More backup generator discussion: Backing up well pump in a different structure

   / More backup generator discussion: Backing up well pump in a different structure
  • Thread Starter
#41  
How about a simple automatic transfer switch that only feeds the well? Normal power comes from the old house and when the power goes out the transfer switch switches to a circuit off the generator.
You won’t need any of the gen start features in the transfer switch as that will be handles by the “main” transfer switch.
I’ve never done this nor have I studied code enough to see if an isolated circuit can be fed by a separate service entrance. But if that’s truly code this would be a work around that I assume would meet code.
If code isn’t an issue (and I don’t think it is) I’ll stand by my first thought in one of the first posts in the thread.


I think, from what I've read and what grsthegreat posted above, that's a code (and/or utility co.) prohibited approach. Even isolated with a dedicated ATS, the generator is effectively providing backup power to two separately metered services. That's why a number of people have suggested the pump has to be completely isolated from the existing house circuitry, so utility or backup power for the pump only comes from one metered service.
 
   / More backup generator discussion: Backing up well pump in a different structure #42  
I think, from what I've read and what grsthegreat posted above, that's a code (and/or utility co.) prohibited approach. Even isolated with a dedicated ATS, the generator is effectively providing backup power to two separately metered services. That's why a number of people have suggested the pump has to be completely isolated from the existing house circuitry, so utility or backup power for the pump only comes from one metered service.

The pump can be completely isolated from the existing house utility circuitry (including the neutral) by a transfer switch at the old house. All this means is that the transfer switch has to be 3 pole (2-hots & N) instead of just 2 pole (2- hots).

A slicker way is running a circuit from the new house panel to the old house transfer switch. This way, in the rare case that new house still has utility power but old house doesn't, pump still runs and genny is not needed; but if new house loses power, then new house panel still gets energized by genny and power still goes to pump.
 
   / More backup generator discussion: Backing up well pump in a different structure #43  
I think, from what I've read and what grsthegreat posted above, that's a code (and/or utility co.) prohibited approach. Even isolated with a dedicated ATS, the generator is effectively providing backup power to two separately metered services. That's why a number of people have suggested the pump has to be completely isolated from the existing house circuitry, so utility or backup power for the pump only comes from one metered service.

Now I’m confused. Are some saying a Backup Gen can’t power more than one metered service? If your barn and house have two meters they can’t share a gen?

It sounds like you are thinking of doing what I recommended in my first post? Now I’m curious and going to have to dive into the code books. I don’t see that as an issue but will need to verify.
 
   / More backup generator discussion: Backing up well pump in a different structure
  • Thread Starter
#44  
According to your diagram, they are in parallel as long as there are no check valves or closed valves that would isolate the water system normally. Your bladder tank in the old house will function in conjunction with the one in your new house.

Pump up you water pressure and turn the pump off. Open a faucet in the old house and you can run down the pressure to both houses. Do it again but this time open a faucet in the new house. Same result in a parallel system. It's no different than doing the same thing in a single house using two different faucets in separate tests.

There won't be a bladder tank in the new house. The new house is treated as a fixture off the existing tank.

As to the well specs, If you should have only a 1/2 hp pump, you're only using a fraction of the wire size capacity. Voltage drop wouldn't be large in this instance. A 2 hp pump would be a different story. If you need to stay with a 30 amp circuit, check some online voltage calculators and find what wire size is acceptable for a 30A 450 foot run.

One example:

Voltage Drop Calculator

Thanks for the link. I need to get the pump specs on my next visit to the property.
 
   / More backup generator discussion: Backing up well pump in a different structure #45  
Distracting from OP once again, but : You may be to Code under a (IMHO) rarely used exception.
The 2017 Code (Article 250.35) allows an exception: No ground conductor is required from main panel, and bonding of ground/neutral at sub panels is allowed if "there are no continuous metallic paths..." between the buildings that connected their ground systems. Essentially they allow you not to have a ground conductor (or thinking of it another way, you can use the neutral conductor for a ground fault conductor back to the transformer) if there's no way normal neutral current can use a parallel continuous metallic "ground" path.

I assume you don't use metal conduits to sub panels?
While this exception is allowed, the problem of using this comes if a future metallic connection (water, gas pipes, duct work, etc..) is installed after the inspector leaves, or years down the road and normal neutral current uses it as a path.


Yes that is the reason I知 allowed, no metallic anywhere between any buildings and never will be.
 
   / More backup generator discussion: Backing up well pump in a different structure
  • Thread Starter
#46  
Now I’m confused. Are some saying a Backup Gen can’t power more than one metered service? If your barn and house have two meters they can’t share a gen?

That's what grsthegreat posted, and he seems to have hands-on experience in the same scenario. I've found similar statements from others during my research.

It sounds like you are thinking of doing what I recommended in my first post? Now I’m curious and going to have to dive into the code books. I don’t see that as an issue but will need to verify.

Yep. Basically what Jcoon proposed in post #3.
 
   / More backup generator discussion: Backing up well pump in a different structure #47  
I like redundicy, I have 2 HVAC system on a house that only needs one. I have 3 generators, 2 freezers, ect.

If I were in this situation, I would install another well for the new house and run a pipe between the houses with necessary valves to feed both houses from either well in the event of a failure.

I would keep them independent and only tie together in an emergency.

Around here, a 4" well with pump and 80 gal tank is around $4500.
Not unreasonable if you are building a new house.

I do understand that wells can be considerably higher depending on geographic location. And this option may not be feasible for everyone.

It would definitely solve your backup power issue though!

Depending on well depth/drilling conditions, a well can cost up to $30/ft.
Drilling a second well @$30/ft. (mine was 337') would cost over $10,000 just for the hole.
Then add pump, drop pipe, wire, trenching, misc, and labor, that 2nd well could cost $13,000.
That option would certainly not work for me.
 
   / More backup generator discussion: Backing up well pump in a different structure #48  
Why four wires? If the well pump is isolated as a single branch circuit from the new house, wouldn't it just be the two hot 120v legs and ground?
not if there is a heater or lights in the well house. most well house panels ive seen have 120 circuits there also. if they are not [present, then yes only 3 wires would be needed.
 
   / More backup generator discussion: Backing up well pump in a different structure #49  
Now I’m confused. Are some saying a Backup Gen can’t power more than one metered service? If your barn and house have two meters they can’t share a gen?

It sounds like you are thinking of doing what I recommended in my first post? Now I’m curious and going to have to dive into the code books. I don’t see that as an issue but will need to verify.
i have never seen an installation allowing 2 different structures, each having their own meter, to share a generator. this would mean both houses are going to also share a neutral seeing as residential transfer switches do not switch the neutral. i once asked an inspector about doing just this scenario and he adamantly stated no way. if there was a way to isolate the neutrals, then that would be a different story. you can have multiple transfer switches fed off of a single generator, but all have to be on same system.

one other thing to consider, the 150 foot run between generator and original house. the voltage drop needed to carry the generators load will need pretty large wires. then you have to consider the fact that the NEC requires that an automatic standby generator that automatically switches over to a whole house switch be capable of supplying the load without shutting down. now youve just added 2 houses to the load calcs. good luck getting the largest air cooled genny (96 amps at 240 v) to power 2 houses and meet code. if you have to switch to liquid cooled or diesel, $$$$$$
 
Last edited:
   / More backup generator discussion: Backing up well pump in a different structure #50  
Also a little off topic, curious to why are you burying your propane tank? Seems just to add cost and a bigger headache for maintenance. Is there no place to hide out of the way above ground?
 
   / More backup generator discussion: Backing up well pump in a different structure #51  
Yup me either! Cost me 8,500 for my 245 foot well.
 
   / More backup generator discussion: Backing up well pump in a different structure #52  
Are you married to the idea of two separate meters? Another option is to just install a single 400a service, with 200a breakers to each house and a transfer switch on the main panel. That way both houses and the well have generator backup, and you only get a bill for one electrical service.

Works for me! Electricity in Ontario is so ridiculously expensive for things like delivery and the basic fee and debt retirement charge each month and A whole bunch other crap like that, that I would not want to have 2 meters on my property. Ask Dave. He will tell you.
 
   / More backup generator discussion: Backing up well pump in a different structure
  • Thread Starter
#53  
one other thing to consider, the 150 foot run between generator and original house. the voltage drop needed to carry the generators load will need pretty large wires. then you have to consider the fact that the NEC requires that an automatic standby generator that automatically switches over to a whole house switch be capable of supplying the load without shutting down. now youve just added 2 houses to the load calcs. good luck getting the largest air cooled genny (96 amps at 240 v) to power 2 houses and meet code. if you have to switch to liquid cooled or diesel, $$$$$$

Not going with whole house. Planning on using an automatic switch with selected loads assigned it (the ones that typically support between 8 and 16 circuits).
 
   / More backup generator discussion: Backing up well pump in a different structure
  • Thread Starter
#54  
Also a little off topic, curious to why are you burying your propane tank? Seems just to add cost and a bigger headache for maintenance. Is there no place to hide out of the way above ground?

Aesthetics. My wife has a background in design and is a full time artist. Life is much happier if I don't clutter the yard with ugly objects. :)
 
   / More backup generator discussion: Backing up well pump in a different structure
  • Thread Starter
#55  
not if there is a heater or lights in the well house. most well house panels ive seen have 120 circuits there also. if they are not [present, then yes only 3 wires would be needed.

The well house is an above ground manhole-caission type structure. I'll examine more closely the next time I go pry the cover off, but the circuits and breakers I see in the basement of the existing house indicate a three wire setup.

Looks a bit like this:

79709d1305068899-how-hide-above-ground-concrete-sewer-2.jpg
 
   / More backup generator discussion: Backing up well pump in a different structure #56  
Now I’m confused. Are some saying a Backup Gen can’t power more than one metered service? If your barn and house have two meters they can’t share a gen?

Why? Says who? What does the utility care as long as your disconnected from them?

Obviously powering from new house is simplest and cheapest. Just adequately size for voltage drop.
 
   / More backup generator discussion: Backing up well pump in a different structure #57  
Howdy,

Well water.. You can have multiple bladder pressure tanks. You could put 1,2,3,4 90 gallons bladder tanks at your new house and still have the bladder tank at the old house. The pump will simply fill it all up and shut off at pressure.

The problem I for see is the fact that power from another source is coming into the basement at the old house. When a person knows they just shut off the main breaker (old house)... and the well pump switch is still hot. Signs and labels don't work.

You could simply move the pump switch to the new house. Run the power from there to the well. Never going into the old house. The water lines remain and pressure bladder tanks all still work as needed. (I am thinking you have a standard submersible pump, with just a pump controller switch)

Well pressure bladders tanks of different sizes are used for different purposes. For a main well with multiple cattle waterers here I have 2 90 gallon pressure tanks.

Another option is a central farm distribution. 1 meter feeding the whole farm.
 
   / More backup generator discussion: Backing up well pump in a different structure #58  
I have a slightly different thought. Power from the new house/ generator but move the controls outside the old house. Then it's only 150' of wire and no mixed electrical systems.
 
   / More backup generator discussion: Backing up well pump in a different structure #59  
I haven't read all the replies but I agree, run the power from the generator to old house and install a transfer switch there as well.
 
   / More backup generator discussion: Backing up well pump in a different structure #60  
Ok went back through my code book and can find no issues with 1 circuit (the well pump) going to the other building. This can have power from both the utility and (with a properly installed gen and transfer switch) the gen as well.
NEC 2014 225.xx and 250.xx address the “separate building” and provide some exemptions for a single circuit.
NEC 2014 also addresses gens but the discussion is around proper grounding, neutrals and ensuring utility and gen power is isolated from each other- proper transfer switch.
NEC 2014
445.xx
702.xx

As mentioned early on in this thread by LueNY a properly labeled and installed single circuit from the new building back to the old building to power the well will be the easiest way to provide utility and gen power to that circuit.
 

Tractor & Equipment Auctions

SANY SY225C 9C5KL EXCAVATOR (A59823)
SANY SY225C 9C5KL...
2088 Chevrolet C7500 Altec TA40 41ft. Bucket Truck (A59230)
2088 Chevrolet...
2005 TerraGator 8104 (A55302)
2005 TerraGator...
2006 iDrive TDS-2010H ProJack M2 Electric Trailer Dolly (A55852)
2006 iDrive...
2024 MACK GRANITE GR46F DUMP TRUCK (A59823)
2024 MACK GRANITE...
2006 Nissan Murano AWD SUV (A59231)
2006 Nissan Murano...
 
Top