From a slight different perspective from a welding site I visit the generator should should have about 50% more wattage capability than runtime wattage requirement of "welder" to take care of initial surge for when initial striking an arc... Of course this is a welder application, BUT I suspect the same theory may apply with start surge requirement for air compressor motor....
So if a welder requires 120 volt at 20 amp, that is 2400 watts at 120 volts so any generator should be capable of supplying 3600 watts (includes 50% factor) ....
Going on that theory if your air compressor requires 15 amp as normal run, then it would be 1800 watts, and with addition 50% factor then generator should be capable of 2700 watts (surge).....A limiting factor may be circuit breaker and receptacle on generator output panel....
I personally use a 7500 watt generator running a 120V MIG welder that requires about 24 amps running full tilt weld (2880 watts) and with 50% factor added in that is 4320 watts... My only issue was the 120 volt 30 amp receptacle on generator was a 3 prong twist lock plug/receptacle and have to convert it to 2 prong w/ground adapter cord to match that on welder (remember this a 120 volt 140 amp MIG welder) .... And yes the welder requires a 30 amp breaker and appropriate wire size when on shop power...
THE main limiting factor of generator is, can the rotating mass of generator (flywheel/armature) maintain the output level of power without severely bogging down from excessive load and causing severe voltage drop and lose frequency stability.... ,
IF you chose to ignore this post its ok.... It was just put up for perspective....
So if a welder requires 120 volt at 20 amp, that is 2400 watts at 120 volts so any generator should be capable of supplying 3600 watts (includes 50% factor) ....
Going on that theory if your air compressor requires 15 amp as normal run, then it would be 1800 watts, and with addition 50% factor then generator should be capable of 2700 watts (surge).....A limiting factor may be circuit breaker and receptacle on generator output panel....
I personally use a 7500 watt generator running a 120V MIG welder that requires about 24 amps running full tilt weld (2880 watts) and with 50% factor added in that is 4320 watts... My only issue was the 120 volt 30 amp receptacle on generator was a 3 prong twist lock plug/receptacle and have to convert it to 2 prong w/ground adapter cord to match that on welder (remember this a 120 volt 140 amp MIG welder) .... And yes the welder requires a 30 amp breaker and appropriate wire size when on shop power...
THE main limiting factor of generator is, can the rotating mass of generator (flywheel/armature) maintain the output level of power without severely bogging down from excessive load and causing severe voltage drop and lose frequency stability.... ,
IF you chose to ignore this post its ok.... It was just put up for perspective....