Wire Amp size in Garage
   / Wire Amp size in Garage #11
Every DIY electrician needs one or more of those books they sell at the big box stores. They are written for the non-electrician in non-electrician language. They have the tables from the code in them and discuss things like not loading a 20A circuit with a connected load of 20A. They are worth a lot more than the cost. The same advice goes for plumbing work and carpenter work where you are trying to at least stab at code issues. Wrong choices in electrical work can burn your house down.
Ron
   / Wire Amp size in Garage #12
Ron
Re 20 amp circuits: thing about circuits is that starting loads might be 20 amps but generally running load is 80 or 90%. Either way the CB is the weak link and even at max amps the wire won't heat up as the CB is the protection.
Most devices that draw 20amps continuous would have a probable 25amp start surge.
In a shop U want 20 as many if not most power tools now want 15amps run and often draw 20 start plus often we want to run 2-3 tools at the same time.
Ever notice the adds? 'powerful one hp motor', well that's maxing a typical 15 amp circuit.
   / Wire Amp size in Garage #13
IMHO bigger is ALWAYS better when running wire. If you have #8 available, use it. It's much more difficult to upgrade later on.
   / Wire Amp size in Garage #14
The little reference book is called " Ugly's " and is available at Home Delay/Home Depot in the electrical dept. I have 2 of them and I don't think I paid more than $10 each. A bunch of valuable information for a small price, IMO. 445A
   / Wire Amp size in Garage #15
I recently replaced my electric water heater... it's rated 240volts, with 4500 watt elements.
It's fed from a 20a breaker with 12-2 wiring.
I was surprised to see, when making the connections, that the wiring inside the heater, from connection box to thermostats/elements, is 14 gauge.
I called the manufacturer... they said 14 gauge wire can handle 20 amps when the conductors are not jacketed... they can dissipate heat better.
Seems to me that inside a water heater is not ideal for dissipating heat...:confused2:
Pete
   / Wire Amp size in Garage #16
Pete
It's always more complicated than just the gauge of the wiring, and frequently comes down to the insulation type and the installation type. For example, some outdoor wire is rated for direct bury but not conduit, precisely due to heating considerations.
One recent learning experience was with 2-2-2-4 Aluminum wire. If used for a branch circuit, it's rated for 90A. If used to feed an entire home, it's rated for 100A. Seems counterintuitive, but it's based on duty cycle, as a service entry feed is rated for 85% load on average (if I remember the number right). But a branch circuit has to be capable of the full amperage 100% of the time. Lots of little tidbits in the code book if you have time to read it.
Even though #12 wire is rated for 20A, the wire should NOT be loaded to more than 80% capacity, for continuous duty, and that's why I'd go with #10 in this case...
SR
After reading these posts and a PM or so, I pulled my #12 out and did run a #10-3 wire with ground. I think the AC I get will be no more that 17-18K Btu so it should be good. I probably could have used a 10-2 wire, but I read someplace that the 10-3 is needed for 120v electronics on the unit. It doesn't really matter now because a 10-3 should handle any wall AC I get unless it's a monster.
   / Wire Amp size in Garage #18
10/3 was the right choice, good for you for doing it RIGHT in the first place!!
SR
   / Wire Amp size in Garage #19
When dealing with smaller AC units a rule of thumb is 12,000 BTUs cooling capacity = 1 HP = 13-16 Amps at 120V. depending on efficiency factor, for compressor motors. For 240 V amps are X .5. In my old refrigeration days I experienced household/light commercial voltages as low as 90 V and those old heavy motors just ran hotter, not so today. Heat pumps; you have to look at the auxiliary electric heaters as they often exceed the motor load. Theoretically the circuitry does not allow both to run at the same time; but, sh** happens. The new high efficiency units probably run less amps than 1 HP used to. We don't need AC here in Puget Sound.
Caveat: the above info may not be totally accurate but it is a close approximation. Todays imports may be using terminology and metrics based on calories, dynes, or joules, instead of BTU.
Ron
John Deere 700 Hydraulic Hay Rake - Durable Side Delivery Rake for Efficient Windrowing (A52128)
John Deere 700...
Western Snow Plow with Brackets (A50515)
Western Snow Plow...
2018 CATERPILLAR 326FL EXCAVATOR (A51242)
2018 CATERPILLAR...
2008 FORD F-750XL SUPER DUTY ASPHALT DISTRIBUTOR T (A51243)
2008 FORD F-750XL...
John Deere 693 Corn Head (A50514)
John Deere 693...
2007 Terex RS350 Soil Stabilizer/ Reclaimer (A49346)
2007 Terex RS350...