I have a large inverter on my houseboat. I have run (Twin) double 00 cable to the battery box. in the box i want to put a fuse block however the fuse block i have will only take one cable would it be acceptable to reduce back to one cable before going into and out of the fuse block.
 
/ Cable size
  • Thread Starter
#3  
Ron,

The fuse i have is very similar to that one .

My inverter required 0000 cable which i was unable to get so as ran TWO 00 cables to get cable capacity. However my fuse will not accommodate two cables so i wondered if I could reduce back to a single cable for about 2 inches either side going in and out of the fuse
 
/ Cable size #4  
Reducing from two 00 to one will make the single 00 cable the smallest point in your wiring. You will not be able to draw enough current through a single 00. Other than cost. Why not use 2 fuse holders. One on each 00 line. Each holder would have a fuse 1/2 total amperage.
What size inverter do you have? My 5000 watt inverter has 00 for a 10' run.
 
/ Cable size #5  
Ron H. is right, you need 2 fuse blocks.

If you use 2 fuse blocks be sure you use fuses rated for 1/2 the amperage load.

Bill Tolle
 

Marketplace Items

2008 New Holland T2420 (A60462)
2008 New Holland...
John Deere XUV825E (A61307)
John Deere XUV825E...
2019 COLEMAN BT200X MINI-BIKE (A64280)
2019 COLEMAN...
2001 Peterbilt 379 Tri-Axle Dump Truck (A59230)
2001 Peterbilt 379...
2012 Freightliner M2106 Bucket Truck, Terex Hi-Ranger HR52M, 52FT Platform Height (A63689)
2012 Freightliner...
2004 International 4400 Flatbed-Dump (A62613)
2004 International...
 
Top