Recent content by alexinPA

  1. A

    Checking filled tires pressure

    In similar thread many years ago))it was recommended to jack up the tire and turn valve on top at 12
  2. A

    Question for electricians

    Thank you! I'll try that
  3. A

    Question for electricians

    The setup is: -Power box is plugged in 50 amp generator outlet -Cable from power box plugged in wall outlet connected to 50 amp circuit breaker in the panel. -There is manual interlock kit installed so generator serves whole house
  4. A

    Question for electricians

    There's no owner manual
  5. A

    Question for electricians

    Not sure what it all means. To clarify, the voltage reading on power meter is ~120 volts all the time. Does it mean wattage I see is half of actual? The generator screen shows 240 v. How can turning on a ceiling fan can reduce total watts? And this is the only one appliance that does it.
  6. A

    Question for electricians

    Tested the power meter this morning. Works fine showing W, A, F. Even catches the surges. Interesting to see how actual W are different from tables provided. One thing I can't explain... My generator is running with low load-about 60w. Turning on ceiling fan and see 2w. Tried a few times. How...
  7. A

    Gas Shutoff's

    I buy regular gas at brand name gas stations only. Add marine Stabil in all engines and never had any problem. Even when some equipment not in use over a year
  8. A

    Question for electricians

    Thank you all for your help! I decided to give it a try and placed the order. Next gen maintenance run I'll test it turning on and off appliances one by one and make a list of wattage/amps. After that I don't need this device to be connected all the time
  9. A

    Question for electricians

    The title says 9 awg (see picture) but description says 10
  10. A

    Question for electricians

    I was watching my counter installed by PPL. It's one of those remote controlled showing different values, incl. kwh, kw, etc. Kw value is cumulative so every night it shows max for a day. Next day it starts over. For a week with AC on never above 5200-5600 w. Wondering if this meter catches...
  11. A

    Question for electricians

    Generator is connected to 50 A breaker
  12. A

    Question for electricians

    Yes, my plan is to use an enclosure. But still worry about 10 awg cable. And I didn't like seller reply about short length/low resistance good for 50A
  13. A

    Question for electricians

    Generator cable is 6 awg. I know things like electric water heater is no go
  14. A

    Question for electricians

    Spec says UL approved
  15. A

    Question for electricians

    You read my mind ! That is exactly what I want to do. Thank you.