Years ago I had a 5500/6500 surge gas unit. It would NOT run my well pump and my oil fired boiler at the same time. Well pump was 220v, boiler was 110v. Since the load of the boiler could not be shared by both legs of the generator, one of the generator output breakers would trip when either load would try to start with the other already running.
Remember, each leg of the generator can only produce half the rated output. You have to look at the loads, including the starting currents, and try to distribute them evenly over both legs. You really can't think of a generator as a single unit with a total of X watts. It really is two individual legs, each with a max capacity of X/2. You have to keep within the capacity of each of the legs. Your 220 loads are shared by both legs, but each 110 load has to go to one or the other leg. So you divi up your 110 loads among the two legs as best you can, but it's never perfectly balanced, So if you are driving multiple 110 loads, it is almost impossible to get the max rated capacity of a generator. Hence the need to buy a generator rated a little higher then the sum of all your loads.
I found some motors require their starting current for longer periods of time than others. For example a well pump or a furnace blower motor require starting current for longer than a refrigerator motor. Unfortunately inexpensive portable gas units don't seem to be able to deliver their rated starting current for as long as some loads require.
Be careful buying a inexpensive unit that just meets your calculated requirements. There is risk that it won't deliver the power you need for the duration you need. It sucks to buy a unit, get it home, hook everything up only to find out it won't do the job. Don't ask how I know...