Electrical/Electronic Question
/ Electrical/Electronic Question #1
RFB
None
Sirs,
I have a standby (could be considered prime power) generator system.
It is a Kubota V3300T turbocharged coupled to a Marelli (USA) generator head, Maximum Output 45,000 watts; Continuous Output Power One-Phase 40,000 watts; Load Amperage at 240 volts, Maximum Load
188 Amps, Continuous Load 167 Amps.
It is sized to power 6500 (6 tons of heat pump HVAC) square feet of combined residence, shop and garage as well as deep well pump and everything that goes with a complete electric location. (No other power source beyond utility supplied electric.)
I have recently completed the installation, and run it with full load about one hour per month as a system check and to keep the fields in good shape.
My question:
I have to small uninterrupted power supplies (UPS) for my computer and router.
They refuse to function under generator power. They receive the power (the LED panel on the UPS shows input voltage and frequency.), but will not provide any output. Once back on line power (not generator) they work fine.
The generator has AVR of +/- 1%. I measured the input voltage to the UPS and it holds steady at 120 - 122 volts, and 62Hz.
Any ideas?
/ Electrical/Electronic Question #2
If possible I would temporarily set the generator to 60 hz or as close as possible. Try to keep the load constant. The frequency will probably drop as the load increases. Then try to run the inverter. This would help isolate the problem. Utility power is very close to 60 hz.
Yes Sir, that is what we aimed for. Is 62Hz too much out? (It stays between 60 and 62Hz, and 120 to 122 volts)
/ Electrical/Electronic Question #4
You might look into the type of sine wave the generator puts out and see if that is compatible with your UPS. I have seen that as an issue in the past.
/ Electrical/Electronic Question #5
Three things that come to mind.
Check to ensure that the UPC is sensing the properly grounded/bonded system. You can eliminated this by putting a temporary jumper between the grnd and neutral terminals at the receptacle. If that solves the issue you'll have to ensure you're system bonding and ground is not compromised when you run your genset. Don't leave the jumper permenently.
The next is a little more difficult to check and to resolve. I you have a true RMS dvom check to see if you have a pure and clean sine wave. Check the peak to zero volts. If you get very lose to 167-172 volts then thats not your problem. If the voltage is out of that range then most likely thats your problem in which case you'll have to set up something different for that circuit. What comes to mind is a battery back with a true sine wave inverter or put up with the fact that a couple items will not work when your running on your genset.
Lastly it may be an interference issue where the genset is putting to much noise on the line and you'll need a chock coil to suppress the resonating frequencies. If this is the case its a pretty simple fix. Contact the generator manufacturer, they may have a kit or you can try a local electronics stores. The kit is pretty low tech and useally pretty cheap. The kits pretty involve a few coils of wire wrapped around an iron core. One chock coil per line including the grnd and neutral.
Confused yet, cause I am. and I need a beer:drink:
I am not an electrician, but the gentleman that performed the install is a very reputable one, and so I have at least a rational reason to believe that the system is properly grounded/bonded.
I watched when he made the connections and everything is well grounded and bonded at every conceivable location.
Nonetheless, you indicate a jumper from the ground to neutral at the outlet that the UPS is plugged into?
Are there any negatives or drawbacks from doing that? (Referencing your "Don't leave the jumper permanently" statement.)
I do not have a "true RMS dvom" (nor the knowledge to use one) so I may have to "put up with the fact that a couple items will not work when your running on your genset." I will not have the internet while on gen power anyway, because power failures around here also shut down the dsl systems. The point of the UPS is to buy time for a proper shutdown of the computer system.
I might even try plugging straight into the outlet instead through the UPS. Everything else works plugged in directly, so that might be the simplest solution.
Thanks for the feedback.
/ Electrical/Electronic Question #7
Your neutral conductor gets grounded only once, at the service entrance and no where else. By putting the jumper your grounding the neutral a second time. Its okay to do it for a short (no pun intended) time but over time your running the chance of getting circulating (eddie) currents in the neutral "circuit" which could cause heating of the neutral conductor.
Some electronics electronics "search" for a voltage difference between neutral and grnd. If the voltage is out of range it shuts down to prevent damage.
/ Electrical/Electronic Question #8
If you UPS is an APC brand you can set the sensitivity of the UPS "down" to work on not so clean power and they will then run. I had to do that with mine when running on the generator. Look online on the APC (American Power Conversion) website and download he manual for your UPS and reprogram it. It was an easy thing to do. I cannot speak for other brands.
Some of the real small UPS's made by APC do not have this setting but all of the 750 VA on up seem to unless they were very old.
James K0UA
/ Electrical/Electronic Question #9
"I might even try plugging straight into the outlet instead through the UPS. Everything else works plugged in directly, so that might be the simplest solution.
" I would not recommend this if you value your PC !!
/ Electrical/Electronic Question #10
RFB,
I have an APC 1000VA UPS and it works fine. On the back there are two outlets at the top and 6 outlets at the bottom. The top 2 are labeled surge protected only. Those two outets are not on the battery side. Make sure you are not plugged into those. Sometimes the simple stuff escapes us.
Ron
Thank you gentlemen,
Unfortunately my ups's are Belkin 550 and CyberPower 850AVR with no sensitivity controls.
I am plugged into the backup outlets on the UPS's
The CyberPower has an LED indicator panel that shows the input power...120-120 volts AC, at 62Hz, but it will not allow output.
I just found this on the CyberPower site:
"CyberPower UPS systems are not designed to work with generators. Many generators output a ‘dirty’ AC signal that is not recognized by the UPS, which causes it to remain functioning off battery power."
/ Electrical/Electronic Question #13
Yeah looks like you are out of luck there, unless you swap if for one of the APC UPS's..That have the sensitivity control. My APC 1000 works fine on the Generator after the adjustment.
/ Electrical/Electronic Question #14
With a gen set that large (or any size, for that matter) I hope you are completely isolated from the grid when it is hooked in, including being locally grounded and breaking your neutral circuit back to the transformer. To not do this endangers the linemen.
Yes sir, this is completely isolated with a 400 amp seevice entrance rated manual trasnfer switch.
Sorry for the typos.
The router and modem use wall warts and the computer IMac I believe transforms to DC as well, so I think that all of these systems are DC.
As I mentioned, this is setup to buy time for an orderly shutdown, not to run while on gen power since there is no internet access for power failures in this neck o' woods.
The puzzle for me was why the ups's did not function on gen power, and I think that is solved.
I sincerely appreciate all the help.
/ Electrical/Electronic Question #19
Just a thought to consider if I read this right...
Seems you generator kicks on, shows the apc is charging, but it's not. The stuff plugged into it(your computer) continues to work, except they are draining the apc's reserve power.
Another way around it, if i read this right, is to charge the battery of the apc via the tractor's alternator, instead of converting 120 to 12 and then back to 120 for the computer to run. (Assuming the battery in the apc is 12v). Takes another set of wires to run, maybe adding a 12v plug on the apc so that charging the battery straight from 12v is not so much of a hassle. Also might consider moving the apc closer to where the tractor typically sits during generator useage.
More than one way to skin a cat...and since all an apc consists of is a 120v to 12v (ie battery charger) a storage device (ie a battery) and a 12v invertor to convert the stored power to 120v. By charging the battery from the tractor's alternator, you just skipped one of the process'.
David from jax
/ Electrical/Electronic Question #20
David from jax
I don't know if the UPS will like the alternator power. Its a pretty unstable power supply voltage varies to much and unclean power. Just a thought.
2026 Stout TB-76 Tri-Blade Brush Cutter (A64047)
2026 Stout TB-76...
2013 29ft. Larson LXI292 Boat with 2007 30ft Loadmaster T/A Boat Trailer (A64557)
2013 29ft. Larson...
130 BBL VAC TRAILER (A63569)
130 BBL VAC...
2025 GIYI GY-P45 Hydraulic Breaker Mini Skid Steer Attachment (A64553)
2025 GIYI GY-P45...
2019 HYUNDAI V12530152-AJS 53' X 102" T/A VAN TRAILER (A59910)
2019 HYUNDAI...
2011 Takeuchi TL250 Compact Track Loader Skid Steer (A64553)
2011 Takeuchi...