Water supply / pressure problems - suggestions?

/ Water supply / pressure problems - suggestions? #21  
ByronBob, the other thing not yet metioned is that the smaller the pipe for any length means a higher water velocity for a given GPM. This creates a situation that can ge damaging to electric valves, 90's, tee's and even to the pipe itself in the event of valves closing sudenly.
 
/ Water supply / pressure problems - suggestions?
  • Thread Starter
#22  
Hey everyone, thank you for the posts thus far.

OK.. So my pipe size stinks.... Still, I might be dense here but since the water company's feed to the manhole looks only to be 3/4 inch metal, how can my 1 inch plastic pipe be the limiting factor? Is it just the resistance the pipe provides to the volume of water being pushed? I understand that a larger pipe would not provide the same resistance per the volume of water moved.

Anyway, let us make the assumption that the wife won't let me trench up the lawn to put in a new pipe. /forums/images/graemlins/mad.gif Even that would not solve the problem of the frequent utility interruptions. So....

Could I put a couple of those 120 gallon retention tanks in series followed by a pump to a bladder tank connected to the house supply? Do those retention tanks handle pressure so I don't need a valve to shut off the flow from the municipal feed when they are full?

Are there downsides to this?

Having 240 gallons on tap along with the water in the bladder tank would sure mitigate the problems related to utility outages.

Thanks again.. Ron
 
/ Water supply / pressure problems - suggestions? #23  
Ron,

At 10 gpm flow, this would be say a shower and filling a washer, you would loose 55.5 psi for the 1500 feet of pipe. This does not include the loss of pressure through the water meter, valves, difference in elevation, etc. If the street pressure is day 60 psi, you can see you will have less then 5 psi on your end of the line.

When you only flow say a shower the flow is perhaps 3 gpm, the more flow the higher the loss of pressure. Based on the table Rat included in his post, for schedule 40 plastic pipe at 1 gpm the loss is .03 for every 100 feet, at 5 gpm it is .66, 7 1.24, and 10 gpm 2.40, as the flow increases so does the friction loss through the pipe.

As far as putting in the tanks, I will leave that for others, but it sounds like a fix. It would mean less tractor seat time /forums/images/graemlins/mad.gif
and not as much fun as digging a 1500 foot trench 3-4 feet deep. /forums/images/graemlins/grin.gif /forums/images/graemlins/grin.gif
 
/ Water supply / pressure problems - suggestions? #24  
There is a difference between 120 gallon tanks and 120 gallon pressure tanks. Much of a pressure tank is air. You will not be getting 120 gallons of water. TO call it a storage tank is really not quite accurate. It does indeed have water in it, it's purpose is not to store water so much as pressure. In situations where there is an inadequate supply of water, an in ground tank is used where we are. The cold climates will probably be different. On a well with 2 or 3 gpm, we are required to install a tank. The tank is usually around 3000 gallons. In it is a pump to supply the domestic water. The well pump keeps the tank full via a float switch. It has 24 hours a day to keep it full.

It is not unusual to have a 3/4" tap to the water utility line. Again, look at the water friction loss chart. It will show you the PSI loss for 100' lengths of pipe in a given size and material. 6' of 3/4" pipe at 60 PSI may well provide you with 30+ gallons per minute. 1000 feet of the same pipe will drop the pressure drastically and definitely drop the GPM by a considerable amount. Change the run at the 3/4" utility tap to 2" or larger (depends on overall length) and the PSI drop will be almost negligible. Pressure is close to the same, GPM is similar as well.
 
/ Water supply / pressure problems - suggestions? #25  
I don't know if a pump would allow you to have pressure on both sides of it. For example a well pump draws water on one side of it to pressurize the other side. It uses a one way flow control valve to shut off the water flow when it's not needed. If you put a pump in and there was pressure on both sides of the system I don't know if you can do that.
Another thing that water companies bark about is modifying water supply in this method. The tanks would give you more volume but no more pressure.
I don't know the answer to this question per se but my tank in the basement which is 120 gallons is made out of fiberglass resin and will handle at least 100psi. Very lightweight and strong.
 
/ Water supply / pressure problems - suggestions? #26  
Not sure what your asking. If your pump has a supply with 60 PSI of pressure, thats a bonus. You want a pump to have a supply pressure, some require it. On the outlet side of the pump will be a check valve. Most water companys will require you to install a double check valve prior to supplying water to the pump.
 
/ Water supply / pressure problems - suggestions? #27  
</font><font color="blue" class="small">( 6' of 3/4" pipe at 60 PSI may well provide you with 30+ gallons per minute. 1000 feet of the same pipe will drop the pressure drastically and definitely drop the GPM by a considerable amount.)</font>

I am certainly dense on this topic, because this doesn't make sense to me.

How can the GPM change due to the length of the pipe? I understand that the pressure will drop, due to friction with the inside of the pipe, but water is an incompressible substance, and if the pump is putting 30 gpm into one end of the pipe, then 30 gpm has to come out the other end. /forums/images/graemlins/confused.gif /forums/images/graemlins/confused.gif

Is this loss of gpm what causes a fixed displacement pump to burn out? Is this what is meant by "Head pressure"?

Just looking to understand what this all means.

Thanks,
Dave
 
/ Water supply / pressure problems - suggestions? #28  
Not sure what this relates to as I have no idea about GPM and water pressure other than... If I am in the shower and somebody flushes a toilet do I get scalded.

We are 900 feet from our meter with 3/4 PVC put in by the previous owner. From what everyone is saying this can't possibly work but our water pressure isn't any worse than I have experienced when we were in town. Ya if the wife flushes the toilet while I am in the shower the water gets a little warmer but not bad enough for me to even think about replacing 900 feet of water line. I would be tickled if it was 1 inch. Not sure why it's working as well as it is unless we have some really high pressure at the meter.
 
/ Water supply / pressure problems - suggestions? #29  
The pump may be capable of 30 GPM with no head, but if it has a head pressure, that figure will change. Water pumps can be put into a situation of zero GPM, the pressure will go to the maximum the pump can produce. They are not like the fixed displacement gear pumps used in tractors to pump hydraulic fluid. In a centrifigal pump, that may about 30 to 90 PSI depending on the design. In that situation, the impeller will simply spin in the pressurized cavity. It will eventually heat the water sufficiently hot enough to collapse the threads of most PVC fittings. In a well pump, you can have multiple stages that continue to feed each stage an increase in pressure. It's not unusual to see these pumps go well over 200 PSI. The GPM on your well pump will depend on it's HP and of course, the head pressure. A 3/4 HP pump with zero head may be able to pump 25 gal/min but placed in a well 300' deep with a head pressure of 150PSI just to get it to the surface not to mention pressurizing the system, it won't give you 25 GPM, it will be something less then that. Look a t a pump manufactuers web site. It gives the GPM for a given pump based on head pressure.
 
/ Water supply / pressure problems - suggestions? #30  
Look at it this way. Try blowing water through a garden hose and then try blowing it through a straw. You could have 60psi set up for both but the size of the line restricts the water pressure. And just like electricity water looses pressure by length away from it's source.
 
/ Water supply / pressure problems - suggestions? #31  
Rat

Could he put a shallow well pump in with the W/A pipe on the intake side and put a bladder tank with an 80 gallon retention tank on the supply side? I thought with shallow well pumps the intake water was dead. I didn't know if he could do something like this or not?
 
/ Water supply / pressure problems - suggestions? #32  
Personally, if I have a supply that is good and it's just a matter of increasing pipe size, that is what I would do and forget anything to do with a pump. Pumping water can be expensive especially if you use it to irrigate. Increasing the pipe to 2" may cost 3 or 4 times more then putting in 1" PVC but it's still pretty cheap.

I have yet to ever use a shallow well pump. Out here they are pretty much obselete. A standard irrigation boost pump will supply a tremendous supply of water and can actually draw water if no pressurized supply is available. They are typically limited to about 60 PSI. Where I live I have a well for my domestic needs and have what is called ditch water for my irrigation. It is untreated snow runoff where the pressure is captured and brought to us in large pipes. We tie into it for a given charge and supply. We buy it in miners inches. A miners inch is about 11 gpm. Our pressure is about 120 PSI. It is a great and effective way to irrigate, something we need to do here in California in the summer as after May, we just don't get any rain. Some folks get the water but no pressure and must pump. To do even a few acres is very costly and can add about $300 or more to your electric bill each month.
 
/ Water supply / pressure problems - suggestions? #33  
Dave, the easiest way I've found to think about it is that your 30 gpm pump will put out 30 gpm with zero pressure on the outlet side. As you add pipe to the outlet side this creates a pressure loss when you pass water through it. Think of this pressure loss in the pipe as a back pressure against the pump and you will see why the flow drops. If the outlet line is too small or too long the pressure losses within the pipe can be higher than the pump is capable of putting out and there will be no water coming out the end of the line.

A positive displacement pump is usually a high pressure pump and will generally keep pumping until it blows something up, either the discharge lines, shut-off valve or itself. That's why they are usually fitted with a pop-off valve to bleed the pressure down before it becomes a "bomb". Centrifical pumps, on the other hand, are lower presuure pumps that will put out their maximum working pressure and then quit producing. You can shut the valve on a discharge line and it will pressure up the line to it's max working pressure and continue to spin to keep it at that pressure. That continued spinning with no throughput builds up heat and leads to burn out.

I don't know if this will be of any help. /forums/images/graemlins/confused.gif
 
/ Water supply / pressure problems - suggestions? #34  
</font><font color="blue" class="small">( Look at it this way. Try blowing water through a garden hose and then try blowing it through a straw. )</font>

More importantly for him is the following.

Head down to your local home store. Find two identical looking 1/2 inch hoses, one 25 ft and the other 50 ft. Peer around and make sure noone is watching. Wrap your lips around the metal end of the 25 footer and blow. Do the same to the 50 footer. Maybe a 100 footer if you can find one.

Feel the difference?

That "back pressure" or "resistance" limits flow. Your flow is a combination of pressure and volume. Decrease flow and you decrease one or the other or both.

This is basic physics and applies to a huge number of fields. It applies to water pipes. It applies to electrical wiring, both for your mains power wiring and your cable tv.

You ARE going to have losses. That is unavoidable. You can either crank up the initial pressure/voltage/signal so the you have the desired pressure/voltage/signal at the desired flow/current or you can increase the size of the pipe/wire/cable to reduce the loss. Alternately you can boost the pressure/signal one or more places along the transmission path.

If it were me, I would run bigger pipe. You are way undersized. A single booster pump risks bursting the pipe close to the pump. It has got to cost a lot more to install multiple booster pumps than it would cost to upgrade the pipe. It DEFINATELY costs more to maintain multiple booster pumps than to ignore a bigger pipe.
 
/ Water supply / pressure problems - suggestions? #35  
A great example. Around my place, if I use 75' of 5/8" hose (I only have one) on my largest RainBird impacthead which uses about 12 GPM, my throw is drastically dimished. When I go to my 3/4", it gets back to the diameter it can achieve. If I tie two 3/4" hoses together there is a noticeable drop. If you ever have been to a park or golf course, typically you will see 1" hoses and often times well over 100'. I can guarantee you it is not because they enjoy dragging the extra weight around.

"Find two identical looking 1/2 inch hoses, one 25 ft and the other 50 ft. Peer around and make sure noone is watching. Wrap your lips around the metal end of the 25 footer and blow."

Do you know where that end has been? /forums/images/graemlins/grin.gif
 
/ Water supply / pressure problems - suggestions?
  • Thread Starter
#36  
Hi guys... Forgive me bringing up an old post but wanted to give you an update. We had a plumber check out our supply issues and they recommended we use a booster pump to improve pressure. I did the research myself and purchased a lesser expensive solution to see if we got good results. If this hadn't of worked, I would resort to trenching a new supply line.

On Saturday, a friend of mine helped me to install one of these Davey Pumps in my basement. We used the HS18-30HT1 model which is rated at 22+ GPM. The pump is very quiet and provides ample pressure and volume for our home. We are very happy at this point that filling a bath tub takes only about 4 minutes.

It doesn't address my supply issues to have water available to me for use when the municipal supply is interrupted but I plan to address that later this year.

Thank you again for all your help and input.

Ron
 

Marketplace Items

2019 GALYEAN EQUIPMENT CO. 150BBL STEEL (A58214)
2019 GALYEAN...
2019 Toyota Corolla Sedan (A55853)
2019 Toyota...
2025 Kubota SVL75-3HFWCC High Flow Cab Track Loader - 70 hours
2025 Kubota...
2019 Ram 2500 4x4 Crew Cab Pickup Truck (A60352)
2019 Ram 2500 4x4...
DRESSER GALION 712 TANDEM ROLLER (A62129)
DRESSER GALION 712...
2016 Ford F-150 4x4 Crew Cab Pickup Truck (A61568)
2016 Ford F-150...
 
Top