Beam Span?????

/ Beam Span????? #1  

dieselscout80

Elite Member
Joined
Nov 17, 2007
Messages
2,643
Location
South Carolina
Tractor
New Holland TC45DA
I want to know how far a beam can span. I finishing my basement.

Beam in questions is made of three 2"x10" and a 1/2' sheet of plywood nailed together.

It is part of the main floor of my house and has floor 2"x10" joists attached perpendicular on both sides on 16" centers. The joists are supported by the block foundation on both sides one side spans about 11'9" the 12'3". The load above the beam is a hallway and a bed room/office and in the attic there are 5 roof truss supports.

I want to span 17' if possible without additional supports.

First question can the existing beam support the 17' foot span?

Second what do I need to do to reinforce the existing beam?

I've thought about running another beam under it made from 20' either 2"x6", 2"x8" or 2"x10" with 1/2" plywood and attach it to the existing beam with metal plates between the joists.

I've thought about running another beam under it made from 20' either 2"x4", 2"x6" steel and attach it to the existing beams.

A friend who is a ENG mentioned cutting the plywood out and taking a I beam with a 7" web and having the the top flange removed and placing it where the plywood was and then bolting through the 2"x10". How would I cut the plywood out my only idea has been a chainsaw?

Could I use 3 x 2 x 3/16 Steel Angle on both sides of the existing beam and bolt it through and do the same thing?
 
/ Beam Span????? #2  
Your local building department can tell you what they will approve.

Clear spanning 17' is a looooong way for a carrier bean, if I understand you correctly. This center beam carries the floor joists?
 
/ Beam Span????? #3  
Your local building department can tell you what they will approve.

Clear spanning 17' is a looooong way for a carrier bean, if I understand you correctly. This center beam carries the floor joists?

Agreed. There are specific codes and requirements that vary by area/district/location, whatever. For a residential structure, I would advise you to get whatever you have in mind approved by whoever the appropriat authority is in your area.

And when it comes to basic strength, you gain MUCH more by going deeper rather than wider. And you really need to know the loading that is going to be on the beams, and not just " a hallway and the floor joists". Calculating the span gets a lot more complicated with wood/plywood laminated beams, certain types of connections, how they are attached, hast size nails, type of glue, ETC. It is not as cut and driedas just sizing a steel beam for load x.

Get with a PE in your area and do it to code, follow his reccomendations. It will be well worth the money and peice of mind.
 
/ Beam Span?????
  • Thread Starter
#4  
Your local building department can tell you what they will approve.

Clear spanning 17' is a looooong way for a carrier bean, if I understand you correctly. This center beam carries the floor joists?

Not sure what you mean by carrier beam, but the joist are butted into the beam. I plan to add metal joist backets that will support the joist and be screwed to the beam.
 
/ Beam Span????? #5  
Not sure what you mean by carrier beam, but the joist are butted into the beam. I plan to add metal joist backets that will support the joist and be screwed to the beam.

Yup. In our lingo, that's a carrier beam. It will be carrying something akin to 28 floor joists and all they weight that they support in walls, flooring, furniture, etc. Agreed you need to consult with an engineer and have approval by the township/village/city/county etc. You are not asking the impossible. Not at all. It's just that "guessing" is reckless. You need scientific facts. Best wishes. Around here, we use 8" i beam steel. But, we post it every 12 ft. You're asking to clear span 17 feet.
 
/ Beam Span????? #6  
I want to know how far a beam can span. I finishing my basement.

Beam in questions is made of three 2"x10" and a 1/2' sheet of plywood nailed together.

It is part of the main floor of my house and has floor 2"x10" joists attached perpendicular on both sides on 16" centers. The joists are supported by the block foundation on both sides one side spans about 11'9" the 12'3". The load above the beam is a hallway and a bed room/office and in the attic there are 5 roof truss supports.

I want to span 17' if possible without additional supports.

First question can the existing beam support the 17' foot span?

Second what do I need to do to reinforce the existing beam?

I've thought about running another beam under it made from 20' either 2"x6", 2"x8" or 2"x10" with 1/2" plywood and attach it to the existing beam with metal plates between the joists.

I've thought about running another beam under it made from 20' either 2"x4", 2"x6" steel and attach it to the existing beams.

A friend who is a ENG mentioned cutting the plywood out and taking a I beam with a 7" web and having the the top flange removed and placing it where the plywood was and then bolting through the 2"x10". How would I cut the plywood out my only idea has been a chainsaw?

Could I use 3 x 2 x 3/16 Steel Angle on both sides of the existing beam and bolt it through and do the same thing?



What your friend was talking about is called a flitch plate beam. Below is a link to a worked example with at 2x10 beam / flitch plate with 1/2" steel.

STRUCTUREmag: Flitch Plate Beams


The example shows a 12' span.... Seems to me in your case it would make economic sense to break it up into two 8.5' sections. Which is probably what you already have...

Steve
 
/ Beam Span?????
  • Thread Starter
#7  
What your friend was talking about is called a flitch plate beam. Below is a link to a worked example with at 2x10 beam / flitch plate with 1/2" steel.

STRUCTUREmag: Flitch Plate Beams


The example shows a 12' span.... Seems to me in your case it would make economic sense to break it up into two 8.5' sections. Which is probably what you already have...

Steve

The existing beam had two support posts 12' 6" apart in the 34' total span.

We don't having an inspector/inspection program out here.
 
/ Beam Span????? #8  
Go to your local lumber yard that has experience with engineered beams, not glu-lams but beam products that are manufactured from veneers or strands, Georgia Pacific, Louisianna Pacific, whoever services your area of the country. A good over the counter lumber salesman can easily through the manfacturer's tech tables tell you what size manufactured beam you need for your loading and span requirements. Use the L/480 tables or higher. Please don't take this on your own by sandwiching whatever together as life and limb are at stake.
 
/ Beam Span????? #9  
The existing beam had two support posts 12' 6" apart in the 34' total span.

It is a whole lot easier to span 12'6" than 17'.

You really need to have this beam designed by an engineer.

The steel angle idea is not going to work.

The right way to get rid of the plywood is to start over with new 2x10s.

You can probably buy an engineered wood beam which will span the length required, but the depth will be a lot greater than 9.5". Whether you can accept the reduced headroom in that part of the basement is up to you.

A steel beam can probably span this distance, but costs are higher than wood.

The other way to go would be to design the basement with more posts. I haven't done any calculations, but my sense of this is that if you could work out a floor plan with three posts, four nearly even spans, you could use a wooden beam with a depth you can live with.

I doubt the original beam met modern standards...

As has been mentioned, you get a lot more good from a deeper beam than you do from a wider one.
 
/ Beam Span????? #10  
It sounds like the basement floor and surround is already in but I am unclear of that. If it is and you decide to add posts to shorten the spans, at that point you don't have any bearing post footings in place which would mean cutting the slab and digging footings and adding steel for each post. That in itself would be monumental. Start by calcing (shouldn't cost you a dime) an engineered beam.
 
/ Beam Span????? #11  
So are you saying that you want to modify the origional 12' 6" span and make it 17'?
Are there any load bearing walls/posts above this beam?
A steel I beam would be the best, but if that isn't possible then your gonna need to go wider than a 2x10 to span 17 ft. Over time it will sag for sure.
In my oppinion based on supporting only the floor, a 14" laminated beam would work fine.
You could add securely bolted angle braces at each end to shorten the span if possible.
If the beam also supports the 2nd floor or roof then you should talk to an engineer about it for sure.
 
/ Beam Span????? #12  
Here's my take:

He wants to span 17'. The load being supported is a finished floor load from a residence. So the design load per square foot should be around 40 PSF/live and 10 PSF/dead for a total of 50 PSF.

This beam is supporting floor joists that are perpendicular to it. One side spans 11'-9", the other 12'-3". The beam will have to support the load over half the span of each side (the remainder of the load is supported by the concrete block walls on which the floor joists bear (or are attached).

So our total floor area to be supported is 12' wide (half of 11'9"+half of 12'3") by 17' long, for a total square footage of 204 sq. ft. Multiply this by 50 psf = 10,200 lb load.

What I'm not sure of it if there is additional loading to be supported, because I'm not sure if there is a wall above that is holding up weight and if there is ceiling and roof loading or if the trusses that he mentioned actually span the distance and while they may set on the wall that sets on the floor area, the floor actually bears (essentially) no additional load.

So now we've got to see if the existing beam will hold the weight.

The span table I have works in 2' increments, so I'll average between 16' and 18' span.

A 2x10 will hold up about 1,000 lbs over 17'. It's a triple 2x10, so that's only going to support about 3,000 lbs.

If it were supported at the mid-point of the span, then the loads are cut in half. A 2x10 at 8' span supports 2,139 lbs, so a triple would hold 6,417 lbs (which is well over half of our load of 10,200 lbs).

In the flow chart of this project, if he can add a post (and a footer), that will be the cheapest way to support this.

If a clear span is required, I would say he would need to go with an engineered beam or a steel beam.

From an old chart that I have, there are many beams that will support 10,200 lbs over 17 ft. The two lightest that I could find are a standard I-beam, 10 x 4 3/4 (25.4 lbs/ft) and a wide-flange I-beam (10 x 5 1/4, 21 lbs/ft). There are a couple of 8" tall beams that would support it as well. Both of the beams listed are rated to support at leat 16 kips at 18' span.

In my opinion, this is more of a carpentry equation than an engineering calcution. I think that we are dealing with (more a less) a residential situation, so dragging engineers into is probably not necessary.

Obvious disclaimer: unless local codes require stamped or engineer-approved plans, etc. etc. etc. I'm fortunate that I live in an area without such codes for residences, so I have never had to deal with building permits, inspections, etc. so I cannot account for that.

At any rate, bottom line, I don't think the existing beam is capaple of supporting the load, long term. I don't think that a good answer can be manufactured from dimensional lumber being attached to it. I think the options are either:

1. a post on the existing beam
2. a steel beam in place of or underneath the existing beam
3. a pre-engineered wood beam in place of or underneath the existing beam

Good luck and take care.

Edit:

Sorry, I didn't retain the part about the overall span being 34' and (I'm assuming) you want to separate it into two 17' spans instead of three 12'6" spans. In that case, I would use a steel beam under or in place of the existing and supporting it with a column (unless you wan't to add more posts).

And I see that an inspection is not required, so no worries there. I think it's obvious that the best thing to do is take the advice of unknown people from an internet forum! (This is what I hate about typing a post - I can can't convey voice inflection. I can't even find a proper emoticon. What I'm trying to do is come across with a good-natured ribbing comment, and I'm afraid it may sound like a condescending jack@$$. So I'm just trying to be funny, not a jerk....although sometimes, I can do both).

Anyway, good luck and take (again).
 
Last edited:
/ Beam Span????? #13  
Here's my take:

He wants to span 17'. The load being supported is a finished floor load from a residence. So the design load per square foot should be around 40 PSF/live and 10 PSF/dead for a total of 50 PSF.

This beam is supporting floor joists that are perpendicular to it. One side spans 11'-9", the other 12'-3". The beam will have to support the load over half the span of each side (the remainder of the load is supported by the concrete block walls on which the floor joists bear (or are attached).

So our total floor area to be supported is 12' wide (half of 11'9"+half of 12'3") by 17' long, for a total square footage of 204 sq. ft. Multiply this by 50 psf = 10,200 lb load.

What I'm not sure of it if there is additional loading to be supported, because I'm not sure if there is a wall above that is holding up weight and if there is ceiling and roof loading or if the trusses that he mentioned actually span the distance and while they may set on the wall that sets on the floor area, the floor actually bears (essentially) no additional load.

So now we've got to see if the existing beam will hold the weight.

The span table I have works in 2' increments, so I'll average between 16' and 18' span.

A 2x10 will hold up about 1,000 lbs over 17'. It's a triple 2x10, so that's only going to support about 3,000 lbs.

If it were supported at the mid-point of the span, then the loads are cut in half. A 2x10 at 8' span supports 2,139 lbs, so a triple would hold 6,417 lbs (which is well over half of our load of 10,200 lbs).

In the flow chart of this project, if he can add a post (and a footer), that will be the cheapest way to support this.

If a clear span is required, I would say he would need to go with an engineered beam or a steel beam.

From an old chart that I have, there are many beams that will support 10,200 lbs over 17 ft. The two lightest that I could find are a standard I-beam, 10 x 4 3/4 (25.4 lbs/ft) and a wide-flange I-beam (10 x 5 1/4, 21 lbs/ft). There are a couple of 8" tall beams that would support it as well. Both of the beams listed are rated to support at leat 16 kips at 18' span.

In my opinion, this is more of a carpentry equation than an engineering calcution. I think that we are dealing with (more a less) a residential situation, so dragging engineers into is probably not necessary.

Obvious disclaimer: unless local codes require stamped or engineer-approved plans, etc. etc. etc. I'm fortunate that I live in an area without such codes for residences, so I have never had to deal with building permits, inspections, etc. so I cannot account for that.

At any rate, bottom line, I don't think the existing beam is capaple of supporting the load, long term. I don't think that a good answer can be manufactured from dimensional lumber being attached to it. I think the options are either:

1. a post on the existing beam
2. a steel beam in place of or underneath the existing beam
3. a pre-engineered wood beam in place of or underneath the existing beam

Good luck and take care.

Edit:

Sorry, I didn't retain the part about the overall span being 34' and (I'm assuming) you want to separate it into two 17' spans instead of three 12'6" spans. In that case, I would use a steel beam under or in place of the existing and supporting it with a column (unless you wan't to add more posts).

And I see that an inspection is not required, so no worries there. I think it's obvious that the best thing to do is take the advice of unknown people from an internet forum! (This is what I hate about typing a post - I can can't convey voice inflection. I can't even find a proper emoticon. What I'm trying to do is come across with a good-natured ribbing comment, and I'm afraid it may sound like a condescending jack@$$. So I'm just trying to be funny, not a jerk....although sometimes, I can do both).

Anyway, good luck and take (again).

IMO it is more than a simple carpentry equation. There is a lot of unknowns that neither you NOR I can account for without actually seeing it in person.

While your numbers are correct, they assume no loading from the walls and the supported roof trusses that he mentioned there are a total of 5. Depending on exactly how the stuss is designed and supported by other means will vary the amount of load that will be seen by the walls, and thus the floor and beam. There is no way to know for sure without a PE looking at it. And in your triple 2x10 beam you are also not accounting fot the 1/2" plywood.

I will also add that I have not seen a w10x21 beam. To my knowledge they jump from a w10x19 to a w10x22, but I could be wrong. Minor detail none the less.

And a question for the OP. Why are you wanting to go to all this trouble just to eliminate ONE post in the basement??? You mentioned it is already that the current beam is supported by 2 exixting posts @12'6" appart. And you are wanting to cut it down to just one. WHY??

A carrier beam under a hous has to support HUGE loads. Most common is a 30x50 foundation with a BIG w8x28 beam running the entire length. And even them are supported at ever 12'6".
 
/ Beam Span????? #14  
IMO it is more than a simple carpentry equation. There is a lot of unknowns that neither you NOR I can account for without actually seeing it in person.

While your numbers are correct, they assume no loading from the walls and the supported roof trusses that he mentioned there are a total of 5. Depending on exactly how the stuss is designed and supported by other means will vary the amount of load that will be seen by the walls, and thus the floor and beam. There is no way to know for sure without a PE looking at it. And in your triple 2x10 beam you are also not accounting fot the 1/2" plywood.

I will also add that I have not seen a w10x21 beam. To my knowledge they jump from a w10x19 to a w10x22, but I could be wrong. Minor detail none the less.

And a question for the OP. Why are you wanting to go to all this trouble just to eliminate ONE post in the basement??? You mentioned it is already that the current beam is supported by 2 exixting posts @12'6" appart. And you are wanting to cut it down to just one. WHY??

A carrier beam under a hous has to support HUGE loads. Most common is a 30x50 foundation with a BIG w8x28 beam running the entire length. And even them are supported at ever 12'6".

In fairness to me, I mentioned that I was unsure of the additional loading, so I agree that that is an important factor. That is definately something that would have to be considered.

Because the triple 2x10 is only rated to support about 3,000 lbs, the effect of the plywood is negligible in this case (unless a sheet of plywood could support an additional 7,000 lbs over 17').

I haven't seen a w10x21 either, but it shows up on my chart. Obviously going a with a lighter weight beam capable of supporting the load will be a cheaper alternative.

And I agree that someone knowledgeable should look at the situation and see all the loads involved, but unless it is required by code (and it isn't), having a PE is an unnecessary expense. It is just a simple calculation of total load over a distance and finding the appropriate structural member to support it.

I don't know WHY he wants to change the span; I just know THAT he wants to change the span. So I tried to answer his question as best I could.

And who knows .... maybe a PE is looking at this problem right now....
 
/ Beam Span?????
  • Thread Starter
#15  
Here's my take:

He wants to span 17'. The load being supported is a finished floor load from a residence. So the design load per square foot should be around 40 PSF/live and 10 PSF/dead for a total of 50 PSF.

This beam is supporting floor joists that are perpendicular to it. One side spans 11'-9", the other 12'-3". The beam will have to support the load over half the span of each side (the remainder of the load is supported by the concrete block walls on which the floor joists bear (or are attached).

So our total floor area to be supported is 12' wide (half of 11'9"+half of 12'3") by 17' long, for a total square footage of 204 sq. ft. Multiply this by 50 psf = 10,200 lb load.

What I'm not sure of it if there is additional loading to be supported, because I'm not sure if there is a wall above that is holding up weight and if there is ceiling and roof loading or if the trusses that he mentioned actually span the distance and while they may set on the wall that sets on the floor area, the floor actually bears (essentially) no additional load.

So now we've got to see if the existing beam will hold the weight.

The span table I have works in 2' increments, so I'll average between 16' and 18' span.

A 2x10 will hold up about 1,000 lbs over 17'. It's a triple 2x10, so that's only going to support about 3,000 lbs.

If it were supported at the mid-point of the span, then the loads are cut in half. A 2x10 at 8' span supports 2,139 lbs, so a triple would hold 6,417 lbs (which is well over half of our load of 10,200 lbs).

In the flow chart of this project, if he can add a post (and a footer), that will be the cheapest way to support this.

If a clear span is required, I would say he would need to go with an engineered beam or a steel beam.

From an old chart that I have, there are many beams that will support 10,200 lbs over 17 ft. The two lightest that I could find are a standard I-beam, 10 x 4 3/4 (25.4 lbs/ft) and a wide-flange I-beam (10 x 5 1/4, 21 lbs/ft). There are a couple of 8" tall beams that would support it as well. Both of the beams listed are rated to support at leat 16 kips at 18' span.

In my opinion, this is more of a carpentry equation than an engineering calcution. I think that we are dealing with (more a less) a residential situation, so dragging engineers into is probably not necessary.

Obvious disclaimer: unless local codes require stamped or engineer-approved plans, etc. etc. etc. I'm fortunate that I live in an area without such codes for residences, so I have never had to deal with building permits, inspections, etc. so I cannot account for that.

At any rate, bottom line, I don't think the existing beam is capaple of supporting the load, long term. I don't think that a good answer can be manufactured from dimensional lumber being attached to it. I think the options are either:

1. a post on the existing beam
2. a steel beam in place of or underneath the existing beam
3. a pre-engineered wood beam in place of or underneath the existing beam

Good luck and take care.

Edit:

Sorry, I didn't retain the part about the overall span being 34' and (I'm assuming) you want to separate it into two 17' spans instead of three 12'6" spans. In that case, I would use a steel beam under or in place of the existing and supporting it with a column (unless you wan't to add more posts).

And I see that an inspection is not required, so no worries there. I think it's obvious that the best thing to do is take the advice of unknown people from an internet forum! (This is what I hate about typing a post - I can can't convey voice inflection. I can't even find a proper emoticon. What I'm trying to do is come across with a good-natured ribbing comment, and I'm afraid it may sound like a condescending jack@$$. So I'm just trying to be funny, not a jerk....although sometimes, I can do both).

Anyway, good luck and take (again).

Not two 17' spans the one span is 16', but it has a load bearing wall under it with one steel post at about 15' and multiple doubled 2"x4" and one tripled 2"x4".

Here are some pics and some drawings.
 

Attachments

  • Basement  drawing.JPG
    Basement drawing.JPG
    63.9 KB · Views: 382
  • Upstairs Drawing.JPG
    Upstairs Drawing.JPG
    51.5 KB · Views: 291
  • IMG_4383.JPG
    IMG_4383.JPG
    981.1 KB · Views: 2,399
  • IMG_4384.JPG
    IMG_4384.JPG
    964 KB · Views: 1,433
  • IMG_4385.JPG
    IMG_4385.JPG
    936.4 KB · Views: 668
  • IMG_4386.JPG
    IMG_4386.JPG
    967 KB · Views: 571
  • Load Bearing Wall.jpg
    Load Bearing Wall.jpg
    38.2 KB · Views: 1,048
  • Load Bearing Wall doubled 2x4s.jpg
    Load Bearing Wall doubled 2x4s.jpg
    35.6 KB · Views: 343
  • Load Bearing Wall steel post.jpg
    Load Bearing Wall steel post.jpg
    71.8 KB · Views: 548
  • Load Bearing Wall steel post Lower.jpg
    Load Bearing Wall steel post Lower.jpg
    74.7 KB · Views: 417
  • Posts Oridginal 2.jpg
    Posts Oridginal 2.jpg
    193.5 KB · Views: 601
  • Posts Original.jpg
    Posts Original.jpg
    42.3 KB · Views: 358
/ Beam Span????? #17  
For reference Code here in northern Illinois allow 9' span with three 2x10's on a single story house.
 
/ Beam Span????? #18  
Am I correct in assuming that (what you are calling) the truss supports run from the attic area and are either bearing on or are inside the hallway way, which in turn sets on the floor joints that are supported by the beam?

If that is the case, we just need to add together the area of the roof that is being supported by truss supports in the same manner in which we did the floor area being supported and add that to the calculation (and account for the dead weight of the wall).

Are the trusses (are they trusses or rafters - because I don't see any of the webbing that trusses have, so I'm wondering if they are not just rafters) running parrallel with the 34' dimension of the house? Is the peak of the roof in the middle (and I have no idea if it is a simple gable roof or if it is more complicated than that).

I would still say that it will boil down to that there is not a "good" way to do it by adding dimensional lumber to the existing beam. I think you will still have to either go with an engineered wood beam or a steel beam (or add/leave a post).

Good luck.
 
/ Beam Span?????
  • Thread Starter
#19  
I just taked to a building supply place and they recommended removing the old beam for the 17' span and replacing it with 2 LVL's either 14" or 16" deep. LVL's are 1.75" thick so I'll have to put a 2"x10" or a 2"x12" between them to equal my current beam width.
 
/ Beam Span?????
  • Thread Starter
#20  
Am I correct in assuming that (what you are calling) the truss supports run from the attic area and are either bearing on or are inside the hallway way, which in turn sets on the floor joints that are supported by the beam?

If that is the case, we just need to add together the area of the roof that is being supported by truss supports in the same manner in which we did the floor area being supported and add that to the calculation (and account for the dead weight of the wall).

Are the trusses (are they trusses or rafters - because I don't see any of the webbing that trusses have, so I'm wondering if they are not just rafters) running parrallel with the 34' dimension of the house? Is the peak of the roof in the middle (and I have no idea if it is a simple gable roof or if it is more complicated than that).

I would still say that it will boil down to that there is not a "good" way to do it by adding dimensional lumber to the existing beam. I think you will still have to either go with an engineered wood beam or a steel beam (or add/leave a post).

Good luck.

You are correct they are rafters.
 
 
Top