PTO generator problems with electical approval. Pls help

/ PTO generator problems with electical approval. Pls help #1  

gogojuice

Silver Member
Joined
Oct 29, 2013
Messages
181
Location
Canada
Tractor
Kubota
So.. I purchased a 16 KW 50 amp PTO for my tractor.

It was all hooked up by a professional to the panel using an interlock.
EAT-BR2A Cutler Hammer Generator interlock kit 15 2 Amp BR Panel LISTED | eBay

I asked to make sure everything would be ok prior to paying for the install. I was told which kit I should order.
Now I get this. (from the ESA)

Couple things regarding this set up.
1) The UL file number is coming up with nothing - E113887. No search results.
2) The Document indicates that only professional people shall have access to this device. An amateur should never.... anyway This is not something I will approve with a residential domain.

Would suggest an approved Transfer system in place.
Regards,

What are my options?
I'm looking for a whole house setup. Apparently I have to change this soon or they will disconnect my power!

BTW.. I live in Ontario.

Thanks
 
/ PTO generator problems with electical approval. Pls help #2  
Sounds like the professional didn't know the local electrical code.
 
/ PTO generator problems with electical approval. Pls help
  • Thread Starter
#3  
Yep.

Now the company says that they can install a manual transfer switch, but I will only be able to run a couple of circuits. Kind of defeats getting a generator for the whole house, no? There must be something that can be done?

Thanks in advance for help
 
/ PTO generator problems with electical approval. Pls help #4  
I am not sure of what your code is, however my local code does not allow a retrofit interlock. I was able to contact the manufacturer of my load center and purchase a factory installed interlock on a new front panel. The inspector for my location was not worried about the concept of the interlock, they were more worried about proper installation and proper location.

One issue they had that made them require the manufacturer not a retrofit was a person did not properly align the interlock. So therefore it did not function as designed.

Perhaps you can find a new panel with a factory installed interlock. Like the previous person it sounds like the original installer wanted to cut a corner and not do the work to code or correctly.
 
/ PTO generator problems with electical approval. Pls help #5  
In the US, with a supply of 50A I think you are prohibited by code from installing whole house transfer. The transferred circuits must be appropriately sized for the connected generator. Old style analog load shedding is not allowed by code.
 
/ PTO generator problems with electical approval. Pls help #6  
For to legally meet Cdn norms it would need ULC (C=Cdn) stamp.
Often exactly same but just a paperwork exercise ($$) that many figure if good enough for USA then it should be good for CDN.
Often is also the case with engineer approvals as well.
Shucks they even get into provincial squabbles. ((approved in Ontario still needs a Quebec eng. signature)
Would seem that borders influence engineering principles no matter where you studied.
It is all really self protection and nothing to do with cash grabbing (LOL)
EGO's running wild.

Provide the same data for USA UL and for sure the C will require some additional test simply to let you know that they are in control.
It is all about your safety you understand. (and not a cash crab)

My take is if UL is OK, then screw them all and go for it.
 
/ PTO generator problems with electical approval. Pls help
  • Thread Starter
#7  
Thanks for the responses.
I'm not electrically inclined, hence that is why I hired a professional.
Now it seems I should have hired the local apprentice or the guy next door lol.

So if I have to change it.... what are my options??
 
/ PTO generator problems with electical approval. Pls help #8  
What is ESA?
 
/ PTO generator problems with electical approval. Pls help #9  
The interlock you purchased will work fine as a back fed source for your whole house panel. The only issue is that you will be required to shed loads, something all AHJs loathe. A formal transfer panelor a sub panel sized for your load will also work.
 
/ PTO generator problems with electical approval. Pls help #10  
It's simple. They don't recognise the certification as it doesn't have Canadian certification. I'm guessing, to get that, would cost as much as what a manufacturer would pay.

It's like, we have a whole system of Government that determines vehicle safety but at the end of the day it's the US that makes these rules, and the only thing we REALLY insist on is that the speedo reads KMS!

My friend works with ESA all the time and they are a major pain in the butt! Every inspector sees things differently.
 
/ PTO generator problems with electical approval. Pls help #11  
Since no one will come right out and tell me what ESA stands for I'll have to guess that ESA is the inspection agency and this is a permitted job.

I don't think any interlocks are fully UL rated. If that is what is being required you'll need a trasfer switch.
 
/ PTO generator problems with electical approval. Pls help
  • Thread Starter
#12  
Sorry,

ESA = Electrical Safety Authority. (Inspector)

https://www.geninterlock.com/images/layout/Recognition_Letter_84974_r1.pdf

Here is the UL rating. (UL67)

The inspector couldn't find anything on the device so automatically discounted it. It is being resent with the info.. he should of found.. and is looking at it now.
I don't have much hope as he was so quick to discount it without researching it.
 
/ PTO generator problems with electical approval. Pls help #13  
Sorry,

ESA = Electrical Safety Authority. (Inspector)

https://www.geninterlock.com/images/layout/Recognition_Letter_84974_r1.pdf

Here is the UL rating. (UL67)

The inspector couldn't find anything on the device so automatically discounted it. It is being resent with the info.. he should of found.. and is looking at it now.
I don't have much hope as he was so quick to discount it without researching it.

That letter basically says nothing. UL67 are the standards for electrical panel boards which must be met. The panel is then inspected and receives its UL rating seperately. That interlock has no UL rating, and even if it did, to be used as a recognized assembly with your Cutler panel the entire assembly would have to be inspected. The MET labratory recognition mark has the very same weight as the "Rock Knocker Recognition Mark", it is just something somebody said.

You asked your electrician to give you a hook up which was "OK". This he did, your interlock will work fine as long as you load shed when it is energized. But it certainly will never met CSA or UL rating, nor will it likely pass a inspection in your neck of the woods (although there are spots in the USA that would pass such an assemblage).

How much did the electrician charge you? Installation of that interlock should be about a ten minute job. You will now either need a real life transfer switch which will pass inspection, or cancell your inspection and make do with the interlock or a combination of the interlock and a subpanel.
 
/ PTO generator problems with electical approval. Pls help #14  
MET Labs is the anti-UL. From their website
25+ years ago, we broke the UL monopoly for product safety testing and certification in the United States.

So if an agency requires UL certification, and you get MET certs instead, then you're SOL
 
/ PTO generator problems with electical approval. Pls help #15  
Howdy,
I believe you are using a 2nd hand manufactured part. It is not in the true UL approved system.

Did you notice the paperwork instructions with it? Was it a real Cutler-Hammer instructions?

Anyway. What you need to do. You need to purchase a real interlock from the manufacturer of your panel. If you have a Cutler-Hammer service panel, you will need to see if Cutler-Hammer makes a approved interlock. You would then have the proper certification to get approved. :)

Cutler-Hammer BR Panel interlock Kits Brochure
 
/ PTO generator problems with electical approval. Pls help #16  
A "whole house" system would require both a generator AND transfer switch that matches the capacity of your panel.

The 16kw rating on your generator is probably the peak or surge rating. Most homes will have 200 amp panels these days.

If you were planning to pull a permit you should have told the electrician that up front and had him pull the permit.
 
Last edited:
/ PTO generator problems with electical approval. Pls help #18  
Howdy,

UL and ULc are met by the manufacturer. You need to purchase a real Cutler-Hammer part. Not a copy.
 
/ PTO generator problems with electical approval. Pls help #19  
Have you contacted the electrician? Seems he should be involved in bringing the project to code at his cost. Unless you specified the parts and e just installed them.

We are in process of upgrading house to 200 amp service, installing gen panel and a bunch of other stuff.

Contractor pulls all permits and insures we pass inspection. If not they fix whatever is wrong at no additional cost to me.
 
/ PTO generator problems with electical approval. Pls help #20  
Howdy,
I believe you are using a 2nd hand manufactured part. It is not in the true UL approved system.

Did you notice the paperwork instructions with it? Was it a real Cutler-Hammer instructions?

Anyway. What you need to do. You need to purchase a real interlock from the manufacturer of your panel. If you have a Cutler-Hammer service panel, you will need to see if Cutler-Hammer makes a approved interlock. You would then have the proper certification to get approved. :)

Cutler-Hammer BR Panel interlock Kits Brochure

This is it.

Calling an electrician to install a product the OP found on eBay is what they did. Now turning around and saying the device isn't approved- must be the electrician's fault- is misguided. It's a different story if you had called the electrician and asked them them to provide the parts as well.

Sounds like the eBay seller is misrepresenting something and the inspector caught it. Bummer.

The other option is a "whole house" transfer switch. The manual ones are under $1000 depending on the amps needed. 100a, 200a or rarely larger on a house.
 
 

Marketplace Items

2019 John Deere 30G Mini Excavator (A63109)
2019 John Deere...
Deere 35G (A62180)
Deere 35G (A62180)
Electric Concrete Mixer (A61166)
Electric Concrete...
2016 PETEBILT 579 69 SLEEPER (A62613)
2016 PETEBILT 579...
New/Unused Quick Attach Skid Steer Brush Cutter (A61166)
New/Unused Quick...
New/Unused IRMC Massage Chair (A61166)
New/Unused IRMC...
 
Top