Pole barn condensation

/ Pole barn condensation #1  

karman 4564

Member
Joined
Jun 20, 2007
Messages
39
Location
Northwest pa,
Tractor
johndeere
The contractor starts next week on my new 40x80 pole building,after reading several pole barn build stories i have a concern about condensation,What can or should I do to prevent this from happening,
 
/ Pole barn condensation #2  
Install fans
 
/ Pole barn condensation #3  
Large louvered, screened opening at the peak, on each end - fan on each end. There are web sites that will give fairly specific specs on size of opening and rating for fan(s).
 
/ Pole barn condensation
  • Thread Starter
#4  
Thank you for the quick reply's,
Does it make a difference if the building is insulated and finished on the inside
 
/ Pole barn condensation #5  
40 x 80 is a great size...

We want pictures!
 
/ Pole barn condensation #6  
Thank you for the quick reply's,
Does it make a difference if the building is insulated and finished on the inside

Yes. If you have the ceiling well insulated (at the bottom of the rafters) along with good ventilation for the attic space you should be fine. The condensation comes from when you have the inside of the roof a different temp than the outside.

So if you heated the inside and the underside of the roof was getting that heat while cold outside, you'd have a problem. Reverse in the summer.
 
/ Pole barn condensation #7  
Thank you for the quick reply's,
Does it make a difference if the building is insulated and finished on the inside

Understand condensation and dew point. It will happen- no matter what- it’s science. The thing you want to control is where it’s occurring in the wall.
The fans work because they are bringing the inside and outside temps in alignment or close enough to prevent the condensation.
So if you are doing interior walls and insulation up against the steel siding you could be trapping the moisture in the wall structure (between Sheetrock and metal). Check out something like building science .com. They have the details (drawings) and the studies of ways to prevent moisture/mold issues. We typically just frame the interior walls and hold the batt insulation an inch plus off the steel siding. That HOPEFULLY puts the condensation in an area that can dissipate the moisture.
 
/ Pole barn condensation #8  
If the interior space is to be heated insulation is only part of the equation. You have to keep interior moisture from going through the insulation and condensing on the exterior skin. Vapor barrier is what that is called. It virtually has to be airtight. Like Neumann stated, that is the means of draining that moisture. hat has it own set of problems like corrosion and mold growing. Then again folks tend to get by with things in spite of the science. Usually its pay me now or pay me later (with inflated $). I have seen many steel buildings where the roof insulation is saturated with water and falling down from the weight.

Ron
 
/ Pole barn condensation #9  
Air has a dew point. That is the temperature at which it can no longer hold all the water vapor that it contains. If the air comes in contact with a surface that is colder than the dewpoint of the air then it will condense on that surface, just like on the side of your beer can.

Objects radiate heat from their surfaces. I radiate my heat towards you and you radiate heat towards me and since we are similar in temperature there is no heat loss to each other. The roof of your barn radiates heat towards space. Space has no heat to radiate back towards your barn. This is called radiant over-cooling.

The roof of your barn on a cloudless night will radiate so much heat towards space that it will cool to as much as 10 degrees f below the temperature of the air. This is why frost forms on the roof when the air temperature is still above freezing.

When you insulate the roof, it will become colder because it no longer gains radiant heat from the ground below it. If the insulation allows the air from below to freely come in contact with the underside of the metal roof, then a significant amount of moisture can collect rather quickly, just like on your beer can.

You can limit the amount of water vapor that comes in contact with the cold surface by using a vapor retarder on the underside of the insulation but you must also limit air movement through the assembly.

The concepts are simple. The solutions can be tricky. The conditions, climate and materials all affect the approach that is effective.

I will add just a few interesting things to consider in helping to understand the concept. Notice that the roof of your car(parked out in the open) will be wet with dew but the sides are dry. This is because the sides are facing other heat radiating objects and the roof is facing space. Cloud cover reduces the radiant heat loss from the roof and ground by re-radiating heat back to the ground. The clouds overhead are cold but not "deep space" cold. Dew doesn't fall, it forms on cold surfaces.

One other odd thing to know. Humid air rises. It is less dense and more buoyant than dry air. This explains part of why airplanes have a harder time taking off in high humid conditions. The reason is that air at a given pressure and temperature only contains a set number of molecules and water vapor is made up of oxygen and hydrogen which are lighter than the oxygen and nitrogen that make up air. The more hydrogen molecules are added to the volume of air, the fewer nitrogen molecules are in that volume. Humid air rises until it reaches a level in the atmosphere where it can no longer hold all the water vapor and at that point it condenses out to form clouds. In a still air building, condensation will tend to occur at the peak of the roof first which is why ridge vents are important in a vented roof system.

Roof ventilation is not the only or even the best way to manage moisture but it is one way. There is no cheap and easy way to do a great job of handling moisture in a metal building. There are cheap ways that may be better than nothing. They may work ok or fail miserably depending on your climate and conditions.

Aren't I just mr. Happy?
 
/ Pole barn condensation #10  
On the walls can you use Tyvek between the metal and purl ins? Or should it go between the posts and purlins?

Starting a 42x72 tomorrow. The first 24x42 will be insulated with a mini split. The ceiling will be metal with r30. The bottom of the walls, interior, will be 3/4" plywood 8 foot up with 5' metal on top of that to ceiling. Should I put a vapor barrier between metal ceiling and insulation?
 
/ Pole barn condensation
  • Thread Starter
#11  
Thanks everyone,
From what I learned from all of you was,I should make sure the contractor installs tyvec on the outside walls prior to the steel going on to act as a vapor barrier and install ceiling fans,
I like he idea of vents at each end of the building and will look into that.
Here's what I plan to do...install insulation covered by 1/2 " osb,on the walls.white steel on the ceiling with blown in insulation in the ceiling.
Will this alleviate any condensation,

I got inspiration and ideas from all the threads I've read about post barn builds and I plan to post pictures,
 
/ Pole barn condensation #12  
Tyvek (spun polyolefin) is not a vapor barrier. It is designed as a drainage plane that allows vapor to pass freely through it. It has a perm rating depending on which version or manufacturer that varies between 7 and 60 perms. It resists liquid water if it is properly installed but it almost never is.

Fiberglass insulation allows water vapor to pass freely through it and also suffers from movement of air through it. It will allow convective loops to form within a wall that can carry large amounts of water vapor through it where it will collect on any cool surfaces that it finds. I have seen dramatic failures caused by this phenomenon but it will not be your problem. Your problem will be allowing water vapor to pass straight through your assembly and collect on the underside of the roof structure.

The second biggest problem you will encounter is related to the steel framing members. Steel passes heat easily through it and not only will you suffer thermal losses that create comfort and cooling and heating cost issues, you will also have moisture collect in certain climate conditions when the steel is cold in winter months.

Unfortunately, these issues are too complex to teach as an aside in a discussion forum related to other topics such as pole barns and tractors. There are discussion forums related to building science where these issues are discussed and understood. I'm sorry if my ability to convey the issues is inadequate. It is very important to me as I hate to see building failures and it happens all around me. People never find the money to do it right the first time but they seem to find the money to fix it later at a much higher cost.

Best of luck with your project.
 
/ Pole barn condensation #13  
Sounds like it would be better to avoid metal buildings all together unless it is something like an open carport or lento?
 
/ Pole barn condensation #14  
RayfromtTX is hitting the nail hard on the head....take his advice 100%
For outright steel buildings I would spray foam them ...only viable option IMO.
If your doing a wood pole barn with steel sheeting exterior I would frame in insulate the walls and ceiling with fibreglass or better yet rock wool or even blown in cellulose and vapor barrier the whole inside before putting up the interior cladding/sheet rock or ?
Before adding the exterior steel cladding, strap to add a airspace to vent for the walls then tyvek then cladding...for roof use tar paper below the roof steel as no matter what the steel is going to condensate regardless...the tar paper will help mitigate and if moisture collects it follows the tar paper down and out the eaves and not drip onto your insulation.
Yes the attic space needs to be very well ventilated ever how you decide to do that (full ridge vent with open eaves say)



My 2 cents for what it is worth
 
/ Pole barn condensation #15  
We have a 1860 Barn with 14 to 24 inch wide vertical board redwood siding (No batons) with a 80 year old tin roof from with lead washer nails.

The barn is 40 x 60 and summer/winter... never a hint of moisture and no insulation anywhere or wraps or building paper/felt.

Could the condensation aspect be high dependent on local conditions?
 
/ Pole barn condensation #16  
We have a 1860 Barn with 14 to 24 inch wide vertical board redwood siding (No batons) with a 80 year old tin roof from with lead washer nails.

The barn is 40 x 60 and summer/winter... never a hint of moisture and no insulation anywhere or wraps or building paper/felt.

Could the condensation aspect be high dependent on local conditions?

Yes totally
 
/ Pole barn condensation #17  
All that stuff uses energy .... LOTS of energy.

Unless you're planning on living out there or you're Jay Leno with millions in classic cars to store, what's the point? Barns and sheds store yard machines and tools under cover from direct weather. Most older barns are well ventilated and have stood for decades. My shed with a galvanized tin roof sweats a bit, but I don't sweat the sweat.
 
/ Pole barn condensation #18  
I built a pole barn myself 2 years ago. There is a product called foil faced bubble insulation that is installed on the roof system then the metal roof is installed on top. I haven’t had a drop of condensation in my building. It is basically bubble wrap with foil on one or both sides. It’s expensive but it does the job. There are other types out there that are foil faced foam. Any reputable pole barn material supplier or lumber yard should be able to help you out.
 
/ Pole barn condensation #19  
Gregb46,
In a out 12 years that bubble wrap will deteriorate. It has on every barn I used it on. Just finished putting a ceiling in a very nice barn to cover that mess. I have a thread in here on it.
 

Marketplace Items

WANCO LIGHT TOWER (A60736)
WANCO LIGHT TOWER...
(INOP) GRAVELY ZERO TURN LAWNMOWER (A59823)
(INOP) GRAVELY...
ATTENTION! PLEASE READ (A60463)
ATTENTION! PLEASE...
2012 DOOSAN G25 GENERATOR (A58214)
2012 DOOSAN G25...
2011 DRAGON 150 BBL ALUMINUM VACUUM TRAILER (A60736)
2011 DRAGON 150...
2005 JLG BOOM LIFT (A59228)
2005 JLG BOOM LIFT...
 
Top