I am looking for some feedback on a project I am considering. My home was just placed on town sewer and is allowing people to reuse their septic tanks as cisterns for irrigation purposes. I already collect all my roof runoff and carry it to daylight on a low part of my property. I am fortunate in that the drain line runs right past the septic tank. It would be trivial to connect it to the tank.

My home currently has an in-ground system using Hunter PGP heads. Each zone has 6 heads. I can configure each head to run anywhere from .1 to 5 GPM. I figured 2gpm is a good starting point, thats 12gpm per zone.

These heads can run as low as 30psi, so I can start with that. The tank bottom is 8ft below grade.

Using the formula to calculate HP=QHS/e3956
Where
Q=flow in gpm; H=head in feet;S=1 for water; e=efficiency(80%); 3956=conversion factor to end up with HP

To determine Head feet from psi (@ 30 psi and 50 psi)
30 psi*2.307psi/ft= 69 ft; total H=69ft+8ft.
(50 psi*2.307psi/ft=115ft: total H=115+8ft)

12gpm x 77 ft x 1 /(0.80)x 3956 = .29HP
(12gpm x 123 x 1 / (0.8) x 3956 = .47HP)

So this would indicate a ½ hp submersible pump would work to drive my system. Would an off the shelf sump pump from the big box store work in this application? Would a sump burnout with this much use?

Since my septic is only 1000gallons, I think I can really only use it to water 2 zones. 1000 gallons at 1" per week will not cover my ½ acre of lawn in August.

Thoughts?
 
   / septic to cistern for irrigation #2  
I guess that the septic has been completely cleaned so no parts will clog nozzles! Could you use the water for a drip system instead? That might allow for more efficent use of the limited water amount.
 
   / septic to cistern for irrigation
  • Thread Starter
#3  
Tank was cleaned and dysinfected according to Board of Health regulations. Water in tank is clear and does not have the tell-tale septice smell. You can assume that no such solids exist in the tank. However, measures will be taken to prevent leaves and other material from clogging the pump.
 
   / septic to cistern for irrigation #4  
is this lawn irrigation or agricultural irrigation?
 
   / septic to cistern for irrigation #7  
I also connected to the town sewer 8 years ago. I use my old system for storm water management, not for irrigation but just to control the roof water and also some surface drains along the back of my house where the water during a heavy rain would pond up and come in my window wells.

My tank is 75 years old and very small (the leach field drains perfectly though) so it would not work for irrigation, at a 1000 gals that makes it more practical.

JB
 

Tractor & Equipment Auctions

2003 VOLVO VNL TANDEM AXLE SLEEPER TRUCK (A54313)
2003 VOLVO VNL...
Informational Lot - Shipping (A55218)
Informational Lot...
2008 DOOSAN G25 GENERATOR (A52472)
2008 DOOSAN G25...
2015 Volvo VNL 64T (A55218)
2015 Volvo VNL 64T...
Deer Gates (A53424)
Deer Gates (A53424)
3-Point Hitch Root Grubber - Heavy-Duty Tree and Stump Puller for Tractors (A55301)
3-Point Hitch Root...
 
Top