Generator question (household wiring to be more accurate)

   / Generator question (household wiring to be more accurate) #91  
Leedscase,
Thanks for the reply. 702 is the correct section for this discussion. User permitted to manually transfer load. Nothing prohibiting generator connection to subpanel, as long as you have manually tranferred from utility.
So both the OPs and Aarons cases meet code if they follow the correct procedures. Aarons case with the kirk keys makes it fool proof, does the same function as the sliding lock.

As i said before, i don't do this, but don't believe it is against code, if your AHJ agrees. I use extension cords from generator to the load.
 
   / Generator question (household wiring to be more accurate) #94  
Usually generator threads degrade into a pi$$ing contest over back feeding. Glad to see this one was different.
 
   / Generator question (household wiring to be more accurate) #95  
Usually generator threads degrade into a pi$$ing contest over back feeding. Glad to see this one was different.

Agreed.. and on that note I think I'll install a kirk key on my dryer plug and main breaker.... Should be ok right ???
 
   / Generator question (household wiring to be more accurate) #97  
Agreed.. and on that note I think I'll install a kirk key on my dryer plug and main breaker.... Should be ok right ???
Save your self some money and just pull the meter!

SR
 

Tractor & Equipment Auctions

2008 UTILITY VS2DX DRY VAN TRAILER (A54607)
2008 UTILITY VS2DX...
UNUSED EINGP MSC2030F 20' X 30' ALL-STEEL CARPORT (A54757)
UNUSED EINGP...
2006 INTERNATIONAL 4300 DT466 SBA 4X2 BUCKET TRUCK (A51406)
2006 INTERNATIONAL...
KIDS DIRT BIKE (A53424)
KIDS DIRT BIKE...
2000 JOHN DEERE 310SE BACKHOE (A52705)
2000 JOHN DEERE...
2018 BMW 430I  4DOOR SEDAN (A54607)
2018 BMW 430I...
 
Top