It痴 interesting you would use my quotes that include the reasons why I would put a box in and then say their is no reason to use a box. Also note my response was in direct response to a question as to why I would use a box. Also note that my comments (including my first) reference what I would do. Not what anyone must do. In fact I point out that many will do it different ways!
You either didn稚 read the thread or you were mentally off when you did......so confused by your response.....
I did the same thing but I think I used 2 1/2", old electrician buddy said conduit is cheaper than replacing that wire, and in the event you ever do have to replace it the conduit already in place will be cheaper than a trencher rental.
The wiring to my horse barn I had to replace last year. I had used overhead triplex wire in conduit simply because I had it, it didn't last long. I first lost one leg and just lifted that leg on each end then when the other went I replaced it with direct burial. Being the conduit was already there it made it less than a hour job for my dad and I for a 150' run.
Please cite the section of the NEC that prohibits using UF in conduit.Putting direct burial wire in conduit de-rates the ampacity. Code does not allow it. Direct burial rated wire alone or conduit with THWN/THHN or XHHW wire are code.
Ron
Nothing about not putting it in conduit.https://www.electriciantalk.com/f5/nm-b-uf-cable-pvc-conduit-10655/ said:Article 340 UF Cable
340.10
Uses Permitted. Type UF cable shall be permitted as follows:
(1) For use underground, including direct burial in the earth. For underground requirements, see 300.5.
(2) As single-conductor cables. Where installed as singleconductor cables, all conductors of the feeder grounded conductor or branch circuit, including the grounded conductor and equipment grounding conductor, if any, shall be installed in accordance with 300.3.
(3) For wiring in wet, dry, or corrosive locations under the recognized wiring methods of this Code.
(4) Installed as nonmetallic-sheathed cable. Where so installed, the installation and conductor requirements shall comply with Parts II and III of Article 334 and shall be of the multiconductor type.
I have to somehow splice three pieces of 12 2 direct burial.does anyone know the least expensive way to do this?it will be buried about 2 foot in dirt and won't be live all the time.thanks
Thanks for the ideas. I have plenty of wire to work with on this. But there would be three wires all coming together so it would be difficult to use some of the less expensive ways.
This is where more information is better than less. Nowhere does it mention if this is a break/damage/repair or new installation. Nor does it mention is any of these three line are already in the ground and maybe one is being added.
The posts mentioning wires being 'too short' are thinking this is a break in or addition to existing lines. At first I thought it was about using three pieces of wire to make a new run, splicing them together end to end instead of a single longer piece. Now we see the bit about three lines coming together at a single point ('T' or 'Y' configuration). If that's the case, I would definitely use an underground rated box that I could open up later if necessary.
I prefer conduit whenever possible and practical for added protection from critters and tools. I don't see how it's possible to affect capacity ratings of any cable by using PVC conduit. Steel conduit ... maybe.
He also mentions it will be two feet deep, so a box extension won't accomplish much if he doesn't extend all three lines to the surface.