Square D Q0 200A Panel - how to convert to sub panel (separate neutral / ground bars)
   / Square D Q0 200A Panel - how to convert to sub panel (separate neutral / ground bars) #11
I did double up some of the #14 grounds into a single #12 green wire. I think that's ok? There were no 4 wire 240V circuits in the panel.
The ground is a safety feature. On 120v circuits it has to be able to carry the full breaker current of the circuit. A #14 wire can carry up to 15 amps, a #12 up to 20 amps. One #12 can't carry the current of two #14.
I'm also trying to figure out the thick aluminum ground conductor. It looks like it's going to neutral on both panels. Are either of the two panels we see the main service entrance, or are they subpanels? Ground and neutral have to be bonded at the main entrance and then separate everywhere else in the system. If these are subpanels that thick ground conductor has to go to ground, not neutral.
Originally both were main service entrance panels with a 400A meter base connected directly to both panels. I converted the one on the right to be a subpanel since it now has a Service Entrance rated transfer switch in front of it. The panel on the left is still a main service entrance panel. I'll pick up a large ground lug that will allow me to transfer that thick aluminum ground conductor to ground in the right side panel.
Thanks. I'll pick up both some #12 and #14 bare copper wire and wire every ground separately to the ground bar. I'll pick up another ground bar as it looks like I'll need to install another one to make everything fit.
If/when I transfer some circuits from the left service entrance panel to the right sub-panel, it looks like I'll have to extend all 3 wires from the service panel to the sub-panel. Just moving the breaker over and extending the hot won't cut it I don't think since the ground would then be connected to the combined neutral/ground in the left panel.
   / Square D Q0 200A Panel - how to convert to sub panel (separate neutral / ground bars) #14
On the newer panels, there is a green bonding screw that connects the neutral to ground. I'm not seeing that screw in your older panel. That said, for my QO subpanels, I had to install a ground bar just like you did. Looks like you have a dedicated ground (maybe a bit light on the gauge? I believe this wire should be a #6) and have the wire polarities taped, so the install is looking good to me. Do you have nolox on the aluminum ground wire?
   / Square D Q0 200A Panel - how to convert to sub panel (separate neutral / ground bars) #15
Most QO panels I have worked in have a spot for the ground bar to go in the panel. Look behind the wires near the top of the panel. If not why not just put the ground bars there? Panels are panels not junction boxes to make splices in. (It would fail inspection here with wire nuts used to continue the grounds).
Also if the right panel is now a SUB-PANEL it should not have a MAIN BREAKER it should be MAIN LUGS since the transfer switch has the main breaker.
I added another ground bar at the bottom and moved all the bare ground wires from the neutral bars to the ground bars. I also extended each one separately instead of having 2 #14's share a single #12.
I also added a small ground bar at the top side of the cabinet, where I terminated the 2 large aluminum ground wires.
Here's a view from the outside showing the meter base and transfer switch.
That is a #6 ground wire going to the grounding rod. #6 is what was there before. So I extended the original #6 from the grounding rod into the transfer switch and then run a new #6 from the transfer switch to the 200A sub-panel.
Not sure what you mean by wire polarities. I do have neutral taped white and the 2nd 220v feeder taped red. Do you mean that I should tape the 1st feeder blue like it is in the meter base coming from the power company as shown here? (you have to look close, but there is blue tape on that one wire running along the bottom up to the left most lug)
By nolox, do you mean anti oxidation paste? If so no, I only used that on all the 3/0 copper wire. There was none used before on anything.
I thought about that, but space is pretty tight at the top of the panel. If I fail inspection, I suppose I'll go back to do it that way after all. I would just to with one large horizontal bar in that case.
I agree that would be ideal, but I can't image the current setup failing inspection due to having one extra 200A main breaker. If I have to remove that 2nd main breaker, I'd probably need to custom fabricate some bars to carry the current from the main lugs to the bars.
   / Square D Q0 200A Panel - how to convert to sub panel (separate neutral / ground bars) #19
How did you delete the old feeder that you took out of the meter enclose ???
It was a huge pain. My original plan was to route the 3/0 copper through the opening between the meter base the the right panel. But once I got the old feeder removed from the meter base, I realized there was no conduit in the wall between the meter base and panel on the inside. So I then had to unbolt the inside panel as was the bared able to get to the set screws on the 2" clamp on the back. Once I got that loose, I was able to pull the old feeder through from the inside. I was lucky that the clamp on the meter base was not tight and I was able to pull the feeder through, although I had to pull on it hard to get it to go. Once I got it out, I mounted the panel to the wall again and installed a 2" plug in the hole.
I thought about installing a 2" conduit pipe in the wall between the meter base and panel, but after pulling out the old feeder, I realized that the existing hole was not 2" diameter but rather 3 smaller holes drilled next to each other, just large enough for that original feeder wire. So I had to get rent a core bit and drill and drilled a 2 5/8" hole in a new location, and then installed my 2" conduit for the new feeder wires to run through.
LEE G550 MOTOR GRADER (A51242)
LEE G550 MOTOR...
2021 FORD F-150 XL EXT CAB TRUCK (A51406)
2021 FORD F-150 XL...
2018 GENIE GTH-5519 TELESCOPIC FORKLIFT (A51242)
2018 GENIE...
2019 VOLVO VHD84F300 TRI-AXLE DUMP TRUCK (A51222)
2019 VOLVO...
(4) Texas Built 25' Stand Alone Panels (A50515)
(4) Texas Built...