The welder circuit breaker should be 50 amps, and smallest wire size (copper) should be 8 awg. Do you have 8 or 6 awg wire off of that 60 amp circuit breaker? If you are using 8 awg the breaker will have to be changed to a 50.)</font>
My copy of the NEC requires #6CU for a general 50A branch circuit.
There are some exceptions which might allow an #8 conductor
to be used but they are special cases a of single conductor
in free air, alone in a conduit, buried, etc..
The issues are minimizing the temperature elevation of the
conductor's insulation and minimizing voltage drop. The
former is to prevent breakdown/melting of the insulation and
the later is to minimize the voltage reduction seen by the
load which should be within 5% of nominal from all sources
combined.
That said the NEC is assuming continuous worst case full
draw off the branch circuit where an AC buzz box maxes out
to 20-40% duty cycle drawing its full load of 45-50A. So
you could 'get by' with a lighter gauge particularly for
short cable lengths and/or for newer inverter welders which
can compensate for excessive voltage drop. But if you are
making it part of a structure, it would be wise to follow
code.
The welder circuit breaker should be 50 amps, and smallest wire size (copper) should be 8 awg. Do you have 8 or 6 awg wire off of that 60 amp circuit breaker? If you are using 8 awg the breaker will have to be changed to a 50.)</font>
My copy of the NEC requires #6CU for a general 50A branch circuit.
There are some exceptions which might allow an #8 conductor
to be used but they are special cases a of single conductor
in free air, alone in a conduit, buried, etc..
The issues are minimizing the temperature elevation of the
conductor's insulation and minimizing voltage drop. The
former is to prevent breakdown/melting of the insulation and
the later is to minimize the voltage reduction seen by the
load which should be within 5% of nominal from all sources
combined.
That said the NEC is assuming continuous worst case full
draw off the branch circuit where an AC buzz box maxes out
to 20-40% duty cycle drawing its full load of 45-50A. So
you could 'get by' with a lighter gauge particularly for
short cable lengths and/or for newer inverter welders which
can compensate for excessive voltage drop. But if you are
making it part of a structure, it would be wise to follow
code.