"Close" to 60 should be fine for most motors. Microwaves tend to be a finicky appliance, and some UPS units have trouble outside of 58-62Hz.You don’t have a well pump or other 60hz AC motor in your house?
Those certainly care about 60hz being under frequency
It's been a long time since I've run across an A/C induction motor that didn't read 50/60 hz on the motor plate.You don’t have a well pump or other 60hz AC motor in your house?
Those certainly care about 60hz being under frequency
Yep!"Close" to 60 should be fine for most motors. Microwaves tend to be a finicky appliance, and some UPS units have trouble outside of 58-62Hz.
@CalG I've run a WINCO PTO generator for a week more or less straight for 18 hours a day. My only tweak was to put the tractor in 1,000rpm PTO, and then drop the engine speed until the PTO was running 540rpm to save fuel as the tractor had a ton of HP, relative to what the generator needed.
All the best,
Peter
You’re confused. Most American market motors are designed for 60hz.It's been a long time since I've run across an A/C induction motor that didn't read 50/60 hz on the motor plate.
When I first tried running my 3/4 hp deep well pump off my 5k generator, it couldn’t reliably start it. Often just bogged the generator down until a breaker would trip, or I would kick off the breaker."Close" to 60 should be fine for most motors.
One hz? That is one fussy well pump motor.When I first tried running my 3/4 hp deep well pump off my 5k generator, it couldn’t reliably start it. Often just bogged the generator down until a breaker would trip, or I would kick off the breaker.
The generator was factory set at 60hz no load. When I measured, it dropped to 59hz with a moderate load, and 58.5hz when bogged by the stalled deep well pump.
I adjusted the no load to 61hz, no load. During startup there’s a quick drop to 60hz.
Deep well pump starts and runs perfectly now.
Deep well pumps can have enormous starting currents depending on well depth, static water level, and number of check valves