radios1
Elite Member
they are probably using an isolation transformer with a shielded secondary to power it along with a GFCI, so no current to ground, it's still a hazard though, since you can get a shock from hot to neutral!..
they are probably using an isolation transformer with a shielded secondary to power it along with a GFCI, so no current to ground, it's still a hazard though, since you can get a shock from hot to neutral!..
In 2014 Code bathrooms, and unfinished basements didn't need AFCI.
In 2020 this has been changed to ALL 120V, 1-phase 15/20 amps outlets in dwellings.
Are they better than GFCI? Are apples better than oranges?
They really do different things. And solve different problems.
With most short circuits where you have "good grounds" (green wire connected to metal parts), and a short circuit to that metal part occurs, the "good ground" lets such a large amount of short circuit current to pass that the standard breaker trips or a fuse blows. It's sort of counter-intuitive that you WANT a LARGE amount of short circuit current to occur. So you give it a nice (green wire) path.
GFCI's solve the problem when you have bad grounds (no green wires, or poor, etc..) and the short circuit current doesn't have a good path back to the transformer and current is not large enough to trip the breaker and the metal enclosure stays energized waiting for someone to come along and touch it. GFCI's trip on the tiniest of stray ground fault current.
Like other have said AFCI's compensate for poor contractors.
AFCI's are for the problem where all the current stays IN the proper wire path (i.e. no ground fault for a GFCI to detect), but a poor wiring connection creates electrical resistance at a connection. This is equivalent to creating a mini-heater at that connection (switch, receptacle, junction, etc..) in series with the normal load being operated. This heat can melt things and catch surrounding materials on fire. AFCI's are suppose to detect the arc that comes with these poor connections.
...but note: for this "mini-heater" to be created, the "normal" load has to be pulling enough current that it creates heat at the bad connection.
For most loads like lighting and motors, if there's a bad connection that adds resistance to the circuit (and reduces the voltage the load sees) the user will detect that full voltage is not getting to the load and know there's a problem (lights may flicker, motor may not start, etc..) hopefully before the "mini-heater" bad connection ignites.
But if your running a (say) space heater, you're not going to detect that it's only putting out 1000 watts instead of 1600W, meanwhile the receptacle connection is putting out 300 Watts of heat, etc...(made up numbers). GFCI's or standard breakers can't detect this mini-heater in the circuit because no current is leaking elsewhere, and there is no overload happening (the current might actually decrease with the increased circuit resistance).
If you confident wiring was installed properly, my GUT feeling is GFCI's protect better for future unintended events (like dropping radio in bathtub, insulation on a extension cord getting nicked, etc..). Again: apples and oranges.
:2cents:
Our Xmas lights tripped off two nights ago in a thunderstorm.
The protected plug for the outside, is actually wired through a GFCI inside the garage, behind my stored trailer.
The Xmas lights are thus already done for this year.
I ain't movin all that shxt!
I like isolation transformers. Shaver outlets used to have them.
I always wondered about the physics of electric shock. So say those guys are in a rubber pool, no contact with the earth, not even capacitive. And you put two leads (hot and neutral) in the water with minor seperation, like an appliance. Will someone in the water get shocked? Now what of same thing in a grounded, porcelan (sp?) coated bath tub?
I like isolation transformers. Shaver outlets used to have them.
I always wondered about the physics of electric shock. So say those guys are in a rubber pool, no contact with the earth, not even capacitive. And you put two leads (hot and neutral) in the water with minor seperation, like an appliance. Will someone in the water get shocked?
distilled, but yet, contaminated..We need to get those lazy criminals waiting on death row out of their cells and have them be of some use to humanity. Do you feel that? lol
I get livened up from time to time working on live stuff. Just make sure I'm not grounded and usually stand on a piece of insulated material. But I am always somehow surprised that I don't feel a thing. I guess if the linemen can't feel half a million volts, I'm not gonna feel 110V!
"They" say distilled water doesn't pass electricity, but I am confused, because water sensor probes in Diesel filters, I am playing with, rely on the conductance of water, and that will be distilled.
The stupid thing about GFIs is that they start to cause problems in EXACTLY the locations they were meant to serve. Hardly a point running outside extension cords in the wet, X-Mas lights or a block heater. They will trip every time!
All residential panels are same internal sizes. Commercial panels are generally 24" wide, but they surface mount. Homeline panels now utilize neutral bars that work with gfci and arc fault breakers so there is no white tail wire. this really frees up space in panel. As long as you take care making up a panel, the use of gfci and arc fault breakers really dont get in the way. I group all my wires in a way to make interiors very clean and dont appear overcrowded. Now if every breaker hads a white nurtral coiled tail, then the panels are a real messOn the subject of AFCIs, I have a puzzle that some of the electricians might have some insight into.
Most circuit breaker panels are sized to fit between two studs set at 16" OC, so they are 14.5 inches wide. The space between the breaker and the side of the box is about 4 inches (depending on the manufacturer), which has never been overly generous for running wires when they enter the box at the top or bottom. AFCI or GFCI breakers are quite a bit larger, leaving only about 2.25 inches between the breaker and the side of the box.
So breakers with increased functionality are getting bigger, but not the panels that they go into. Making a panel box larger wouldn't cost much more, since the internals stay the same, but it would make wiring the breakers a lot easier. Framing a wall to accept a larger box would be simple. So why are we stuck with 14.5" wide panel boxes? Or are there wider ones now available? Or am I missing something?
(The replacement for our old FPE Stab-Lok box was a "plug-on neutral" box, which cuts down somewhat on the wires)
Chris
what brand panel is it. I use siemens and square d panels and you can use top , bottom or sides for wire entry. No restrictions from entry. As for wire nutting that’s not supposed to occur...And to make matters worse, usually the Utility entry and main breaker occupies the top portion, and it's not allowed to put your branch circuits through there, so you are denied one side of the panel for wiring.
I am building a load shedding system which is in a cabinet adjacent to my load center. I have to run my heating circuits into this new box. But if the wires are not long enough and you can't make connections inside the load center cabinet, sp what is a guy supposed to do? Can you solder connections or something to make them compliant?
I agree, and thats why im sure inspectors dont say much about it.As ridiculous as that is, since the entire electrical service panel is made up of nothing BUT JUNCTIONS. Service in, neutral bar, ground bar, breakers with screw terminals, etc. Who dreams up this stuff? Maybe we should just skip the wire nuts and use un-insulated screw clamps to join wire segments inside a panel; would they be allowed then?
Since we're including GFI breakers in this discussion, what about a circuit that has a GFI and then downstream (farther from the main panel electrically) there is another GFI? I always thought that the first GFI protected the rest of the downstream outlets.
Pretty sure every one I have seen will protect downstream receptacles. Some of them don't have an outlet on the front, but they all protect downstream receptacles.I thought they made 2 types of GFCI receptacles, one that protects downstream devices and one that doesn’t. Now I’m not sure if they make ones that don’t. I don’t see any sold on-line that don’t.
Since we're including GFI breakers in this discussion, what about a circuit that has a GFI and then downstream (farther from the main panel electrically) there is another GFI? I always thought that the first GFI protected the rest of the downstream outlets.