help figuring steel needed for hoist/roof support

   / help figuring steel needed for hoist/roof support #1  

newbury

Super Star Member
Joined
Jan 8, 2009
Messages
14,845
Location
From Vt, in Va, retiring to MS
Tractor
Kubota's - B7610, M4700
I thought I posted about this a few years ago but can't find it.

I've got a 40x60 shop w/ 12' ceilings. It's presently got 2 support posts near the center. The posts are 4" x 3/8" angle iron 13.5' apart.
20141209_070837.jpg

Because of the possibility with this changing climate dumping 10" of snow on us I'm thinking of upgrading and making a support for a hoist at the same time.

I'd like to put up 2 posts adjacent to the 2 present posts with a beam running between them that I can hang a 2 ton hoist off. See red.

shed-hoist.jpg

I'd like to be able to lift about 2K off the back of my trailer or truck, so I don't need a Shield Arc 10K gantry. I'd probably "tie" them into the present posts.

So to TBN - either what's a good site to figure out what I need for steel (pipe, column, beams?) or suggestions for what I need?

As always price is a main concern.
 
   / help figuring steel needed for hoist/roof support #2  
2,000 lbs or 2 tons for the lift? Are you replacing the beam already there with another one? Are you setting new posts?
 
   / help figuring steel needed for hoist/roof support #3  
If you know your loads, this chart may help. ;)
 

Attachments

  • I-Beam chart1111.jpg
    I-Beam chart1111.jpg
    80 KB · Views: 220
   / help figuring steel needed for hoist/roof support #4  
I would just add another one or two beams to the one already there, looks like you have the room.
Then, wrap a tin sheathing around where the chain will be for your hoist.
I would also add the re-enforcements to the side's like you showed in your drawing.
Thats how mine is done.
 
   / help figuring steel needed for hoist/roof support #5  
I would 1st get the beam setting on the angle iron post, not hanging the way it is now. Then I would bolt 1/4 X the width X 13.5 feet of the beam on each side of it.
 
   / help figuring steel needed for hoist/roof support #6  
I've got a 40x60 shop w/ 12' ceilings. It's presently got 2 support posts near the center. The posts are 4" x 3/8" angle iron 13.5' apart.

I'm not sure, but I think using angle iron as a post is not good.
It has poor buckling strength.
Use round or square tube, or a W profile 'I' beam. Cement filled tubes "Lally columns" are good too, and available at most lumber yards.
 
   / help figuring steel needed for hoist/roof support
  • Thread Starter
#7  
2,000 lbs or 2 tons for the lift? Are you replacing the beam already there with another one? Are you setting new posts?
2,000 lbs is about the most I plan on having to lift.

If you know your loads, this chart may help. ;)
Thanks, nice to see you back. Always good to get advice from someone with 3 weeks of experience.
I would just add another one or two beams to the one already there, looks like you have the room.
Then, wrap a tin sheathing around where the chain will be for your hoist.
I would also add the re-enforcements to the side's like you showed in your drawing.
Thats how mine is done.
I was planning on 2 uprights, a crossbeam, and braces as indicated in red.

I'm not sure, but I think using angle iron as a post is not good.
It has poor buckling strength.
Use round or square tube, or a W profile 'I' beam. Cement filled tubes "Lally columns" are good too, and available at most lumber yards.
I was initially planning on Lally columns. These were Vestil FJB-150 Basement Floor Jack, 54" - 150" Height Range, Maximum Height Capacity (lbs.) 2588, Minimum Height Capacity (lbs.) 11200: Jack Post Bottle: Amazon.com: Industrial & Scientific an inexpensive one I found.

What sizes/thicknesses would be needed for either tube or I beam? Or is there a site with a handy calculator to help me work it out?

Like I indicated I planned on putting braces to support the crossbeam so it didn't span as much.

Again, thanks for all the replies.
 
   / help figuring steel needed for hoist/roof support #8  
Thanks, nice to see you back. Always good to get advice from someone with 3 weeks of experience.
Thanks!;):thumbsup:
When I built my bridge crane. I designed it, sent Auto-Cad drawings to the head of the engineering department of the company we worked for, so he could tell me what size iron to use. I told him I planned on use 4-inch schedule 80 pipe for the posts. He said he wouldn't even waste his time figuring the loads for that pipe, it was way over kill. I ended up using the pipe in the four corners, but used 8" x 8" x 1/2" wall square tubing for the two center posts. Hey when you get the iron for free, you use it.:D
 

Attachments

  • Span Beam 28.JPG
    Span Beam 28.JPG
    240.8 KB · Views: 687
  • Connection.jpg
    Connection.jpg
    40.1 KB · Views: 171
   / help figuring steel needed for hoist/roof support #9  
OK - first of all never ever come here for advise on safety issues. This entire site is full of misinformation. GET A PROFESSIONAL do the correct calculations. Why come here for advise by a bunch of YAHOOS ( including me ) You want proof, simply looking at some random " CHART" is the most dangerous thing you could do. What about Working Load Limits, Proof Load, Breaking Strength/Ultimate Strength, Design Factor (sometimes referred to as safety factor)....and then there is the thing NO ONE talks about Shock Load. ........A load resulting from rapid change of movement, such as impacting, jerking or swinging of a static load. Sudden release of tension is another form of shock loading. Shock loads are generally significantly greater than static loads. Any shock loading must be considered when selecting the item for use in a system. That simple little math calculation can take 2,000 pound and make it 8,000 pound.
So would you put a loved one under a 2,000 pound load with a cable rated at 3,000 pound and a shock load of 8,000 pounds - take a guess what will happen.
YOU WILL KILL SOMEONE
Now do the right thing and get a professional engineer do the calculation as it related to rigging etc., safety is not one thing you can ever save money on. Do it right or you will kill someone.
 
   / help figuring steel needed for hoist/roof support #11  
Cat_Driver nailed it. There are those of us who have had structural steel classes and those who have not. I do not have my license though. Much of that design knowledge is rusty in my head but I still have the books and would not hesitate to build something myself or criticize someone else's work/numbers. Any critical structure or device which has the potential to hurt someone should be reviewed by a professional who has experience with steel design.

Everyone likes to throw up a beam table from the internet and say that will work. What the uneducated/uninformed don't realize is that there is more than one failure mode that must be accounted for when designing with steel. IIRC there is around 7 of them? (Someone can correct me on this if need be but its more than 1 or 2) The simplest solution to these failures is to over estimate/oversize everything and a lot of the problems go away as long as weight/cost isn't a concern. While a single beam this might be a solution but its cost prohibitive on a larger scale and why structures must be designed by professionals and certified as such. [/rant]
 
   / help figuring steel needed for hoist/roof support
  • Thread Starter
#12  
With travel time to and from my site I doubt I could get an engineer w/ credentials to design something for less than $500 to $1,000 they don't work for free.
A quick check online shows I can buy a mobile gantry crane with the approximate dimensions I need for about $1,400 http://www.hoistsdirect.com/shop/1992#tab1 w/o shipping.
I'm not building a complex structure.

It's getting so every thread on here recommends hiring a professional for anything.
 
   / help figuring steel needed for hoist/roof support #13  
newbury that chart I posted above. I found that on a gantry crane web site. So those are point loads in the center of the span. They are not allowable uniform loads. Generally points loads are about half of uniform loads.

Here is a chart for W shapes, they are stronger than S shapes. They do sell trolleys that will run on the flange of a W shape.
 

Attachments

  • Wide frlange 3.jpg
    Wide frlange 3.jpg
    76.7 KB · Views: 118
   / help figuring steel needed for hoist/roof support #14  
......
What sizes/thicknesses would be needed for either tube or I beam? Or is there a site with a handy calculator to help me work it out?
I don't know. I just had to point out that using angle as a post is a bad idea. If you took the same amount of steel, and made it into a tube, it would withstand higher loads. But how much load? Or what wall thickness/diameter would be best? I haven't a clue.

That's what engineers are for.
I am not an engineer.
 
   / help figuring steel needed for hoist/roof support #15  
I am a registered Professional Engineer and I'm not going to get into trying to design this thing because I'm not sure I fully understand the configuration. However, let's not get carried away. 2000 lbs (1000 lbs per post) is not much. My 4x6 pole barn posts carry about 6 times that under snow load and I'm sure they have all kinds of margin.

The post above that angles make bad posts is correct. Angles are good for members in structures but posts should be closed forms (tubes or pipes) to give equal buckling resistance in all directions. If I was doing this and was sure I wasn't going to exceed 2000 lbs, I would seriously consider wooden posts. In any event, make sure you have appropriate bracing to keep it from buckling or folding. (And don't stand underneath when lifting.)
 
   / help figuring steel needed for hoist/roof support #16  
With travel time to and from my site I doubt I could get an engineer w/ credentials to design something for less than $500 to $1,000 they don't work for free.
A quick check online shows I can buy a mobile gantry crane with the approximate dimensions I need for about $1,400 Vestil FHS-4-15, 2 Ton, Fixed height Gantry Crane, Height 10', Span 15' | HOISTS DIRECT w/o shipping.
I'm not building a complex structure.

I would buy the crane in a heartbeat and be done with it. A gantry on wheels has so many advantages over a fixed crane it is hard to count them. But the big deal is the crane can move to the truck so a lot of possibilities open up. Plus, the maker of the crane has done the engineering and is responsible for it.

If I were doing it, I would spend a little more and get a 4,000 lb crane, or maybe even higher. Match the crane to the cargo capacity of the truck. If you want to lower the span, this reduces costs and makes it easier to rate the crane for a higher load. I don't know what you are planning to move, but anything that is 15' wide and only 2000 lb is a very strange load.
 
   / help figuring steel needed for hoist/roof support
  • Thread Starter
#17  
With travel time to and from my site I doubt I could get an engineer w/ credentials to design something for less than $500 to $1,000 they don't work for free.
A quick check online shows I can buy a mobile gantry crane with the approximate dimensions I need for about $1,400 Vestil FHS-4-15, 2 Ton, Fixed height Gantry Crane, Height 10', Span 15' | HOISTS DIRECT w/o shipping.
I'm not building a complex structure.
I would buy the crane in a heartbeat and be done with it. A gantry on wheels has so many advantages over a fixed crane it is hard to count them. But the big deal is the crane can move to the truck so a lot of possibilities open up. Plus, the maker of the crane has done the engineering and is responsible for it.

If I were doing it, I would spend a little more and get a 4,000 lb crane, or maybe even higher. Match the crane to the cargo capacity of the truck. If you want to lower the span, this reduces costs and makes it easier to rate the crane for a higher load. I don't know what you are planning to move, but anything that is 15' wide and only 2000 lb is a very strange load.

I wrote I needed to lift 2,000 lbs max and the 13.5 foot width I'm trying to deal with is present post spacing. This would let me span my trailer and lift something off to the side.

And the link I posted was for 2 ton rated crane, should I look instead for a 4,000 lb rated crane. :)
 
   / help figuring steel needed for hoist/roof support #18  
I wrote I needed to lift 2,000 lbs max and the 13.5 foot width I'm trying to deal with is present post spacing. This would let me span my trailer and lift something off to the side.

And the link I posted was for 2 ton rated crane, should I look instead for a 4,000 lb rated crane. :)


2 Tons = 4000 lb.

When taking a load off a vehicle, the typical method is to lift it and drive the vehicle out from under the load.
 

Marketplace Items

DRAGON 500 BBL ACID TANK (A58214)
DRAGON 500 BBL...
2004 JOHN DEERE 160C LC EXCAVATOR (A59823)
2004 JOHN DEERE...
1999 Wallace Trailers Tri Axle Low Boy Equipment Trailer (A59230)
1999 Wallace...
2016 JLG T350 TOWABLE BOOM LIFT (A60429)
2016 JLG T350...
2013 Ford E-350 Cargo Van (A59230)
2013 Ford E-350...
2022 RAM 2500 HEAVY DUTY (A55745)
2022 RAM 2500...
 
Top