Electric Motor Starters
/ Electric Motor Starters #1
Toolguy
Platinum Member
West Michigan
B3030
I recently found a deal on a used 3HP heavy-duty air compressor. I have it hooked up in my shop now and it works OK buts it really draws the amps when starting. I may not have enough electrical capacity to run it the way it should. While running it draws about 18 amps on both legs and the voltage is good at 115 to 118. However, when it starts up it draws 68 amps and the voltage drops to 104 momentarily. The 20A breakers do not trip. This seems excessive to me and I am worried that this might hurt the motor over the long haul. I know that magnetic or capacitor starters are needed on some motors. Does anyone know if a starter of some type would help? I have 125ft of 8ga wire running from my main electrical panel to the breaker box. From there it is another 50ft to the compressor. I only have 12ga wire from the breaker box to the compressor but I ran a parrallel set of 12ga wire to the compressor as a test to see if it made a difference with more wire capacity. It did not change the amp and voltage readings. I am stumped at this point. Any help would be greatly appreciated. Thanks.
P.S. The compressor has an unloader so it is not starting under pressure. It does have a huge cast iron pulley/fan on the pump. I am thinking it probably draws a lot of power to get that thing turning.
/ Electric Motor Starters #2
inrush currents are normally 2~3 time the running current on any motors. SO I'd say you are probably OK if it is only a 3~5 seconds of start up. Otherwise a start capacitor may be needed. that does not mean that the motor was designed with this in mind. most motors that are designed for them have end switches that spin up and disengage the cap others use 2 caps a start and a run cap. these are heavy duty applications like compressors which need a LOT of torque. this is the application you should probably have. anyhow if it was one you had no big deal go with it & hope it lives a long & happy life...
mark M
/ Electric Motor Starters #3
The voltage drop and current while starting is OK. However, a circuit should not exceed 80% of its rated current for continuous operation. For a 20 amp circuit this would be 16 amps. I would change to 10 guage wire and a 30 amp breaker for that unit. You cannot use paralleled wire permanently. This should also help with voltage drop while starting at least a little. The short time that the high current and low voltage occur will not damage the motor.
What else are you running on this 8 guage wire. If you have a lot of other loads then the voltage will be lower to the compressor while they are running. You should test running voltages while running your other loads if you plan to run them while running the compressor.
The only other draw on the 8ga wire is a few flourescent lights and my wall outlets. When all the lights are on there is a 2 volt drop. I rarely have them all on at the same time and the wall outlets are used very little as well. When I get around to it I think I will upgrade the wire to 10ga and change the breakers to 30a just to have a little margin of capacity.
This compressor will not get used very much. I had a single stage, light duty 4hp compressor for years. The main reason I changed was because it took forever to put air in my truck tires which require 110psi. That is near the upper limit for a single stage compressor. The regulator was set at 95psi on and 120psi off. In order to get 110psi in the tires the compressor would have to be running. So for every tire I would have to bleed the air off to get the compressor to turn on and then hold the inflator on the valve stem until the compressor shut off. Not a very time efficient way of doing things.
The other reason I changed is because I stumbled across the new compressor for only $300. I have already sold my old one for $265. The new (to me) compressor is old but is in good condition. The motor seems to be newer than the compressor as it is a different color. The compressor shows some signs of having been apart before so perhaps it was rebuilt at some point in it's life. When I got it it was set to turn on at 155psi and shut off at 175psi. I have it turned down to 120-140. That is more than enough pressure for my needs. Running it higher is just a waste of electricity.
Thanks for all the help, guys.
/ Electric Motor Starters #6
Ok, dumb question! I am almost certain that the motor can be wired for 230 volts, so why don't you change it for the higher voltage and put it on a double pole breaker? To the best of my knowledge, all single phase motors rated a 1/2 hp or greater are dual voltage, so this should be your first option.
This will literally drop your amps in half, and the motor will also start faster. Plus, although you don't run it that much, it will cost less to run because the load on you meter will be balanced.
Changing the voltage should be as easy as switching two or possibly four wires, and there should be a diagram either on the motor plate itself, or under the cap that covers the wire terminals.
/ Electric Motor Starters #7
Up that 50 foot run to 10AWG should help.
/ Electric Motor Starters #8
I'm thinking it already is wired 240V. A single phase 3HP motor connected at 120V will pull 34A. Besides he said it draws about 18A on both legs.
/ Electric Motor Starters #9
You may well be right, though that 34 amp rating assumes full load which he isn't under. He said he has 120 volt, that drops down as the motor starts, so that is what I based it on. I assumed he was measuing it across both terminals, not one terminal to ground. And a 120 volt motor will draw the same amps on both legs also, they will just be twice as much as for a 240 volt motor.
Based on what he wrote, it sounds like his motor is 120 volt, and lightly loaded at 18 amps, probably because he is set the pressures way down from their possible maximum and possibly because the motor may be larger than necessary or geared down to reduce the load.
The motor is 240 volts. Three wires. Two 120 volt. One neutral. Just FYI. Thanks.
/ Electric Motor Starters #11
Ok, then you really shouould upgrade your wire and and breaker sizes. As mentioned, a 20 amp breaker shouldn't be loaded at more then 80% capacity for any time more than a few minutes. Doing so will tend to weaken it and cause it to eventually trip too soon. Also, although you are within the #12 wires rating of 20 amps, if you increase the breaker size, then the #12 wire is too small. A heavier wire will result in lower operating costs due to lower voltage drop over time.
/ Electric Motor Starters #12
From what you said, it sounds like you think you have the motor wired for 240VAC (2 legs?). 3HP and 240VAC equals about 11 amps and 120VAC would be 23 amps full load. So, either you are wired for 120VAC or you are overloaded. In either case, something needs to change. Either increase the wire and breaker size for 120VAC, or wire for 240VAC.
If in fact you are wired for 240VAC and still drawing 18amps steady state you have a problem:
the motor is failing either electrically or mechanically
the motor is undersized for the application
the compressor is failing
your meter is reading incorrectly
FYI, balancing the load through the meter has no effect on your power bill. You are charged for the energy you consume regardless of the configuration. Some will argue about line loss at higher current, but it is negligable in a home setting.
/ Electric Motor Starters #13
Gizmo, I did the math and my numbers come out close to yours. On the other hand I have a 1.25 horsepower well pump which is rated at 9 amps at 240 volts. So I think we are not accouting for inefficiences and power factor enough. He should look at the name plate for the ratings not use our calculations.
/ Electric Motor Starters #14
My pocket book, that I often use in the field if a motor nameplate is ineligible or missing, says 17FLA/230V/3hp.
/ Electric Motor Starters #15
rotory phase converter and replace that single phase beast with a 3 phase.
/ Electric Motor Starters #16
:rolleyes:
Here are some pictures of the compressor and the motor plate. The quart of oil in the picture is just there to give it some size comparison.
Today, I changed the 20amp double breaker to a 30amp. The 20amp breaker kept tripping when I tried to start it this morning. No problem tonight with the 30. As soon as I get time I am going to change the 12ga wire from the breaker box to the compressor to 10ga. This compressor will not be used on a regular basis. Unless I have problems after that I am going to leave it alone. So far, it is doing what I want it to do. Thanks for all of the good advice.
/ Electric Motor Starters #18
You need to change wire size to at least 10 guage.
/ Electric Motor Starters #19
Couple of questions if your still looking for answers, if you can take the belt off and just run the motor unloaded, what does it draw for current? With the belt on and starting from no air pressure in the tank, what does it draw say up to 20-30psi? Same thing except starting from 120psi, what is the draw? Are there capacitors in the motor junction box? If so, what are the values on them? If the starting cap is weak, you'll get less starting torque, if the run cap is weak you'll have less power and higher current. Just my two cents.
Steve
Actually, If I would not have checked the amps when I first installed it, you would never suspect that anything is unusual. When it kicks on at 120psi it only takes about 1 second, or less, to get up to full speed. The only thing noticeable is that the lights flicker. With my old, smaller compressor the lights never changed when it started. The flickering lights are what got my attention so I got out my digital, clamp-on amp meter. It is possible that the meter is wrong, though. When I get the chance I'll borrow a different one and compare. I am going to change the wire to 10ga and call it good for now. Thanks again.
LILLISTON 4R ROLLING CULTIVATOR (A63291)
LILLISTON 4R...
2022 Bautista Welding and Custom 40ft. 10 Ton T/A Gooseneck Flatbed Trailer (A61573)
2022 Bautista...
2000 Mack CH613 Dump Truck (A59213)
2000 Mack CH613...
JLG Scissor Lift (A64047)
JLG Scissor Lift...
2025 Unused SDLGC80 60v Electric Golf Cart (A64194)
2025 Unused...
Rotary SPOA9-200 Automotive Lift (A59228)
Rotary SPOA9-200...