How low is low ? A starting point is typically ambient x 2.2~2.5 in F. (for high side) assuming the charge is correct. *** Did the compressor fail ? Why did it fail ?
If i"m in to it, I look at an oil sample. Is it metallic / dark / discolored / contaminated ? If so, compressor likely circulated trash through the system including your txv . Evap core and lines should be flushed individually. Any muffler (if present) can't be flushed. Condenser can be pulse flushed with specialized equipment but not worth the investment unless you do this often. So you will be buying a condenser too. You have to be SURE all solvent is out before charging. Unfortunately no free lunch here. Taking short cuts usually results in the new compressor failing in a few months. Parts and labor... you can see why a/c costs $$$. 1234yf (the new refrigerant is worse) :banghead: