I thought I'd turn to this site for some sensible feedback. I build an ICF House in 2012-2013, I acted as the General Contractor and thought I had everything covered but recently started noticing some flex in my Aquatic Shower Enclosure not to mention the old water spot in the ceiling last night? It appears the water is going under the Drain Assembly's lip that screws down on the surface of the enclosure as I stand on the base and it flexes downward creating a gap for water to escape. Discovery - Plumber did not install any "Foundation Material" when setting the unit as required in the Aquatic Install Instructions and as verified when I removed the base trim from the adjoining wall and cut the drywall inspect, thank goodness my base trim is 7-1/2 inch high and the cuts are hidden. Because of access limitations I'm searching for a solution.

Reading the Jacuzzi Bonaire Shower Stall Installation Instructions: "Materials that may be used are a floor leveling compound, mortar, plaster or minimal expansion structural foam having a density of a minimum of 5 lbs./cubic feet. I would like to pursue the use of foam if possible. Also, I found a Foam Dispensing Gun on the HDepot Site with a 23 inch long tip giving me a good reach. I'm looking for a brand of low expansion foam that meets the Jacuzzi Specs for hardness/structural support. Blogs also recommend placing plastic backs under the unit then filling with the foam so it doesn't stick to the sub-floor or shower enclosure just in case the enclosure is removed in the future and future noice considerations. A Big Warning/Red Flag , many Blogs indicate unless the right foam is used it will breakdown and compress over time resulting in voids, movement, and full-circle I go. As another thought I also read lots of people recommend USG's product called Structo-Lite as a Foundation Material but I don't know if I could use some type of mechanical a pump with a small hose to get it in there, we're talking a 2 inch void. Any Technical Recommendations/Suggestions would be appreciated.
 
Last edited:
/ Shower Enclosure - No Supporting "Foundation Material" #2  
Sounds like a good diagnosis.

Another material to consider is blocks of high density foam like that used for blocking heavy stuff for shipment. Maybe you could find some of that and manage to stuff it in around the drain.

Or, there is this: FOAMULAR® 1000 High Compressive Strength Rigid Foam Insulation

2" thick foam sheets for load bearing applications.

After you get some support around the drain, some plumber's putty between the tub and the drain flange should help too.
 
/ Shower Enclosure - No Supporting "Foundation Material" #3  
As an observation, I installed a Jacuzzi tub in our last house that required the plaster bed for support. It was a large two-person tub with a good bit of slant in the bottom, plus I wanted a finished height for the tub taller than the tub depth. What a project. I built a plywood ramp that would leave ~2" of bedding space between the ramp and the tub bottom, mixed the plaster, spread it, seated the tub in the plaster, etc.

It worked fine but there are tub brands that come with integrated bottom support that make all that bed building unnecessary. I would look for that if I had to do it again.
 
/ Shower Enclosure - No Supporting "Foundation Material"
  • Thread Starter
#4  
UPDATE from DOW, not sure what this means, I'll have to investigate how it's applied but for others encountering this situation here's what they said:

"GREAT STUFF™ sealants use moisture in the air to cure. They are designed to fill small cracks and gaps. The foam does not cure properly if it is used to fill large voids unless it is put down in layers and allowed to cure before the next layer is applied. Do not use GREAT STUFF™ sealants to fill enclosed voids such as behind drywall or under tub surrounds. Instead of using GREAT STUFF™, consider using Dow FROTH-PAK™ Class A polyurethane foam insulating system in cavity applications.

FROTH-PAK™ is commonly used in this application to fill a void under a pool or spa to stop flexing, provide structural support, insulate and reduce vibration. However, installers should be aware that the foam will expand 3 to 5 times and will exert a lot of pressure on the pool or spa. Use a brace to secure the pool/spa or fill the pool/spa with water to add weight to keep the pool/spa in place when foaming. It is always recommended to check with the local building code official to confirm the use of FROTH-PAK™ in these applications.
 
/ Shower Enclosure - No Supporting "Foundation Material"
  • Thread Starter
#5  
It worked fine but there are tub brands that come with integrated bottom support that make all that bed building unnecessary. I would look for that if I had to do it again.

dave1949, Thanks for your thoughts, I only wish I had the access to do what you suggest without doing a complete demo however, drywall and trim up and finished and Dreamline Glass Doors installed. I'll have to go in from the side, hopefully with a Foam Dispensing Gun, Dow says their Great stuff Pro Gun 14 has the option of 26 1/2 inch barrel length. That has now been replaced with the option of a 40 inch barrel. Thats good news for me if I can find the right foam to use.
 
/ Shower Enclosure - No Supporting "Foundation Material" #6  
As an observation, I installed a Jacuzzi tub in our last house that required the plaster bed for support. It was a large two-person tub with a good bit of slant in the bottom, plus I wanted a finished height for the tub taller than the tub depth. What a project. I built a plywood ramp that would leave ~2" of bedding space between the ramp and the tub bottom, mixed the plaster, spread it, seated the tub in the plaster, etc.

It worked fine but there are tub brands that come with integrated bottom support that make all that bed building unnecessary. I would look for that if I had to do it again.

I built a housein1973, lived in it 27 years and now son lives in it so I have had a chance to see how some of my bright ideas worked out. On the tub I had been observing flex in the shower floors when visiting friends living in new homes. I grew up bathing and showering in a cast iron tub. The movement just made things feel cheap. Also I was inexperienced builder, just winging it. Pressed for time to get things done and move on to next task, I did what Dave 1949 did. I mixed some buckets of concrete and poured it in a frame made from scrap wood pieces and set the shower unit in, careful to not press down on any one area in the bottom but gentle pressure while wiggling and satisfied my self that the bottom had not been flexed upward anywhere, cleared the drain and supply line access area, nailed the unit to the walls and wondered how this was all going to turn out. I worried that there would be a crunchy feeling stepping into the shower as it aged, perhaps cracking and popping, and maybe even stress crack due incompatibility of thermal expansion rates. In fact, it has always been perfect. Just visited with my son this past weekend and the shower unit is as solid as could possibly be, that's 41 years of heavy use.

BTW the instructions with the shower unit said it was self supporting and that warranty was void if it was set on anything other than a flat solid surface. I laughed at the idea of a worthwhile warranty action and proceed to do what made sense to me knowing that some times I learn an expensive lesson. This one still brings a smile every time I use it because all the builders were telling me it was a waste of time, they did nothing but nail it in.
 
/ Shower Enclosure - No Supporting "Foundation Material" #7  
It sounds as the mfr. wanted the shower pan to be "mud set". I usually mud set mine, even when they don't require it. Basically I mix a couple of bag of mason mortar and throw it on the floor. Pile the mortar high so the shower pan displaces it. Set the pan and tap it into position while leveling it. You can not pull the shower back up, so keep working it down without going too far.

It sounds like you can see the bottom of the shower through the drain hole in the sheathing. A closed cell expanding foam (Great Stuff) might be a good option for you. You could try the max expansion, but don't get too crazy or you could lift the pan. I've used a rubber hose in the past to extend the nozzle for those hard to reach places. Waiting a day between layers will help you control the pressure of the expanding foam. If you can't wait, a exceedingly light mist of water to ensure sufficient moisture to cure.

The Frothpak stuff is very difficult to find and obscenely expensive. See if you have a ABC supply nearby, they'll sell to you if you don't have an account.
 
/ Shower Enclosure - No Supporting "Foundation Material" #8  
I was hoping you had enough clearance from the end or side to slide some material in.

If you use the spray foam, maybe you could disassemble the drain itself, leaving the drain pipe in place. Block the opening in the pipe, then spray the foam around the pipe. The hole in the pan is probably bigger than the drain pipe outside diameter. Maybe enough to get spray wand in there. Not a total solution but it could help get the foam into the area.

You can trim out any foam that expands into the drain hole. I would tape down a plastic cover inside the floor pan first in case the foam bonds to the pan floor.
 
/ Shower Enclosure - No Supporting "Foundation Material"
  • Thread Starter
#9  
Found the FROTH PAK on-line, their #12 Kit (12 cubit feet coverage) runs about $40.00. As DOW's Technical Support Email to me indicated, ANY Great Stuff Products, regardless if it the "PRO" Series or not, cannot be used, it is not designed to handle any structural weight and will eventually break-down as the base flexes "CRUNCH". I have to laugh though, you look on-line and everyone recommends their "Big Crack" Blue Can Foam...those who go that route are in trouble. I did contact Jacuzzi's Techncial Support Team, they will not recommend any brand meeting thier specs and simply re-state it must have a minimum density of 5 lbs./cubic feet, a circular conversation for sure.......... To re-cap, a good 3/4 subfloor under the shower enclosure, properly framed as per rough-in, hole for plumbing A-OK.......Everthing done perfectly except no Foundation Material as the unit was set. As the General contractor you can't be in all places at once so that was missed although stated to follow all mrf instructions, they were even taped to the unit but that's spilled milk and I'm not going to tear the unit out and so the search for a solution. Becasue the unit is totally enclosed and finished-off (installed in 2012) I removed the base trin from an outside wall, cut the drywall up 6 inches between the studs, I can see the gap along the bottom of the enclosure......... Turns-out the FROTH PAK will probably not work, although it has a good pressure stream there are no extension available for the nozzel to allow me to stick it in say 24 inches and shoot small batches.... Onward and Forward as they say..........
 
/ Shower Enclosure - No Supporting "Foundation Material" #10  
I have one more idea. Not a great one, but ...

Can you work on it from the bottom? It would be less cost and overall disruption if you could take down the (sheet-rock)? ceiling below the shower. Drill foam shooting access holes in the sub-floor (carefully to avoid hitting the shower pan), spray the foam in, repair the ceiling.
 
/ Shower Enclosure - No Supporting "Foundation Material" #11  
I thought I'd turn to this site for some sensible feedback. I build an ICF House in 2012-2013, I acted as the General Contractor and thought I had everything covered but recently started noticing some flex in my Aquatic Shower Enclosure not to mention the old water spot in the ceiling last night? It appears the water is going under the Drain Assembly's lip that screws down on the surface of the enclosure as I stand on the base and it flexes downward creating a gap for water to escape. Discovery - Plumber did not install any "Foundation Material" when setting the unit as required in the Aquatic Install Instructions and as verified when I removed the base trim from the adjoining wall and cut the drywall inspect, thank goodness my base trim is 7-1/2 inch high and the cuts are hidden. Because of access limitations I'm searching for a solution.

Before you go spraying foam or putting anything at all under the unit. 1st Your shower floor and brass drain should not be separating when you step on the floor and it flexes. I am not sure if you know how the drain assembly works but. You apply a nice amount of plumbers putty around the top lip of the brass drain slide it into hole and then slide up your rubber washer and then a friction washer followed by the large brass nut from underneath. Keep cranking down until you get a nice seal and the top ring is set nice against the shower pan most of the plumbers putty will have come out. wait a few and tighten the nut some more. Your 2" pipe slides inside the brass drain just past the top of the black rubber washer and you tighten down the nut from the top side using the tool provided with the drain.

Ok now with that being said. and the reason i said all that is you should have no separation from the shower floor and your drain lip even with flex. If you do have flex i would suspect that your drain was not properly tighten to the shower pan. It is very hard to get separation even with flexing of the floor. most times your pipe at the trap will flex first. So please do yourself a favor before you really make it a nightmare to work on. Some how verify your drain assembly is tight . Once you put that foam or what ever you use in your done no more room to work. I hope you get it to work right with out having to take out the shower unit. At least now you know what plumber NOT to call for when you need future work done. Good luck with your project.
 
/ Shower Enclosure - No Supporting "Foundation Material"
  • Thread Starter
#12  
Dave1949, I have full access under the One Piece Fiberglass Shower Enclosure going in from the side. The real issue is finding a suitable foam having a density of a minimum of 5 lbs./cubic feet. The FROTH PAK meets what I'm looking for, I've sent their technical group another question: "Can I tape a 2 foot length of 1/2 pex to the nozzle so I can get a more controlled flow or will it set-up before it reaches the end/opening". I'd attach the pex (one time use) to a doubled-up 16" X 16" zip lock freezer bag and slowly fill it up. Froth Pak expands 3X to 5X so steady as she goes would be the process. Once filled and hardened I'd pull the pex hose out. I'd have (4) of the Pex/Hose set-ups all ready before starting. The drain is approx 18 inches from the side = 36" wide. All I need to do is place 4 bags around the drain, forming a square, to add support. The bags would prevent it from sticking to the subfloor or to the underside of the enclosure in case it has to be removed in the future.
 
/ Shower Enclosure - No Supporting "Foundation Material"
  • Thread Starter
#13  
BuilderML,

Glad you wrote, my Plumber just left and essentially did what you suggested, step-by-step, almost like he was following your post. His first comment; "drain was not properly tighten to the shower pan". So he pulled it out, cleaned it up and really torqued-it-on tight. He said there was so much movement the lip started to create a wear mark on the shower pan. While we was first inspecting the movement he said he'd never seen a pan move with the slightest touch. It's an Aquatic Shower Enclosure, he said I reallt still needed to get something under the unit for support regardless so I'll continue but the lose drain assembly has been fixed.
 
/ Shower Enclosure - No Supporting "Foundation Material" #14  
It's messy, but I always just mix half a sack of readi mix concrete and shove it under as far as I can, then use the end of a 2x6 to force it all in even farther. There gets to a point when you can't put any more under there.

Eddie
 
/ Shower Enclosure - No Supporting "Foundation Material" #15  
It's messy, but I always just mix half a sack of readi mix concrete and shove it under as far as I can, then use the end of a 2x6 to force it all in even farther. There gets to a point when you can't put any more under there.

Eddie

I agree with Eddy, you can also use lightweight drywall topping compound or even duro-rock 90 mixed somewhat dry and done as Eddy said. We did a LOT of homes drywall & often would have a few bags of 90 mixed with plus-3 to have something lighter in weight poured under them. That can be done using a drywall pump & hose...

Mark
 
/ Shower Enclosure - No Supporting "Foundation Material" #16  
BuilderML,

Glad you wrote, my Plumber just left and essentially did what you suggested, step-by-step, almost like he was following your post. His first comment; "drain was not properly tighten to the shower pan". So he pulled it out, cleaned it up and really torqued-it-on tight. He said there was so much movement the lip started to create a wear mark on the shower pan. While we was first inspecting the movement he said he'd never seen a pan move with the slightest touch. It's an Aquatic Shower Enclosure, he said I really still needed to get something under the unit for support regardless so I'll continue but the lose drain assembly has been fixed.

I am glad he was able to get it to work for you without having to take the shower pan out.:thumbsup: As far what to place underneath to support the base. Make sure what ever you place under you use caution while packing or setting in place. You do not want your floor to flex up if your forcing cement under with a 2x This will most likely create a soft spot in the pan floor. Remember you are just looking to support the floor not rebuild it from under with cement. Have fun.
 
/ Shower Enclosure - No Supporting "Foundation Material"
  • Thread Starter
#17  
EddieWalker, Thought you'd join-in on this post. Yes, your recommendation is looking more along the line of what I will do, after weighing the risk/reward the Foam Adventure is way too risky for my blood because of the uncontrolled expansion. For sure I need something that won't shrink or breakdown over time, not sure if it has to flex a bit. Many recommend USG's product called Structo-Lite, do you know of that product. The subs I've spoken with always cover the Foundation Material in plastic before setting the units, should I try to stuff/pack the mixture in a plastic bag to prevent sticking and future noise.

SPIKER, I'm not familiar with duro-rock 90, I've used Durabond 90, is that what you meant. I see SHEETROCK makes the Plus 3 Product, so you mixed them together to create your Foundation Material. Do you remember the mixture %

MLBuilder, Your insight on the loose Drain Assembly really hit the mark and your words of caution pretty much sums-up my concern about using foam, with my luck the foam would not spread evenly as it expanded upward under the pan and therefore causing heaving and unevenness and then I'm in big trouble, the Drain Assembly would never seal.... As suggested my EddieWalker and SPIKER, I'll go a more conventional route with a mixed mortar and physically shove it in there.

In Summary I need to ensure its non-shrinking, won't breakdown but I could use some guidance if it needs to have some flex. The last issue; "The Plastic Bag Approach". Should I attempt to shove it into a bag placed underneath the unit so the mix doesn't physically stick to the subfloor and bottom of the enclosure. That thought has been carried along ever since reading blogs about the possibility of future noise..... One good thing in all this, getting the real story out about using Foams to support Tubs, Shower Enclosures and Shower Pan. Dow's Technical Department really set the record straight with candid feedback of their: "Great Stuff Foam" Product Line and their more Commercial FROTH PAK Kits.
 
Last edited:
/ Shower Enclosure - No Supporting "Foundation Material" #18  
I've found that when setting fiberglass tubs and showers, that in order to get the drain on, you need to be able to move the tub or shower around a little bit. It's a bear getting everything lined up and then secure. Then you attaché the tub or shower to the studs. The newer ones come with tabs that you screw through that go over the edge of the lip. I've used fender washers for years and like them a lot for the same purpose.

With your situation, the shower is already mounted and hopefully secure. It's not going anywhere, so whatever you use should be there to provide a solid base to support the weight of anybody in the shower. If it flexes, the drain will probably come loose again over time. Worse case scenario is if there is too much flex, you might get a crack somewhere.

Concrete is easy to work with and dries very solid. Mix it as dry as you can so you can push it with the end of the board. You don't want it to be soupy, but you want it wet enough so that it will fill all the voids and create a solid base from the floor to the underside of the pan.

Eddie
 

Marketplace Items

UNUSED INDUSTRIAS AMERICA F08T-8' LAND LEVELER (A62130)
UNUSED INDUSTRIAS...
Hydraulic Breaker Excavator Attachment (A61567)
Hydraulic Breaker...
2020 VERMEER LP873SD1 VAC-TRON VACUUM TRAILER (A63276)
2020 VERMEER...
(APPROX. 35) DIAMOND PLATE DBL AXLE FENDERS (A62131)
(APPROX. 35)...
2012 Peterbilt 386 T/A Day Cab Truck Tractor (A60352)
2012 Peterbilt 386...
New/Unused Quick Attach Auger with 2 Bits (A61166)
New/Unused Quick...
 
Top