Kohler 10kw propane genset with Wakasha 4cyl.

   / Kohler 10kw propane genset with Wakasha 4cyl.
  • Thread Starter
#11  
I will get a photo of that other tag next trip out there. I'm betting its 4 pole 1800 rpm. Seems logical, I don't see any room for gearing. I'm learning, generators new to me.
 
   / Kohler 10kw propane genset with Wakasha 4cyl.
  • Thread Starter
#12  
I googled using littlbills post as food for knowledge.

Question:
Is a 1800 rpm generator 4 pole.

AI Overview
Learn more

1500/1800 Rpm High Efficiency 3 Phase 4 Pole Diesel Power Permanent Magnet  Generator Magnetic Alternator

Yes, an 1800 rpm generator is typically a four-pole generator when producing 60 Hz power. Specifically, a 1800 rpm generator using a 4-pole alternator will generate 60 Hertz power. Conversely, a 3600 rpm generator will have two poles.

It says 1800rpm on the engine tag on the genset. Not that I didn't believe Littlebill ;)
Thinking about it 1800rpm will be a nice easy cruising speed.
 
Last edited:
   / Kohler 10kw propane genset with Wakasha 4cyl. #13  
Load that baby up, and it's going to be thirsty on propane.

SR
 
   / Kohler 10kw propane genset with Wakasha 4cyl.
  • Thread Starter
#14  
It does have a good size fuel feed line and regulator. It appears that it was hard plumbed in with 1" iron pipe. I have two 100# tanks.
I wouldn't be bothered by filling one of those daily rotating the two tanks just during outages if need. Our outages are usually less than a day. I'm on a good size trunk line

That would seem to be a lot of fuel usage.
I could convert it to gasoline.
It seems propane would be more efficient.
Are the propane Generac systems thirsty?

I could never see a payback on the cost of an installed Generac system. Unless the grid fails for ###.
 
   / Kohler 10kw propane genset with Wakasha 4cyl.
  • Thread Starter
#16  
Well, no gasoline then 😵‍💫

The tag says 54.8 amps per term. If that's per terminal with two terminals at 240 volts that's 108 Amp max. So, this generator is basically a 100 Amp service.
Is that right?
I wouldn't go much past 80 percent of that.

I'll stick with propane. (y)
Converting my Hyster 8000# lift to propane worked out well.

I could see the generator working pretty hard on a cold winter day. Not using stove or dryer without turning the furnace off.
 
   / Kohler 10kw propane genset with Wakasha 4cyl. #17  
Well, no gasoline then 😵‍💫

The tag says 54.8 amps per term. If that's per terminal with two terminals at 240 volts that's 108 Amp max. So, this generator is basically a 100 Amp service.
Is that right?
No. It’s single phase. 54.8 amps is it.
You don’t double the current number.
 
   / Kohler 10kw propane genset with Wakasha 4cyl.
  • Thread Starter
#18  
Ok, I need to do some math. The furnace and the coffee maker is all we really need.
 
   / Kohler 10kw propane genset with Wakasha 4cyl.
  • Thread Starter
#19  
On a240 generator you have two lines. Two terminals. Thats why I doubled Amperage x-2 two,,terminals.

I. Found this thread. Post#5
 
Last edited:
   / Kohler 10kw propane genset with Wakasha 4cyl. #20  
54.4 amps per leg x 115 volt = 6.25 KVA
or
54.4 amps x 230 volts = 12.5 KVA or with a power factor of 0.8 10KW.

2 pole generator needs 3600 rpm for 60 Hz power
4 pole generator needs 1800 rpm
6 pole generator needs 1200 rpm
8 pole generator needs 900 rpm
10 pole generator needs 720 rpm

The 10 pole used to be fairly common in the oil and gas processing plants often with several in parallel operation.
Using large inline 6, 8, 10 and even 12's and even a few V configure natural gas engines.
 

Tractor & Equipment Auctions

Hyster H225E (A47384)
Hyster H225E (A47384)
2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
2000 Wabash National 53ft T/A Dry Van Trailer (A51692)
2000 Wabash...
2015 PETERBILT 389 TRI-AXLE MID-ROOF SLEEPER (A52472)
2015 PETERBILT 389...
Tandem Axle Rear Truck Frame (A51692)
Tandem Axle Rear...
2019 ExMark S-Series 72in Zero Turn Mower (A51692)
2019 ExMark...
 
Top