Wiring house & shop
/ Wiring house & shop #1
NTG
Roanoke, AL
2016 New Holland Workmaster 33
I'm interested in building a house and shop on some land. I have not contacted the power company yet as I wanted to get some advice on how to route the power into my property and if I have any options available to me. The entrance to my property is funnel shaped with about a 300' road leading into the gate. On my attachment, point 1 is where the end of the county road meets my private road, point 2 is where my private road leads into my property, point 3 is where my shop will be located and point 4 is where my house will be located. The distance between point 2 and point 4 is approximately 470 feet if the wire would be cheaper going that way first. My question is does it matter if I take power to the shop and then to the house, or do you have to go to the house first and then to the shop? The house will be around 1600 sq ft and no unique power needs. We'll have I guess "standard" HVAC, stove, water heater, dryer and well pump connections, so I guess 200A would do it. The shop won't be anything really unique either. It'll be about 1300 sq ft and I'll be running only 1 power tool at a time like a table saw or planer, or maybe 2 at a time like a dust collector while the tool is running. I would like to be able to run a 240v welder, but just a "standard" buzz box stick welder. It'll be just pretty much a "hobby grade" shop, not a commercial enterprise, so maybe a 100A deal? Maybe 40-60A would do it, I don't know. I *will* feed some stuff out to outdoor outlets, lights, etc for animals, coops, pens or whatever, but that probably won't be much of a draw. I'm a "one man show" so the odds of running anything much simultaneously that would overload the system is very doubtful. Ideally, I'd like to put a little utility building just inside my gate and then trench everything myself as I have time so I don't lose any more trees than I have to. If the power company brings the line in overhead, I think it's a 15-30' wide lane they have to have and I'd rather not cut that many trees down if I can help it. However, depending on how much they're willing to run for free versus what I have to pay for, that may sway that decision. :) If anyone can look at my map and at the power company sheet and tell me what I'm looking at, I'd appreciate it. I'll answer any questions I can. I'm not planning on doing this work myself, I'll be hiring an electrician, I just wanted to educate myself as much as possible before approaching the power company. The older I get (translation, the grumpier LOL) the less I'm willing to take what a single employee of any company tells me as "the gospel". I'm certainly not going to argue with a rep from the utility company, I'd just like to be able to bounce ideas off them if they only see "one way to skin a cat" if you will. Thank you.
View attachment AP Install Rates.pdf
/ Wiring house & shop #2
I'd personally stick with 100 amps to the garage. If you decide one day to get a plasma cutter, you'll appreciate having the margin to run a decent size air compressor at the same time as the plasma cutter without tripping breakers.
/ Wiring house & shop #3
In powering my property, I ran power to a Service base with an additional set of lugs for running power to another building so that both the shop and the house will share the meter.
I chose to install a 400 amp service as it really didn’t add all that much to the cost. I have a 175’ run from the junction box to the service entrance at the shop (all underground) and will have another 250’ or thereabouts run to the service entrance for the house. My planning is 200A shop (provisioned to spawn 100A to barn) and 200A for house.
/ Wiring house & shop #4
This must be a common trait here in Spokane, GSVette. I installed a 400 amp service with 200A to my cabin, which I call my shop, & 200A to the house. The last power pole is only about 8 feet from the cabin - that run is overhead.
Thank God, I listened to my neighbor - the run to the house( 80 feet) is buried and in heavy wall plastic conduit. It didn't show at that time - 1982 - but have later seen that I have a wonderful population of pocket gophers. My side yard looks like a practice field for the Army's light artillery brigade.
Yes - when I talked to Inland Power and Light - - they advised that 400A service would be not that much more than 200A
/ Wiring house & shop #5
I think I would go with GSVette's approach. I have an older house/barn and have 200 amp service, taking a 100 amp sub off to the barn. It works but I don't think I have any margin. If I upgrade to a 220v air compressor, welding and running the compressor at the same time could be iffy with surges and other normal loads. If I was building new, I would definitely go 400 with a 200 amp sub.
/ Wiring house & shop #6
NTG - - give an old fart a break. Please put paragraph breaks in future posts. I get lost.......... Thanks
/ Wiring house & shop #7
That sounds like a reading problem.:D
/ Wiring house & shop #8
You may be going at that backwards. Getting information on how others have done similar things is fine, but YOUR utility may have a certain way of doing things. At that distance of separation between the buildings, they may even require two separate services, meters and of course, bills. Best to get in touch with them before getting too deep in plans and options
/ Wiring house & shop #9
I believe you need to start by talking to the power company. They will offer suggestions, solutions and variables based on your location and costs. We may suggest methods that your power company will not do.
I'm in the midst of a build now. The power company went underground from the powerline to my site, 350ft. There they set a 400A transformer pad and meter setter. The setter contains two 200A disconnects. That cost me $1250.
My shop and house are close together with the meter setting sort of between them at the backside. Buildings are only 50ft apart.
I buried 4O wire in 2" plastic conduit using long sweep elbows to the shop. The shop has an outside conduit and elbow up about 6ft thru the wall into the back of the main breaker box. It's a 200A. The wire was expensive at $1.15 per foot times 3.
The house uses the same size/type of wire and conduit. Difference is it stays underground into the house.
This worked great for me. Was cost effective. Clean installation with no overhead to worry about. Both buildings on one meter.
Curious why you want your two buildings so far apart?
My current homestead has the two buildings 200ft apart. That's a hard trek in the dark when it's raining or snowing. I vowed this time to make it easier. I'm 67. When I'm an old man I want easy. :)
/ Wiring house & shop #10
Here's a pic of my transformer, meter setter in case you aren't familiar with them.
/ Wiring house & shop #11
you need at least #3 gauge for 100 amps, but that's at a maximum of 100 feet!. you need to go up one size larger wire for each 100 feet!.. at 470 feet, you need to go up at least 4 times the needed gauge, to prevent problems with wire heating and voltage drop!. unless, your power company will put a primary to secondary transformer near your intended shop!.. #2/0 wire.. "1 conductors per phase utilizing a #2/0 Copper conductor will limit the voltage drop to 4.26% or less when supplying 100.0 amps for 470 feet on a 240 volt system.
For Engineering Information Only:
175.0 Amps Rated ampacity of selected conductor
0.1 Ohms Resistance (Ohms per 1000 feet)
0.043 Ohms Reactance (Ohms per 1000 feet)
12.0 volts maximum allowable voltage drop at 5%
10.222. Actual voltage drop loss at 4.26% for the circuit
0.9 Power Factor
**Note to User:All ampacity values are taken from the Section of 310-15 of the NEC. The conductor characteristics are taken from Table 9 of the NEC. The calculations used to determine the recommended conductor sizes for branch circuits are based on 60°C ampacity ratings for circuits rated 100 amps or less or marked for use with #14 AWG - #1 AWG. Circuits rated over 100 amps or marked for conductors larger than #1 AWG are determined using 75°C ampacity ratings. Calculations to determine service and feeder conductor sizes are based on overcurrent device ratings rather than actual expected loads which are conservative and may yield oversized conductors. No calculations take into account temperature correction factors or conductor de-rating.
This voltage drop calculator is applicable only to NEC applications. It does not optimize conductor sizes for several different loads at various points in a circuit. The total combined load and length of the circuit must be used. Consult with an engineer if your application requires more complex engineering calculations. " Voltage Drop Calculator
/ Wiring house & shop #12
Overhead high tension to a transformer in the yard. Transfer switch for a generator right there. 200amp doesn't cost any extra and you will hate yourself for being cheap afterwards. All underground 120/240V to all buildings .
If you can't afford to do it right, don't do it at all.
/ Wiring house & shop #13
You missed the ground wires that join all electrical service box/breaker box ground lugs together to the same potential. Double ground rods at the meter base and at each breaker panel.
/ Wiring house & shop #14
I didn't realize I needed to be that detailed.
/ Wiring house & shop #15
No rush, but if you get a chance, I'd like to see the inside of your service box.
I assume it's 2 sets of lugs off one side of the Meter to allow for 2 separate 200A services.
This is exactly what I'll be faced with next Spring.
Will be building the Shop before the house.
And, for the OP, the cost to run the Primary from the road across private property to your Meter will vary big time from one area of the Country to the other.
I am on a Co-Op ....... to run overhead Primary it's $2 a foot. Underground is $5.25 a foot. And that my friend is CHEAP.
I'm lookin at needing them to bring in about 600' of Primary.
Closer to the "big city" with a different Electric Utility that cost for just overhead could be 5X that much or more.
/ Wiring house & shop #16
There have been several good suggestions so far;
I'm not sure if I would go with a 400 Amp service or just a 200 Amp with your projected usage it would depend on the cost.
I'm thinking AL. with trees,
I would bring the main in as a buried high voltage to a transformer between my two buildings,
I would have a transfer switch at that location rated for the full load and a main panel with my two or 3 sub feeds so I could have generator feed to either or both locations and I would have all buried deeply in conduit.
Just my way of thinking.
/ Wiring house & shop #17
I'll try to remember to get a pic tomorrow. Yep two disconnects side by side.
/ Wiring house & shop #18
If you have an electrician in mind you can run it past him. If he has worked in the area for a while he will have a good idea of what the Power company will allow, as well as suggestions on the most cost effective methods.
So I guess I'll approach the power company. I didn't know if it mattered if I went to the shop and then the house or the house and then the shop. I'm locating the buildings on the property based on road layout, physical lay of the land and based on where many other things will be located. My ignorance of electrical service may have introduced unseen problems here. Some days I feel like chucking the whole thing anyway. I appreciate everyone's advice. I'll try to get with the power company and report back what I find out.
/ Wiring house & shop #20
Go above ground to a pole at the barn. Then go underground to your house. Cheap and easy. And upgradable. Id recommend 200A each drop. You arent saving anything in the long run if you cheap out now and you will regret not putting in 200A when you had the chance.
Do you get ice and wind storms? Clear out the trees around the above ground portion up front. Stuff grows back faster than you will expect.
2007 International 7500 sba Flatbed 6x6 Truck (A62679)
2007 International...
2019 HYUNDAI V12530152-AJS 53' X 102" T/A VAN TRAILER (A59912)
2019 HYUNDAI...
John Deere 8245R (A64119)
John Deere 8245R...
2015 Ford F-350 4x4 Ext. Cab Pickup Truck (A61573)
2015 Ford F-350...
2019 Isuzu NPR 14' Box Truck (A62613)
2019 Isuzu NPR 14'...
2025 Kivel 48in Fork and Frame Skid Steer Attachment (A61572)
2025 Kivel 48in...