Home electrical help please.

/ Home electrical help please. #1  

ben2go

Gold Member
Joined
May 8, 2008
Messages
260
Location
Upstate, South Carolina,USA
My house lost partial power.Everything slowed down(fans),and the lights dimmed.At first I though it was a brown out, which I have never encountered before.I got up to go check the electrical panel and noticed,everything else in the house was working properly.So out comes the trust ole multimeter.Everything tests fine at 122v to 125v steady, except on two circuits.Circuit A has a string of eight lights and two outlets.With everything off/unplugged,I get 105v to 108v unsteady volts.Circuit B is a string of twelve outlets.I get 94v to 98v, unsteady,with everything disconnected.I checked all outlets in the house and some of the light fixtures.I got the same results.I manually operated the breakers to see if that would bring the voltage back up,it did not make a difference.These two breakers are on opposite sides in the electrical panel.One is on the bottom.The other is second from the bottom,and the circuit under it tests fine.The power comes into my panel from the bottom, but the electrical connections are at the top.What could the problem be?I am thinking bad breakers.I haven't tested the panel yet.I want to wait until I have better light tomorrow,so I don't fry myself.Oh,and I pulled out a few of the outlets, and tested them at the connections,same results,low voltage.
 
/ Home electrical help please. #2  
I'm thinking transformer at the pole. Is it hot where you are? I'd call the power company- unless you have Fed Pac breakers, but it sounds like the transformer to me.
 
/ Home electrical help please. #3  
Do you have anything that can short in the circuit like copper to aluminum?

I remember fondly how my brother excitedly showed me that he discovered why he was getting his bare feet shocked on his porch steps as he stuck his multimeter leeds into what I assumed was cat pee and measured 107 v.

<cue you might be a redneck if your brother….>
 
/ Home electrical help please. #4  
most main breakers boxes now a days every other circuit, comes off one of the 2 hots in the panel.
other words 1 side is 110v, and other side is the other 110v. but rather it alternates back and forth down the panel. which hot the breaker connects with ((more setup for 220amp breakers))
==from description you gave, 2 breakers, 1 on each hot in the panel is giving low voltage.

i am wondering if you have any metal electrical boxes, that these 2 wires might go through. say going through a box between switches and lights.

i have found mice and bugs inside fully inclosed electrical boxes (switches to outlets, to other) i have also found were a wire nut has came loose or a wire on a light switch or outlet has came loose.
--stuff were wires have came loose / nuts came loose = areas were family members "stoomp" there feet (heavy walkers) or kids bouncing around or the like.

===========
might suggest pulling breaker undoing the hot wire going to it. and then put breaker back in panel and test between breaker and neutral and see what you get. ((primarily testing breaker itself)) i would repeat with other breaker as well. if both check out. then you have an issue some place. and means pulling outlets switches, etc... and back tracing till you find the culprit. or wiring.
 
/ Home electrical help please. #5  
errr

These two breakers are on opposite sides in the electrical panel.One is on the bottom.The other is second from the bottom

just caught above. after posting. and confusion on my part of what you mean.


TOP..............TOP
left row....right row
9................9
8................8
7................7
6................6
5................5
4................4
3................3
2................2
1................1
BOTTOM...BOTOM

from your description you are stating ((left row 1, and right row 2?))
 
/ Home electrical help please. #6  
Where is your breaker box. is it in a dry place or is there a lot of humidity there? If so it might just be corrosion in the box.
 
/ Home electrical help please. #8  
Check the circuits for line leakage and then on to the breakers or do it vice/versa. Or, install new ground fault breaker. If it keeps tripping off there may be a circuit problem.

Note: not an electrician
 
/ Home electrical help please. #9  
Does turning one of the two breakers off have any effect on the other one?? It could be that a shared ground wire has a bad connection.
 
/ Home electrical help please. #10  
When you test you voltage, are you using the same common or ground for every test? If so, then I would remove the breaker and test the bar that the breaker attaches to just to make sure it's the proper voltage. If that tests properly, then disconnect the wire and put the breaker back on. Test the breaker at the attachment point of the wire. If that is low, it's the breaker, if it's correct, attach the wire and see if it changes. If it does, you have to keep working your way down the line to find the problem. My guess is that its either the breaker or the wire is loose that's attached to it. You might also check the common wire for that line and make sure it's tight.

Since all the other breakers test out fine, I think they are probably fine.

Do you have copper or aluminum wire as your main feed into the house? Sometimes aluminum needs to be re-tightened. It will also oxidize and cause problems if it's not treated. There is some stuff that you put on your aluminum ends to stop this, if it's not treated, it might give you issues.
 
/ Home electrical help please. #11  
Does turning one of the two breakers off have any effect on the other one?? It could be that a shared ground (grounded/neutral) wire has a bad connection.

This is what I 1'st suspected, except:
- You would tend to get an overvoltage on one leg (L1), and an undervoltage on the other (L2) that adds up to 220/240 volts. (- although I suppose, a loose connection could then cut this to the 206V (108V + 98V) that the OP measured.
- Hopefully his house doesn't have multiwire ciruits that share a neutral run from (2) single pole breakers (located on opposite sides of the panel.) This would be unlikely.

I'd still do the test, it can't hurt.

Check for loose breaker
I was also going to say check for loose connections. Do you have aluminum wiring? Have you had large loads plugged into outlets lately, like say an A/C? Has it been really hot there lately? - But if you measuring 98V right at the terminal of the breaker (and not just at a receptacle) then maybe this is not your problem.

If your measuring 98V at breaker terminal, turn off breaker, remove branch circuit wire from breaker, turn breaker back on and remeasure voltage at breaker terminal. If it's still 98V and all other breaker's are at 120V, then the breaker (or it's connection to the panel) is the problem and not the circuit wiring.

Edit: ^ Sort of the same thing EddieWalker said as I was typing this (but in reverse order).
 
/ Home electrical help please. #12  
Twice I have had a breaker fail down at my pier due to some insect that gets inside the breaker, then makes some sort of cocoon. Eventually it grows big enough to mess up the breaker.

I keep the breakers off until i need to use a circuit (one is 220V/20A for boat lift, and the other is 110V/15A for a receptacle).

The first time I heard sizzling noises when flipping the breaker, and the lever wouldn't close all the way. Replaced the breaker and tore it apart to discover why. I figured maybe I had worn out the breaker using it as a switch, but no, it was the darn insect inside! I think I posted a thread here on TBN.

The second time it happened in a 2-3 day period after I installed the new circuit for the receptacle and before the inspector was coming over. Right after install, it tested fine. I went down with my GFI tester a day later to verify the GFI tripped, and the lights indicated a fault. Lots of head scratching, as it just was fine a couple days earlier. Got out my voltmeter and was only seeing 90-95V on that circuit. Went around in circles a bit then tested the breaker to determine it was the problem. Replaced it, took apart the old one, and saw the same insect/cocoon inside. Anyhow, that's the point of my ramble, is that a bad or contaminated breaker can indeed give you low voltage on the circuit.

If this happens another time, I guess I need to figure out how to seal up the breaker box or breakers (the breakers all have a small air vent molded in them which I assume is important, but that's obviously how the bugs get in).
 
/ Home electrical help please. #13  
Some of the guy got close....

You have a loose neutral (the white wire). The cause is a bad connection. If it was only one circuit it could be in either the hot or neutral but since you have a problem with two it is in the shared neutral.

And yes I'm a licensed master electrician.....and a degree or two..but those may make me dumber....
 
/ Home electrical help please. #14  
Some of the guy got close....

You have a loose neutral (the white wire). The cause is a bad connection. If it was only one circuit it could be in either the hot or neutral but since you have a problem with two it is in the shared neutral.

And yes I'm a licensed master electrician.....and a degree or two..but those may make me dumber....

I had a loose neutral on an electric water heater once... That thing gave me fits .
Sometimes it would work , some times it wouldn't.
I finally found the loose connection in a junction box

You can get some screwed up volt meter readings with a bad neutral .
 
Last edited:
/ Home electrical help please. #15  
Some of the guy got close....

You have a loose neutral (the white wire). The cause is a bad connection. If it was only one circuit it could be in either the hot or neutral but since you have a problem with two it is in the shared neutral.

And yes I'm a licensed master electrician.....and a degree or two..but those may make me dumber....

Maybe...But it hasn't been established there is a shared neutral. And there shouldn't be one. ....if there was a shared neutral w/ a bad connection, you would tend to get an overvoltage on one of the circuit legs (L1) and an undervoltage on the other circuit leg (L2) that added together = 240 volts. [The voltage measured in each leg (in reference to the floating neutral, not the panel ground), would be determined by the impedance of the loads turned ON in each leg (i.e. With a disconnected/floating neutral, the loads on L1 & L2 are now in series with each other on a 240V circuit, instead of each being pegged at 120V to neutral/ground. The 240V is now split across L1 & L2 circuit loads in accordance with their impedance).] - A picture would do a better description than words.

What is interesting is he's doing these measurements with no loads turned on, i.e. no way for L1 and L2 to be in a 240V series circuit (which is what you'd have if you had a lifted neutral.)

He's also measuring 98V at the panel in reference to the panel ground, not at a remote receptacle in reference to a (floating/loose) neutral.

I hope the OP let's us know.

-...and that's my 2 cents :rolleyes:
 
/ Home electrical help please. #16  
Maybe...But it hasn't been established there is a shared neutral. And there shouldn't be one. ....if there was a shared neutral w/ a bad connection, you would tend to get an overvoltage .....


-...and that's my 2 cents :rolleyes:

It has been established by the facts he has presented. Also, you seem stuck on the 'overvoltage' thing, let me explain, he is measuring with everything unpluged. Also, I would wager and say both breakers are on the same phase.
 
/ Home electrical help please. #17  
It has been established by the facts he has presented. Also, you seem stuck on the 'overvoltage' thing, let me explain, he is measuring with everything unpluged. Also, I would wager and say both breakers are on the same phase.

...ok. Don't get me wrong, I'm not arguing, just kicking ideas around. Let's say they're the same phase, & he is measuring with all loads off or unplugged. Meaning there's no current, and without current, there's no voltage drop across a loose connection: so how do you get a reduced voltage reading anywhere, even at the breaker?

Even if they're not the same phase and the branch circuit's common neutral is lifted, you should still read 120V to (panel) ground at each breaker terminal as long as the panel ground is bonded with the transformers center tap. You just wont read 120V to (now floating) neutral.

Maybe we have to go back to Eddie's question: Is OP measuring voltage in reference to the same ground/neutral on every measurement?
 
/ Home electrical help please.
  • Thread Starter
#18  
I am doing this with all loads off the circuit.

I can't find any shared neutrals.They are all in their individual slots in the break box.Here is what I did today.I pulled every outlet,switch,and light fixture.Nothing obvious wrong and everything was clean and tight.So I went and bought one replacement breaker.I shut off the main breaker in the panel.I replaced the breaker that had the lowest voltage.When I went to turn the main breaker on,the little lever just flopped around as if it were connected to nothing.There was no resistance in the breaker lever.I shut the power off at the main disconnect outside at the power meter.So, I went and bought a new Siemens 100 amp main breaker and installed it.While I was at it,I cleaned all the terminals and sanded them lightly with fine sand paper.I also went through every thing in the panel checking for corrosion and tightening everything up.At this point I have a new main breaker and a new breaker on the lowest voltage circuit.All of the breakers in the panel are off.I flipped the main on, and reset the breaker with the lowest voltage,and I got nothing.So I kept resetting breakers, until I have power at the lowest voltage breaker.When I rest my 220v 20a water heater breaker,I all of a sudden have power to that side of the elec panel.This breaker is above four of the 120v breakers.When the water heater breaker is tripped,they all loose poser on that side.The thing is,my water heater has it's own circuit.Now I am completely stumped.

There is no aluminum wiring in this house.The main power feed,from the main shut off to the elec panel, is aluminum.Not my preferred choice but it was here when I got the place.
 
/ Home electrical help please. #19  
^^^^ Lets state a few of ohm's laws. 1. current is same measured anywhere in the circuit. 2. Voltage is different at each spot in a circuit, all voltage drop in a circuit equals the total voltage applied to the circuit i.e. 120V.

He is measuring voltage (pressure) not current (flow). You can have pressure and no flow.

The bad connection has resistance, the balance of the 120V is being dropped (used up) at the bad connection. This is why he is reading low at the places that should be a solid ~120.

All the low readings he has taken are at the outlets not the panel. If he measures between the breaker and a good ground he will get his 120. This is because he has removed the bad connection from the circuit he is measuring.
 
/ Home electrical help please.
  • Thread Starter
#20  
^^^^ Lets state a few of ohm's laws. 1. current is same measured anywhere in the circuit. 2. Voltage is different at each spot in a circuit, all voltage drop in a circuit equals the total voltage applied to the circuit i.e. 120V.

He is measuring voltage (pressure) not current (flow). You can have pressure and no flow.

The bad connection has resistance, the balance of the 120V is being dropped (used up) at the bad connection. This is why he is reading low at the places that should be a solid ~120.

All the low readings he has taken are at the outlets not the panel. If he measures between the breaker and a good ground he will get his 120. This is because he has removed the bad connection from the circuit he is measuring.

I am getting low voltage at the breakers.Around 94-98v at one and 108-112 at the other.It's also not steady and goes up and down a couple volts either way.
 

Marketplace Items

2019 Ford F-250 Knapheide Service Truck with Liftgate (A61568)
2019 Ford F-250...
2025 Unused SDLGC80 Electric Golf Cart (A60352)
2025 Unused...
2000 CATERPILLAR 988F WHEEL LOADER (A60429)
2000 CATERPILLAR...
22" PIN-ON EXCAVATOR BUCKET W/PINS (A60429)
22" PIN-ON...
2021 Kubota SVL75-2 Track Loader (A63118)
2021 Kubota...
Wacker Neuson RD12 (A57148)
Wacker Neuson RD12...
 
Top