bnixon,
Just put a lincoln buzz box in yesterday thats been sitting around here for years. Sounds like you're having a time of it. The posts so far have pretty much covered your situation, and I guess I just wanted to add my .02.
The welder circuit breaker should be 50 amps, and smallest wire size (copper) should be 8 awg. Do you have 8 or 6 awg wire off of that 60 amp circuit breaker? If you are using 8 awg the breaker will have to be changed to a 50.
The neutral is not required for the lincoln (no 120v requirement) but the ground is required. Is a bare wire from the cable connected to the neutral bar at the house panel? If so, that is your ground wire. The neutral would not be needed if the ground wire is connected. I ran 8/3 w/ ground (black/ red/ white/ bare wire ground) and capped off the white neutral wire at both ends in case it was needed in the future. If the ground wire was cut off, and the white wire is being used as the ground, at least tape it green at both ends to identify it properly.
Regarding the disconnect: the disconnect is required but to have a fused disconnect is not if the circuit breaker feeding it is properly sized for the connected load. In your case the breaker supplying it is larger than the fuse requirement for the machine (referring to the 60 amp breaker at the house panel). The lincoln requires a 50 amp fuse or breaker so if a 6 awg feed with a 60 amp breaker was installed to the welder disconnect the disconnect should have 50 amp dual element time delay (FRN) or equivalent fuses. The cable from the house panel should have a bare wire connected to the ground lugs on the disconnect. Make sure that the lugs installed to the left side of the disconnect are connected to the box electrically (almost looks like a neutral kit is installed instead of a ground kit). The lugs should be screwed right to the metal of the box, not sitting on an insulated stand. Everyone is right on wiring the disconnect; the way it was wired the bottom fuse clips would be hot when you changed the fuses, which could make life a little exciting if you grabbed one, even with the disconnect off.
The Federal Pacific house panel should be replaced. They are a fire waiting to happen should you have a short on a branch circuit and the breaker doesn't trip. The aluminum wiring in the house is also a concern. If you make any connections using that aluminum wire MAKE SURE that you use noalox so that the aluminum connection doesn't corrode and start a fire.
Last but not least it sounds as if you are confused about the use of grounds and neutrals. The neutral wire (in your case the white wire) carries current when a device is connected to one of the incoming phases (the black or red in your case). The ground wire is normally not a current carrying conductor and connects to the chassis of most appliances. If the ground wire was not hooked up on your welder and one of the hot phases contacted the chassis, it would not have a shorting path to trip the breaker and would electrify the housing of the welder. If you touched it and provided a ground path............................ , well you know what would happen /forums/images/graemlins/blush.gif /forums/images/graemlins/blush.gif /forums/images/graemlins/blush.gif.
Just do yourself a favor and be very careful. When working in a hot box it is best to be careful to not provide a grounding path through you. Wear good insulated shoes, never put one hand on a possible ground path (box, water pipe, appliance, etc.) and work in the box with the other, and check to make sure EVERYTHING is off before doing any work. It only takes one time, you know.
Hope this helps.
DaveL
Just put a lincoln buzz box in yesterday thats been sitting around here for years. Sounds like you're having a time of it. The posts so far have pretty much covered your situation, and I guess I just wanted to add my .02.
The welder circuit breaker should be 50 amps, and smallest wire size (copper) should be 8 awg. Do you have 8 or 6 awg wire off of that 60 amp circuit breaker? If you are using 8 awg the breaker will have to be changed to a 50.
The neutral is not required for the lincoln (no 120v requirement) but the ground is required. Is a bare wire from the cable connected to the neutral bar at the house panel? If so, that is your ground wire. The neutral would not be needed if the ground wire is connected. I ran 8/3 w/ ground (black/ red/ white/ bare wire ground) and capped off the white neutral wire at both ends in case it was needed in the future. If the ground wire was cut off, and the white wire is being used as the ground, at least tape it green at both ends to identify it properly.
Regarding the disconnect: the disconnect is required but to have a fused disconnect is not if the circuit breaker feeding it is properly sized for the connected load. In your case the breaker supplying it is larger than the fuse requirement for the machine (referring to the 60 amp breaker at the house panel). The lincoln requires a 50 amp fuse or breaker so if a 6 awg feed with a 60 amp breaker was installed to the welder disconnect the disconnect should have 50 amp dual element time delay (FRN) or equivalent fuses. The cable from the house panel should have a bare wire connected to the ground lugs on the disconnect. Make sure that the lugs installed to the left side of the disconnect are connected to the box electrically (almost looks like a neutral kit is installed instead of a ground kit). The lugs should be screwed right to the metal of the box, not sitting on an insulated stand. Everyone is right on wiring the disconnect; the way it was wired the bottom fuse clips would be hot when you changed the fuses, which could make life a little exciting if you grabbed one, even with the disconnect off.
The Federal Pacific house panel should be replaced. They are a fire waiting to happen should you have a short on a branch circuit and the breaker doesn't trip. The aluminum wiring in the house is also a concern. If you make any connections using that aluminum wire MAKE SURE that you use noalox so that the aluminum connection doesn't corrode and start a fire.
Last but not least it sounds as if you are confused about the use of grounds and neutrals. The neutral wire (in your case the white wire) carries current when a device is connected to one of the incoming phases (the black or red in your case). The ground wire is normally not a current carrying conductor and connects to the chassis of most appliances. If the ground wire was not hooked up on your welder and one of the hot phases contacted the chassis, it would not have a shorting path to trip the breaker and would electrify the housing of the welder. If you touched it and provided a ground path............................ , well you know what would happen /forums/images/graemlins/blush.gif /forums/images/graemlins/blush.gif /forums/images/graemlins/blush.gif.
Just do yourself a favor and be very careful. When working in a hot box it is best to be careful to not provide a grounding path through you. Wear good insulated shoes, never put one hand on a possible ground path (box, water pipe, appliance, etc.) and work in the box with the other, and check to make sure EVERYTHING is off before doing any work. It only takes one time, you know.
Hope this helps.
DaveL