Oil Boiler Setup Questions

   / Oil Boiler Setup Questions #1  

jb1390

Gold Member
Joined
Aug 27, 2010
Messages
431
Location
Southeastern CT
Tractor
Mahindra 3550, Hitachi 120-2
We have been heating exclusively with wood for the past number of years, we have not used the hydronic system at all. I am working to revamp it a bit - and I'm replacing the original (General Motors) boiler, with a Liberty Slant Fin (LD-30P I believe) I bought secondhand. I have some questions about how to set up zone and boiler controls. House is 1150 sf, poorly insulated with single pane windows.

1. We heat Domestic Hot Water with an electric water heater. There is not a DHW coil on this boiler, and I'm not planning to add one. If we end up tying in a wood boiler someday, we may connect DHW to that, but I'm not currently planning to alter the DHW system.

2. I would like to zone with separate pumps. The pumps are relatively cheap, and contain check valves. It seems this is the easier way to go - and will allow appropriate flow for each zone. Otherwise it's a bigger pump with zone valves - and chances are only one zone will ever run due to continued heating with the wood stove. Using separate smaller pumps seems more appropriate and simpler for this application. The pumps would be controlled via relays and thermostats.

3. For ease of control, I was planning on controlling the boiler purely off an aquastat - and the thermostats would tie in only to the pumps. So the boiler would run independently, maintain hot water, and the pumps would move it as required. From what I've read, it seems some systems will increase the boiler temp when it calls for heat, but allow the temp to relax when there is no call for heat, but maintain a lower temp for DHW. Since I am not doing DHW, I was going to get an adjustable aquastat, and adjust the range as required so the boiler doesn't short-cycle excessively. Is this approach ok?

4. We would like 3 zones - one that will be shut off most of the time. This space is not typically used during the winter due to very poor windows and insulation. I was planning on including glycol for this zone - and it will have a heat exchanger and separate pump. I did not want to include glycol throughout the entire system - but would not be strongly opposed if that's the better way to go. It seems the drawbacks outweigh the slight increase in cost and equipment to isolate that particular zone.

Am I missing anything major? Any suggestions on a different approach?
 
   / Oil Boiler Setup Questions #2  
I think you are missing the boat by not using the domestic water circuit on your boiler(add one if you don't have it) ;basically your domestic is free during the heating season.And expensive with electric.
Control the boiler with an aquastat and run the circulators off the thermostats is the way to go.
I would recommend putting glycol in the whole system.
 
   / Oil Boiler Setup Questions #3  
There's no way you can put glycol in one zone and not the whole system, when the circulator runs it will mix it all up. I put glycol in the whole system. I also normally keep the makeup water off, if my system is leaking I want to know about it and fix it. I had expensive damage to a system once that I thought was protected by glycol, but it was leaking and the glycol had been mostly replaced by makeup water.

Hot water from the boiler isn't free, it still takes fuel to make, but it is cheaper than electric. Your boiler will also produce a lot more hot water than any electric water heater. The preference now seems to be for indirect loops in tanks rather than tankless loops, the water temperature is more stable.
 
   / Oil Boiler Setup Questions #4  
I would run glycol in the whole system as that will help keep you from having damage if you have power issues in the winter.
I have an indirect HW heater and its nice, but it can get spendy in the summer.

Aaron Z
 
   / Oil Boiler Setup Questions
  • Thread Starter
#5  
There's no way you can put glycol in one zone and not the whole system, when the circulator runs it will mix it all up. I put glycol in the whole system. I also normally keep the makeup water off, if my system is leaking I want to know about it and fix it. I had expensive damage to a system once that I thought was protected by glycol, but it was leaking and the glycol had been mostly replaced by makeup water.

Hot water from the boiler isn't free, it still takes fuel to make, but it is cheaper than electric. Your boiler will also produce a lot more hot water than any electric water heater. The preference now seems to be for indirect loops in tanks rather than tankless loops, the water temperature is more stable.

If I had that zone separate, it would require a heat exchanger, and 2 circulator pumps to make it work. Just not sure if the cost of glycol would offset the cost of the extra parts, or if there are other issues that arise by using glycol in everything.

I agree that the DHW through oil would save a little in the winter but probably cost more money in the summer - not sure we use enough of it to make it worth the effort for slight winter savings. Someday we will tie in a wood boiler with this system - I was planning on preheating the DHW with the wood boiler if we get it hooked up, and leaving the DHW alone for now.
 
   / Oil Boiler Setup Questions #6  
Be sure the pumps you select are glycol compatible, the seals in some pumps are not. Use glycol like Dow sr-1 designed for boilers and hot water systems, do not, repeat do not use automotive antifreeze in a hydronic heating system too many additives, stop leak, corrosion protection etc. I would use 1 pump and multiple zone valves, depends on how much money you want to spend.
 
   / Oil Boiler Setup Questions #7  
If I had that zone separate, it would require a heat exchanger, and 2 circulator pumps to make it work. Just not sure if the cost of glycol would offset the cost of the extra parts, or if there are other issues that arise by using glycol in everything.

I agree that the DHW through oil would save a little in the winter but probably cost more money in the summer - not sure we use enough of it to make it worth the effort for slight winter savings. Someday we will tie in a wood boiler with this system - I was planning on preheating the DHW with the wood boiler if we get it hooked up, and leaving the DHW alone for now.
We go through almost a full tank of oil each summer. Planning on adding an electric HW heater to use in the summer to help with that. It should pay for itself fairly quickly.

Aaron Z
 
   / Oil Boiler Setup Questions
  • Thread Starter
#8  
Be sure the pumps you select are glycol compatible, the seals in some pumps are not. Use glycol like Dow sr-1 designed for boilers and hot water systems, do not, repeat do not use automotive antifreeze in a hydronic heating system too many additives, stop leak, corrosion protection etc. I would use 1 pump and multiple zone valves, depends on how much money you want to spend.

I'm looking at using Grundfos UPS15-58FC pumps, they are less than $100 each. Based on literature I have seen, they are glycol compatible.
 
   / Oil Boiler Setup Questions #9  
Most of your plan sounds good. Isolating the little-used zone with a separate heat exchanger seems to be overkill and expensive, is the piping and fin tube subject to possible freezing? It may be better to set the thermostat in that area to a lower temp so that zone cycles often, but will not run for long. You can control the boiler in a way that it will only fire if one or more zones call for heat, keeping the boiler hot(weather full or reduced temp) is wasteful. When piping in the pumps, plan on your possible future DHW needs with stubs for another pump, for an indirect heat exchanger. It would be great if an electric HW heater was available with a heat exchanger...does anyone know of one? Adding glycol to the whole system gets expensive and also reduces efficiency. FYI-30 years HVAC
 
   / Oil Boiler Setup Questions
  • Thread Starter
#10  
Most of your plan sounds good. Isolating the little-used zone with a separate heat exchanger seems to be overkill and expensive, is the piping and fin tube subject to possible freezing? It may be better to set the thermostat in that area to a lower temp so that zone cycles often, but will not run for long. You can control the boiler in a way that it will only fire if one or more zones call for heat, keeping the boiler hot(weather full or reduced temp) is wasteful. When piping in the pumps, plan on your possible future DHW needs with stubs for another pump, for an indirect heat exchanger. It would be great if an electric HW heater was available with a heat exchanger...does anyone know of one? Adding glycol to the whole system gets expensive and also reduces efficiency. FYI-30 years HVAC

The room we are isolating is really a 3 season room - the windows are very drafty, the floor is not insulated, and the pipes run underneath that room in a crawl space. Typically we close the door to that room, and it is common in the winter for the snow to stay frozen on the floor in there. We are not looking to change that with the boiler install - but we would like to use the space occasionally. I would be concerned with pipes freezing if we left the heat shut off in there for days over the coldest part of the winter. I don't think the cost is excessive to isolate - I'm looking at $90 for an extra circulator, 80 or so for a heat exchanger, and 25 for an expansion tank, plus the glycol. It seems that the cost of that would be saved in oil pretty quickly.

I had read about the boiler cycling only when called for heat - I thought from what I had read that this was primarily for DHW purposes - so that the boiler would not sit at too high of temperature over the summer, without having to touch the aquastat - but then would increase temp to keep up with heat load. I was thinking of just adjusting the aquastat depending on season - so leave the water temp low for spring/fall, and increase it some in the winter as required to meet heat demand. I was also thinking a programmable aquastat would be a neat feature - if one exists. I'm not too concerned about standby losses - I think most of that loss would be radiated to the basement, which we would like to keep semi-heated anyway. Also would be simpler to wire and control for a first cut. Would this be difficult to modify if I changed my mind later?
 
   / Oil Boiler Setup Questions #11  
Hot water heating systems are not a good DIY project unless you thoroughly understand the engineering and control nuances, much less the piping design and install. In my younger day I was a mechanical systems service technician and used to see it all. The industry has changed tremendously the last 20 years. Trying to design a system via a forum like this is iffy as we have no idea what you already have. It would be helpful if you had a friend or acquaintance in the business to assist you. The installation is not that difficult if you have good mechanical skills; it is getting to that point first.

Glycol is the way to go. Far cheaper in the long run and provides protection to the whole system in the event of a failure during freezing weather. It also acts as a lubricant for the pumps and a corrosion inhibitor. DO NOT leave the make up water source valve on unless you buy a complete automatic make up water system that maintains the mixture and alarms when there is a leak. Leaks have to be fixed quickly or your protection is compromised. By Code yhe make up water requires a Reduced Pressure Back Flow Preventor. You do not want glycol feeding back into your DWS. Most Code Enforcing Authorities require annual test and certification annually.

Remember; Boilers are one huge bomb if not maintained and serviced properly. a home boiler can destroy a whole hose and everyone in it. They are not as forgiving as an electric water heater.

I assume you are not getting a permit to do your project as they would probably require an engineered design. The average inspector is not knowledgeable on boilers except in OR State where I used to work. Therefore, they are usually not much help. Supply houses normally will not help due to liability and they sell not design and install. I had to be State licensed as a Pipefitter/Boiler Mechanic. Most Plumbers could not pass the exam so they were limited to installing hW Heaters less than 200 GL.

This is all not to scare you but to make you proceed with caution. The life you save may be your own.

Ron
 
   / Oil Boiler Setup Questions #12  
I understand your concerns about the 3 season room...your plans for the isolated loop should work fine. The boiler is oversized for your home (you could use one 1/3 that size) and will short cycle unless you install an outdoor reset control, which adjusts boiler water temp depending on outdoor temperatures, this will automatically take care of reducing boiler temps with seasonal and daily temperature swings. Make sure you limit the burner output to the minimum design also.
 
   / Oil Boiler Setup Questions #13  
The room we are isolating is really a 3 season room - the windows are very drafty, the floor is not insulated, and the pipes run underneath that room in a crawl space. Typically we close the door to that room, and it is common in the winter for the snow to stay frozen on the floor in there. We are not looking to change that with the boiler install - but we would like to use the space occasionally. I would be concerned with pipes freezing if we left the heat shut off in there for days over the coldest part of the winter. I don't think the cost is excessive to isolate - I'm looking at $90 for an extra circulator, 80 or so for a heat exchanger, and 25 for an expansion tank, plus the glycol. It seems that the cost of that would be saved in oil pretty quickly.

I had read about the boiler cycling only when called for heat - I thought from what I had read that this was primarily for DHW purposes - so that the boiler would not sit at too high of temperature over the summer, without having to touch the aquastat - but then would increase temp to keep up with heat load. I was thinking of just adjusting the aquastat depending on season - so leave the water temp low for spring/fall, and increase it some in the winter as required to meet heat demand. I was also thinking a programmable aquastat would be a neat feature - if one exists. I'm not too concerned about standby losses - I think most of that loss would be radiated to the basement, which we would like to keep semi-heated anyway. Also would be simpler to wire and control for a first cut. Would this be difficult to modify if I changed my mind later?

I understand in Europe it's popular to have a system where there is an outdoor temperature sensor and the aquastat setting is determined by the outdoor temperature.
 
   / Oil Boiler Setup Questions
  • Thread Starter
#15  
This web site has a wealth of info on the latest solutions for hydronic systems.

Technical Magazine | Caleffi

It is a lot better for you to read it than try to design your system via the forum.

Ron

Thanks for your input. I have been in touch with the local building inspector, and I have resources outside of this forum, if it puts your mind at ease. (I'm also a mechanical engineer - and worked in the MEP field for a short time - hated it, but that's another story). The local inspector did not want detailed documentation on the system - he wanted a price tag for the parts, so he could assign an appropriate fee. This was even true if I installed the wood boiler in parallel with the oil. In my opinion, there is significantly more safety risk with a wood boiler than oil, so I was surprised he didn't want more information on relief valves, heat dump, etc.

You say glycol is the way to go - and in the following sentences, list some of the drawbacks. It seems more hassle than what it's worth for a house that is typically inhabited with a secondary heat source. If designing a system for a house that is left alone for weeks at a time, I'd agree that glycol makes sense for the entire system, but I'm not sure the benefits outweigh the drawbacks for my application.
 

Tractor & Equipment Auctions

2024 CATERPILLAR 305 CR EXCAVATOR (A60429)
2024 CATERPILLAR...
2016 CATERPILLAR 259D SKID STEER (A60429)
2016 CATERPILLAR...
2013 Nissan Rouge SUV (A59231)
2013 Nissan Rouge...
UNUSED IRGC80 Battery Powered Golf cart (A55272)
UNUSED IRGC80...
2013 Ram 1500 Crew Cab Pickup Truck (A59230)
2013 Ram 1500 Crew...
20 UTILITY TRAILER (A58214)
20 UTILITY TRAILER...
 
Top