Simple Electrical Question (hopefully)

   / Simple Electrical Question (hopefully) #11  
The answer is not really simple. Well, it could be but there are a lot of things to look at here. You did not mention if the cable has Aluminum or Copper conductors. Could make a difference here. You didn't say how many "several years ago" was. The conductors could be 60ー, 75ー or 90ー rated. Are they type UF, THWN, THHN, THWN-2, XHHW, XHHW-2? It makes a difference.

Let's say it's copper type THWN-2 and they were 90ー rated, such as in type NM-B cable.
First, NEC Article 110-14 says if the circuit is under 100A then the conductors need to be used at their 60ー rating, unless all terminations in the circuit carry a higher rating. #6 copper at 60ー is able to be used at no more than 55A. However, there is a way out here. According to NEC 240.6, 55A is not a standard fuse/breaker size so you are allowed to round up the the next standard size which is 60A. So if you had a 6-3 type NM-B cable run, you are good to go with a 60A breaker on a 45A load.

Now, let's say it is Aluminum conductors.
#6 at 60ー is only good for 40A according to NEC 310.16 and 110.14

So I need more info to accurately answer your question. Post what cable type was run and I'll try to help more.

Great Post to help a friend!!!
 
   / Simple Electrical Question (hopefully)
  • Thread Starter
#12  
Thanks a bunch, I'll be glad to use the tub to it's max features.
 

Tractor & Equipment Auctions

(2) CAM2 HI TEMP LITHIUM COMPLEX GREASE DRUMS (A54757)
(2) CAM2 HI TEMP...
UNUSED LANDHONOR LHR-MS0608 METAL SHED (A54757)
UNUSED LANDHONOR...
UNUSED LANDHONOR 82" FORK EXTENSIONS (A54757)
UNUSED LANDHONOR...
2015 Land Rover Evoque SUV (A53424)
2015 Land Rover...
UNUSED TELESCOPIC LADDER - 2.5M+2.5M (A54757)
UNUSED TELESCOPIC...
2019 CATERPILLAR 926M WHEEL LOADER (A52705)
2019 CATERPILLAR...
 
Top