grsthegreat
Super Star Member
All good answers .
120V only at the barn is not going to save time, money or effort. And someday, somebody will curse you for not running 240V. Run cable inside conduit. Barn will require two ground rods or a ground plate buried 8ft or deeper. Run bare number six copper to the barn's ground bar and also tie it to the bare ground wire pulled in from the house.
As stated numerous times before . The neutral bar in the barn panel must float isolated from the barn's ground.
Under 100 amps only 1 ground rod is required. Good catch about separating grounds and neutrals. I forgot to mention that. Remember to run 3 wires for 120 or 4 wires for 240 volt systems.