Comparison Home Stand By Generators

/ Home Stand By Generators #421  
Calculating so Called watts via colts X amps and ending up with volt amps is the reason why a "correctly sized" generator will not carry the load.
There is the fact that a 1000W load on 120V can draw 1500VA if there is a leading or laggin power factor. Bubba adds up 4000watts, purchases a 4000Watt generator and wonders why the generator won't carry the load. Loading the 4000 watt generator with a 4000watt load that draws 50amps instead of 33.3 Amps as expected.
 
/ Home Stand By Generators #422  
I think undersizing a generator is a bad idea. I had a Coleman 7.5 kw generator, and I could hear it lug down when my well pump kicked it. One day, it lugged down, threw a rod!! A hot water heater draws at least 4500 watts, and that is a pretty constant load. My well is about 200 ft deep, a 3/4 pump with a 30 amp breaker, so I would allow 3000 watts just for a well pump. You don't want to run a motor on low power, it will shorten the life of the motor.

Your 7.5kw generator didn't throw a rod because of your 3/4hp deep well pump kicking in for 30 seconds. No way-no how.
All small engines are 'rated' at full load. Defect engine, worn, wrong oil, bad oil..
 
/ Home Stand By Generators #424  
It lugged down because it was throwing a rod!

well, that would do it...;) hard to keep up rpm when parts are missing.

lot of snowblower engines blow up for some reason; wonder if it's too much load too quickly
on a cold engine.?????
 
/ Home Stand By Generators #425  
Check Yes, they may seem to promote those brands cause they are the most popular affordable smaller standby generators for the average home owners. Not sure if you browsed the site right cause there are a lot of info on if you click on the left top quick search box under brands, sizes, fuel etc and there are hundreds of portable and standby generators. You can compare and read reviews. I think there is enough info there for the average guy who has no or some clues about generator and this site explains a lot. This was based on my decision to buy a Generac.
 
/ Home Stand By Generators #426  
I have had a Generac NG 17KW for 8 years. Except for one occasion where the contacts were soiled on the auto back-up switch it has always worked. Have the winter kit, change the oil and filter every year, tune kit twice, and replaced the battery. It does what it is supposed to and I am happy.
 
/ Home Stand By Generators #427  
I have had a Generac NG 17KW for 8 years. Except for one occasion where the contacts were soiled on the auto back-up switch it has always worked. Have the winter kit, change the oil and filter every year, tune kit twice, and replaced the battery. It does what it is supposed to and I am happy.

What does the winter kit include?
 
/ Home Stand By Generators #428  
lot of snowblower engines blow up for some reason; wonder if it's too much load too quickly on a cold engine.?????
If you are talking about Ariens, if the oldTecumseh L heads got a little low on oil, and you tilted them (as often happens at the end-of-driveway pile) enough times, the engine would notify you of your poor maintenance practices by breaking the connecting rod and punching a hole in the side of the case. The "youngest" engine I'm familiar with was nearly 10 years old.
 
/ Home Stand By Generators #429  
Check Yes, they may seem to promote those brands cause they are the most popular affordable smaller standby generators for the average home owners. Not sure if you browsed the site right cause there are a lot of info on if you click on the left top quick search box under brands, sizes, fuel etc and there are hundreds of portable and standby generators. You can compare and read reviews. I think there is enough info there for the average guy who has no or some clues about generator and this site explains a lot. This was based on my decision to buy a Generac.

Thanks again, K man, I was looking over on the right-hand side of the page. I did later look at the left-hand side display, whereby you could choose specific brands, and I looked up Kohler, and the 14 RES and the 20 RES seem to have cold starting problems. Mine is the (now discontinued) 17 RES, and I am wondering if maybe these newer 14 and 20 kw generators have gone downhill since I bought my 17 kw in 2010. I have never had a problem cold starting with my 17 RES, even at 20 below or colder.

Meanwhile, it would be interesting for someone to collect a little table with the various specs from the various brands, such as noise levels, total distortion, and the like. It seems that these types of specs, especially the distortion specs, would really affect how hard the generator is on your electronic equipment. Also, I have installed a whole house surge protector, but I have heard that the problem of "brownouts" is the what you really have to watch for in terms of their effects on electronic equipment, including your furnace controller. So, it would seem to be important for the generator to start up as quickly as possible when the voltage drops down but not completely down to zero. My Kohler manual made a big deal out of the fact that the generator kicks on fairly quickly after 10 seconds, and kicks on even if the power isn't all the way down to zero. So another question is, which generators start up quickly, and which generators kick on when, for example, the voltage level drops X percentage? I have been at the cottage when the lights would dim and then brighten, then dim and brighten, to the point where I ran downstairs and turn off the power completely so that the generator would kick in, in order not to damage my equipment. This has happened more than once, and I take it as a kind of warning sign that the power is about to go out completely.
 
Last edited:
/ Home Stand By Generators #430  
Its nice to know some folks don't have a budget. :laughing:

In all seriousness, I understand the need for sump pumps. And I enjoy convenience. I'd just like to know if anyone has figured out how much it would cost to run a large automatic generator 24/7 for a week, instead of everyone saying "who cares?", that's all. ;)

Why the rolling eyes? Maybe some people have it better figured out than you do.
 
/ Home Stand By Generators #431  
We get [after living here for 23 years, I have a pretty good set of statistics for this area] about 10-12 outage [of more than a few minutes] per year. They usually last long enough to get my wife antsy about getting some power back [so she can take a shower or feel confident in opening the fridge] so we are happy to have a manual [but with a battery starter since she can't pull the cord well enough to get our old Coleman camp unit started] 7500w unit. The most important outages are in the winter time, of course, even though we heat mostly with wood which takes no electricity. Each person has to make their own set of decisions depending on their situation and their [or their spouses] desires.
 
/ Home Stand By Generators #433  
Thanks again, K man, I was looking over on the right-hand side of the page. I did later look at the left-hand side display, whereby you could choose specific brands, and I looked up Kohler, and the 14 RES and the 20 RES seem to have cold starting problems. Mine is the (now discontinued) 17 RES, and I am wondering if maybe these newer 14 and 20 kw generators have gone downhill since I bought my 17 kw in 2010. I have never had a problem cold starting with my 17 RES, even at 20 below or colder.
No I think it demonstrates why they are sold through dealers. There is a carb heater kit that is supposed to be sold when installed in cold climates: forget what "cold" is in the manual. The local dealer always installs it though it is technically an option.

While there is some cheerleading for Generac here, locally they are the "low bidder" systems. I asked builders and others who specify generators (but don't have any sales interest) and they were pretty unanimous for Kohler over Generac. Cummins/Onan seems to make a 14kw unit but no one was familiar with them. The only other brand suggested was B&S.
 
/ Home Stand By Generators #434  
Thanks again, K man, I was looking over on the right-hand side of the page. I did later look at the left-hand side display, whereby you could choose specific brands, and I looked up Kohler, and the 14 RES and the 20 RES seem to have cold starting problems. Mine is the (now discontinued) 17 RES, and I am wondering if maybe these newer 14 and 20 kw generators have gone downhill since I bought my 17 kw in 2010. I have never had a problem cold starting with my 17 RES, even at 20 below or colder.
No I think it demonstrates why they are sold through dealers. There is a carb heater kit that is supposed to be sold when installed in cold climates: forget what "cold" is in the manual. The local dealer always installs it though it is technically an option.

While there is some cheerleading for Generac here, locally they are the "low bidder" systems. I asked builders and others who specify generators (but don't have any sales interest) and they were pretty unanimous for Kohler over Generac. Cummins/Onan seems to make a 14kw unit but no one was familiar with them. The only other brand suggested was B&S. Obviously doesn't mean Generac is "bad" and there are a lot of them around.
 
/ Home Stand By Generators #435  
No I think it demonstrates why they are sold through dealers. There is a carb heater kit that is supposed to be sold when installed in cold climates: forget what "cold" is in the manual. The local dealer always installs it though it is technically an option.

While there is some cheerleading for Generac here, locally they are the "low bidder" systems. I asked builders and others who specify generators (but don't have any sales interest) and they were pretty unanimous for Kohler over Generac. Cummins/Onan seems to make a 14kw unit but no one was familiar with them. The only other brand suggested was B&S.

I priced similar (as much as possible) Kohler and Generac units and there was essentially no price difference. I talked with three or four suppliers, three electricians who regularly install standby units, and read reviews for days. There were far more reviews of the Generac units, they tended to have better reviews, and the people I talked to said they preferred Generac to Kohler, but they would install either one I wanted.

At the same price point, there has to be a reason why so many more Generac units seem to be sold.
 
/ Home Stand By Generators #436  
Garandman you know it is like anything else you buy. No matter what brand there is always someone bias against it if they own something different. Most builders do not have sales interest cause they build and leave that to the Electrical Contractors to sell and install Generators. Generac motors are B&S Vanguard which are rated as heavy duty construction grade motors. I have nothing against any generator company as long as it satisfies its customers with good quality equipment. I love my Generac as it starts and does it's job in the cold Winter or hot Summer. So no matter what you buy if it satisfies you then great if it don't then try another brand.
 
/ Home Stand By Generators #437  
Are the noise ratings accurate when it comes to real world homeowner applications?

If I make any changes it will have to be quiet... the topography of the terrain means noise travels...
 
/ Home Stand By Generators #438  
It's interesting that you ask about noise ratings. I think it is great that you are concerned with your neighbors quality of living. However, what I find is that when I need my gen on, guess what? So do my neighbors as I have never had a 'solo' outage that I used my gen for. Most people in our neighborhood are cool [even if they do not have a gen] with the sound [obviously do not locate your unit far from your building and right next to a neighbors home], and are far too busy taking care of their own problems to feel hassled by the noise [which is often coming from several directions at once anyway]. Talk to neighbors [hope you haven't made too many enemies near by].
 
/ Home Stand By Generators #439  
Are the noise ratings accurate when it comes to real world homeowner applications?

If I make any changes it will have to be quiet... the topography of the terrain means noise travels...

I haven't checked mine with a meter (thought about it), but I think the rating seems about right. As I recall, mine is supposed to make about 66dB, which is a fair amount less than some common noises like a lawn mower running. When it's running, I know it's out there running, but it's just a background noise that isn't offensive. When I'm on the far side of the house I can't even hear it at all.
 
/ Home Stand By Generators #440  
I used to live in suburbia and when my 20kw Generac kicked on, not the test, it was pretty noisy at least one house over. But then two others were running too, as noted. Plus at least one or two portable gens which are even noisier. An unpleasant combination of sounds, but you do the best you can to minimize it.
In a really bad situation, like a tornado or hurricane, those neighbors without power may be thankful if yours is still running in your undamaged house. My wife and I used to throw hurricane parties. We would make up big pots of home made bean soup to send to neighbors or invite them over.

I am interested in the comments about preference of Kohler over Generac. I wonder why. Is it because the Kohlers have hydraulic valves and don't have to have their valves adjusted? Is their electrical apparatus of higher quality, or more conveniences? Seems to be a Ford vs Chevy situation here where both are good quality. But what if one can afford a Buick, or a Lincoln? Neither manufacturer makes more than one model per kw range; i.e. no strippers and then a deluxe fully featured model. Few options other than heaters. Compare that to buying a new truck today...

I wish one of the big two here would come up with a solid performance claim, noise ratio,fuel consumption advantage, distortion, even wiring size...then the other would have to respond, and we would finally have a spec competition, which would have to be good. Assuming the specs were meaningful. The availability of wood grain siding is not what we want...
 

Marketplace Items

Arrow Quip 10' Bow Gate (A64047)
Arrow Quip 10' Bow...
2019 Dodge Grand Caravan Van (A61569)
2019 Dodge Grand...
2002 Bobcat 863 High Flow Compact Wheel Loader Skid Steer (A59228)
2002 Bobcat 863...
UNUSED WOLVERINE SB84-84" ROCK BKT (A62131)
UNUSED WOLVERINE...
2017 Ford Expedition SUV (A61569)
2017 Ford...
Morgan 26ft Box Truck Body (A59228)
Morgan 26ft Box...
 
Top