Generator question (household wiring to be more accurate)

   / Generator question (household wiring to be more accurate) #91  
Leedscase,
Thanks for the reply. 702 is the correct section for this discussion. User permitted to manually transfer load. Nothing prohibiting generator connection to subpanel, as long as you have manually tranferred from utility.
So both the OPs and Aarons cases meet code if they follow the correct procedures. Aarons case with the kirk keys makes it fool proof, does the same function as the sliding lock.

As i said before, i don't do this, but don't believe it is against code, if your AHJ agrees. I use extension cords from generator to the load.
 
   / Generator question (household wiring to be more accurate) #94  
Usually generator threads degrade into a pi$$ing contest over back feeding. Glad to see this one was different.
 
   / Generator question (household wiring to be more accurate) #95  
Usually generator threads degrade into a pi$$ing contest over back feeding. Glad to see this one was different.

Agreed.. and on that note I think I'll install a kirk key on my dryer plug and main breaker.... Should be ok right ???
 
   / Generator question (household wiring to be more accurate) #97  
Agreed.. and on that note I think I'll install a kirk key on my dryer plug and main breaker.... Should be ok right ???
Save your self some money and just pull the meter!

SR
 

Tractor & Equipment Auctions

2018 KENWORTH T800 DAYCAB (A53843)
2018 KENWORTH T800...
BUNDLE OF 25" - 49", 2" X 2" TUBING (A54756)
BUNDLE OF 25" -...
2007 Ford Ranger Pickup Truck (A50323)
2007 Ford Ranger...
2017 Ford Explorer AWD SUV (A55758)
2017 Ford Explorer...
2022 CATERPILLAR 242D3 SKID STEER (A51406)
2022 CATERPILLAR...
2013 Ford F-650 Flatbed Truck (A51692)
2013 Ford F-650...
 
Top