Breaker rating

   / Breaker rating #1  

CTyler

Veteran Member
Joined
Dec 20, 2002
Messages
1,553
Location
Blair, Ne.
Tractor
L3130
I just need a sanity check....

A 30 amp double pole breaker means that each leg can handle
30 amps right?

I had a new water heater installed in one of my rental units a while back. Friday it started tripping the breaker after being reset. I bought a new 30 amp breaker and checked the amps and it was pulling ~18amps a leg. Still running ok so far.

Thanks
Chris
 
   / Breaker rating #2  
The breakers will wear out and will have to be replaced, just as you have done. Maybe someone here can explain why.
 
   / Breaker rating #3  
The bi-metallic strip which is responsible for "tripping" the breaker as it distorts from the increased heat due to the larger current passing through it sometimes loses its shape and trips at lower current or amperage amounts then that listed on the breaker. Typically, a circuit breaker is designed to reliably hold any device for a continuous load rating of no more then 80% of its rated capacity. My guess is the old heater was heating up the old breaker.
 
   / Breaker rating
  • Thread Starter
#4  
Thanks for the info.

To close....
I went and looked it up and the breaker should handle 13,200 watts or 30 amps a leg. This matches up with the 10 gauge wire. I figured as much, just wanted that last 1% of confirmation.
 

Tractor & Equipment Auctions

2008 Komatsu WB146-5 (A47477)
2008 Komatsu...
2019 Allmand Night-Lite V-Series 7kW S/A Towable Light Tower (A52377)
2019 Allmand...
ATLAS XAS110 COMPRESSOR (A52472)
ATLAS XAS110...
2018 JLG 1644 4x4 15,600lb High-Capacity Rough Terrain Telehandler (A52377)
2018 JLG 1644 4x4...
2009 Trail King TK110HDG-523 RGN 66 Ton Tri-Axle Lowboy Trailer (A52377)
2009 Trail King...
2007 Ford Focus Hatchback (A54815)
2007 Ford Focus...
 
Top