood and opt for FIVE plys of dimensional lumber instead to have the EXACT SAME 7.5" thick header/beam.

Now in reality the strength will be little to no different. But in terms of engineering and structural calculations......the 5-ply of dimensional lumber will be stronger and rated to carry MORE.

You can harp about the merits of plywood, grain structure, no knots, etc etc all you want. But it doesnt change reality.

You could build your engineered I-joists and use a 1x8 for the web (which is 3/4" thick) or you can use 3/4" thick OSB......
As long as the flanges are the same size and the joist is the same depth.....it wont have an effect on its load carrying stength. Therefore......OSB is no better than dimensional lumber, and is indeed used because it is the cheapest solution.....NOT because it is the strongest.
 
/ Sizing bridge beams #42  
You make my point by missing the point...!
You were talking about built up headers and beams...I remarked about the strength of structural plywood etc...and used TJIs as an example...you said they used OSB because it was cheap...That is not the primary reason...the main reason is it is stronger than typical lumber..and much less (thinner) material is required to achieve the same strength...to use regular lumber it would have to be structural grade lumber with very minimal knots etc. (clear) it the strength of plywood etc. that makes it viable...

On beams etc...to add strength to a built up beam using plywood "flitch" members...requires engineered fastening along with effective adhesive...not as strong as a beam with steel flitch plates but significantly stronger than just 2x's nailed together...
And using structural grade lumber adds to the cost.
 
/ Sizing bridge beams #43  
Not sure what point you are trying to make or argue here anymore?

The discussion was about built up headers and beams. Some people swear sandwiching plywood inbetween makes the beam ALOT stronger, which is false.

Then the "Structual" strength of plywood was called into question....

Now we are talking about OSB and debating about I-joists and where how they get their inherent strength?

Seem to be talking in circles here. Please point out anything I said that was incorrect.

FYI...The plywood/osb web and the adhesive used to secure the bottom member (dado) greatly enhances the tensile strength of the bottom member...this allows lengths of joists (spans) to far surpass solid lumber...like 50++ feet...even considering that the top and bottom member lengths are limited to typical lumber lengths and are finger jointed together to achieve whatever lengths and prevents them from being pulled apart from the tension...


When members I percieve as having a good knowlegde base go back and forth like this is when I learn the most.
Thank you,
Dean
 
/ Sizing bridge beams #44  
That is NOT where the strength comes from.

Again, you can achieve the same strength with a floor "truss", which DOES use dimensional lumber as well as alot of "air" between the top and bottom members.

You can take a 4-ply built up header.......with OSB or plywood in between each of the boards. This header beam will be 7.5" thick...(4 dimensional boards at 1.5" and 3 plys of 1/2" plywood).

You can simply OMIT the 3 plys of plywood and opt for FIVE plys of dimensional lumber instead to have the EXACT SAME 7.5" thick header/beam.

Now in reality the strength will be little to no different. But in terms of engineering and structural calculations......the 5-ply of dimensional lumber will be stronger and rated to carry MORE.

You can harp about the merits of plywood, grain structure, no knots, etc etc all you want. But it doesnt change reality.

You could build your engineered I-joists and use a 1x8 for the web (which is 3/4" thick) or you can use 3/4" thick OSB......
As long as the flanges are the same size and the joist is the same depth.....it wont have an effect on its load carrying stength. Therefore......OSB is no better than dimensional lumber, and is indeed used because it is the cheapest solution.....NOT because it is the strongest.
You are making assumptions making believe it's "reality"...It ain't...geeze...!
LoL...FYI they use plywood or OSB because it's strength allows a much thinner piece of material which is lighter (and cheaper) to be used...many engineered joist employ only 1/2" ply...

Also if you take any typical building lumber say a 2x10 and then take two pieces of 3/4" structural grade plywood and laminate them together (so they are the same dimension as the 2x10)...and do structural tests on the two members the laminated plywood one would far surpass the solid lumber one...on everything but being able to make toothpicks from what was left after the testing...!
 
/ Sizing bridge beams #45  

🍿🍿🍿🍿


I decree, Pine wins, build the bridge out of plywood. Wait, this thread is about a bridge, right?
 
/ Sizing bridge beams #46  
I NEVER said its just like air.

OSB is used in i-joists because its cheaper than dimensional lumber. Not because it increases the strength.

A typical 10" I-joist would have a ~7" piece of osb for the web and a 2x3 or a 2x4 for both top and bottom members.

If you replaced that piece of OSB with a dimensional board......1x8 or 2x8.....and still had the 2x3 or 2x4 on top and bottom.....it would be just as strong if not stronger.

The OSB's only job is to keep the top and bottom members separated. Beyond that it isnt adding strength. Hence the analogy of floor trusses. Rather than a piece of OSB to keep the top and bottom members separate.....they use webbing. (mostly air aside from webbing). AS long as the webbing is strong enough to keep the top and bottom members separated....thats all it needs to do because the strength is in the flanges.

The reason the I-joists are stronger than a dimensional board of the same depth is NOT......NOT......because of the OSB/plywood. It is because it concentrates mass at the edges where compression and tension happens

You can take a steel I-beam and make the web thicker and it does little to add to the strength of the beam. Add mass to the flanges though....and the beam becomes MUCH MUCH stronger.

So you obviously think that the compressive forces at the top of a joist and the tension at the bottom of said joist only exist in the depth of the top and bottom members i.e., 1-1/2 inches (at the top and bottom) since you say that the plywood or OSB isn't adding strength and is only there to keep the top and bottom members separated...

And basically what you're saying is that with a solid member (2x10 etc) joist or beam...as long as you leave that 1-1/2" of material at the top and bottom you can drill as many and as big of holes as you want...NOT...!
 
/ Sizing bridge beams #47  
Yes well not sure of as many as you want, but that's pretty much what I learn in structural ... a downward load on a 4x8 beam will result in the bottom two inch's take care of the tension (minus force) the top two inch's take care of compression (positive force) the rest of the beam body is only there so the two doesn't separate basically taken no load it is neutral force... so you can remove it all and replace it with anything capable of doing only that, keeping together the two side in place, that's where the I shape beam come from ...
 
  • Good Post
Reactions: LD1
/ Sizing bridge beams #48  
Yes well not sure of as many as you want, but that's pretty much what I learn in structural ... a downward load on a 4x8 beam will result in the bottom two inch's take care of the tension (minus force) the top two inch's take care of compression (positive force) the rest of the beam body is only there so the two doesn't separate basically taken no load it is neutral force... so you can remove it all and replace it with anything capable of doing only that, keeping together the two side in place, that's where the I shape beam come from ...
The compressive and tensile forces are not constant along the tops and bottoms especially the bottoms near the bearing points...the top depends on the design live load...
 
/ Sizing bridge beams #49  
Keep in mind going beyond theory, the beam wants to maybe twist and also bend sideways. The web helps with this.
 
/ Sizing bridge beams #50  
The compressive and tensile forces are not constant along the tops and bottoms especially the bottoms near the bearing points...the top depends on the design live load...
mmm, action reaction... the only time the forces from the top vs the bottom would be different in a cross-sectional slice of a beam is the result of a failure of the beam. yes the load varies along the beam, but the forces would be equal in each cross-section.
 
/ Sizing bridge beams #51  
mmm, action reaction... the only time the forces from the top vs the bottom would be different in a cross-sectional slice of a beam is the result of a failure of the beam. yes the load varies along the beam, but the forces would be equal in each cross-section.
You're saying the forces are the same at the center of the span as they are say at 25% from a bearing point??
 
/ Sizing bridge beams #52  
You're saying the forces are the same at the center of the span as they are say at 25% from a bearing point??

Rockbadchild said:
mmm, action reaction... the only time the forces from the top vs the bottom would be different in a cross-sectional slice of a beam is the result of a failure of the beam. yes the load varies along the beam, but the forces would be equal in each cross-section.


no you miss understood me .. I know you know this it's just a communication issue and with LDI it's a technicality issue... as far as calculation goes I know he is right but practically I would be curious to see it... and I think we have the same opinion in that regard ...

I am saying that the compressive and tensile forces are always the same in each cross-section slice of the beam... action = reaction ... but yes these forces do change as you go along the beam but in each cross-section if you have a +5 compressive force on top as a result you will have a -5 tensile force as a result at the bottom.
 
/ Sizing bridge beams #53  
Rockbadchild said:
mmm, action reaction... the only time the forces from the top vs the bottom would be different in a cross-sectional slice of a beam is the result of a failure of the beam. yes the load varies along the beam, but the forces would be equal in each cross-section.


no you miss understood me .. I know you know this it's just a communication issue and with LDI it's a technicality issue... as far as calculation goes I know he is right but practically I would be curious to see it... and I think we have the same opinion in that regard ...

I am saying that the compressive and tensile forces are always the same in each cross-section slice of the beam... action = reaction ... but yes these forces do change as you go along the beam but in each cross-section if you have a +5 compressive force on top as a result you will have a -5 tensile force as a result at the bottom.
Yes I see now what you were saying...cross sections but it's not germane to the point I was making...and BTW...LD1 is wrong about a few things...
 
/ Sizing bridge beams #54  
Yes I see now what you were saying...cross sections but it's not germane to the point I was making...and BTW...LD1 is wrong about a few things...
Please enlighten us.
 
/ Sizing bridge beams #55  
And basically what you're saying is that with a solid member (2x10 etc) joist or beam...as long as you leave that 1-1/2" of material at the top and bottom you can drill as many and as big of holes as you want...NOT...!
You mean similar to this?
truss.JPG
 
/ Sizing bridge beams #56  
You are making assumptions making believe it's "reality"...It ain't...geeze...!
LoL...FYI they use plywood or OSB because it's strength allows a much thinner piece of material which is lighter (and cheaper) to be used...many engineered joist employ only 1/2" ply...

Also if you take any typical building lumber say a 2x10 and then take two pieces of 3/4" structural grade plywood and laminate them together (so they are the same dimension as the 2x10)...and do structural tests on the two members the laminated plywood one would far surpass the solid lumber one...on everything but being able to make toothpicks from what was left after the testing...!
What assumptions am I making?

You seem hell-bent to think that OSB or plywood is some super strong material.

When used correctly, like in I-joists, YES it can make a strong member. But you think too highly of the OSB and what it does. Again, it keeps the flanges separated. Same thing can be accomplished with webbing forming a truss and the use of NO osb or plywood.

But this post is about using a built-up beam/header for a given span.

I challenge you to find me an engineering spec, or span table, or calculation that shows a built up beam with plywood sandwiched is rated higher than the same width out of dimensional lumber only. IE: my earlier example of 4 2x boards with 3 pieces of 1/2" plywood sandwiched vs just using an extra 2x dimensional board in lieu of the 1-1/2" worth of plywood.
 
/ Sizing bridge beams #57  
You mean similar to this?
View attachment 778878
That is an engineered floor truss...where the web members are structural and are charged with distributing the load...
They offer a more rugged floor but are heavy and expensive...

Again...it is the strength of plywood or OSB that makes I-joists a light, viable alternative...otherwise they could use something like luan...LoL
 
/ Sizing bridge beams #58  
What assumptions am I making?

You seem hell-bent to think that OSB or plywood is some super strong material.

When used correctly, like in I-joists, YES it can make a strong member. But you think too highly of the OSB and what it does. Again, it keeps the flanges separated. Same thing can be accomplished with webbing forming a truss and the use of NO osb or plywood.

But this post is about using a built-up beam/header for a given span.

I challenge you to find me an engineering spec, or span table, or calculation that shows a built up beam with plywood sandwiched is rated higher than the same width out of dimensional lumber only. IE: my earlier example of 4 2x boards with 3 pieces of 1/2" plywood sandwiched vs just using an extra 2x dimensional board in lieu of the 1-1/2" worth of plywood.
Find your own proof...you are the one making assumptions...
A TJI is at least 20% stronger than a solid lumber joist... with way less mass...you do the math...
 
/ Sizing bridge beams #59  
Find your own proof...you are the one making assumptions...
A TJI is at least 20% stronger than a solid lumber joist... with way less mass...you do the math...
There is no "finding my own proof".

Because it doesn't exist.

YOU are the one that believes plywood is stronger. I'm simply asking you to show proof.

Saying an I-joist is stronger than a dimensional board is indeed factual. Because the strength isn't because plywood is used for the web and you are changing the structural shape vs comparing apples to apples is size.

Furthermore, I gave you an example of achieving the same or greater strength WITHOUT plywood but via floor trusses.

And you have yet to cite anything I said that is inaccurate.....yet you make the claim in an attempt to discredit what I have said
 
/ Sizing bridge beams
  • Thread Starter
#60  
Steel it is! I will check out the scrap yards to see what is available.
Next I will try to locate an area of the creek that is narrowest. Keeping my footers/concrete blocks 2' from the bank, I am going to end up with a 11' - 14' span.

Is there a good online calc for "point loads" of the different sizes of steel beams?
 

Marketplace Items

2020 JOHN DEERE 770G MOTORGRADER (A63276)
2020 JOHN DEERE...
500 BBL FRAC TANK (A58214)
500 BBL FRAC TANK...
2016 Chevrolet Silverado 1500 Pickup Truck (A64194)
2016 Chevrolet...
Meyer 8' Snow Plow w/ Bracket (A55272)
Meyer 8' Snow Plow...
2014 International DuraStar 4300 S/A Dump Truck (A61573)
2014 International...
*Selling at Royal Auction Tampa, FL Location* (A59228)
*Selling at Royal...
 
Top