I have a large inverter on my houseboat. I have run (Twin) double 00 cable to the battery box. in the box i want to put a fuse block however the fuse block i have will only take one cable would it be acceptable to reduce back to one cable before going into and out of the fuse block.
 
   / Cable size
  • Thread Starter
#3  
Ron,

The fuse i have is very similar to that one .

My inverter required 0000 cable which i was unable to get so as ran TWO 00 cables to get cable capacity. However my fuse will not accommodate two cables so i wondered if I could reduce back to a single cable for about 2 inches either side going in and out of the fuse
 
   / Cable size #4  
Reducing from two 00 to one will make the single 00 cable the smallest point in your wiring. You will not be able to draw enough current through a single 00. Other than cost. Why not use 2 fuse holders. One on each 00 line. Each holder would have a fuse 1/2 total amperage.
What size inverter do you have? My 5000 watt inverter has 00 for a 10' run.
 
   / Cable size #5  
Ron H. is right, you need 2 fuse blocks.

If you use 2 fuse blocks be sure you use fuses rated for 1/2 the amperage load.

Bill Tolle
 
   / Cable size #6  
I think they are giving you some good advice on using 2 fuse blocks.
 

Tractor & Equipment Auctions

Adams 6 Ton Hydraulic Lime Spreader (A55301)
Adams 6 Ton...
2019 MACK PINNACLE P164T DAY CAB ROAD TRACTOR (A51406)
2019 MACK PINNACLE...
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
Case 950 8 Row Air Planter (A55301)
Case 950 8 Row Air...
UNUSED X-STAR ACS LOADER BOOM LIFT (A52706)
UNUSED X-STAR ACS...
Scag Mower (A50324)
Scag Mower (A50324)
 
Top