Bird I used to work on Ruud units, same as rheem, about 10 years ago. One thing that can happen is when you take the blower door off everything looks fine, but with the door closed and the fan running it can pull the insulation off the inside of the unit and restrict air getting into the blower itself. Is the blower clean? The blower is not hard to pull out, should be a plug with all the wiring connections in it, just unsnap it, should be 2 sheetmetal screws to remove and the blower unit slides out. Other than that pull the filter and look in the return duct and see if the insulation is coming loose and blocking the filter.
These things above are probably not happening if the pressures looked ok, and if they were happening you would probably have a coil freezing up. Also with the blower unit out you should be able to look up through the air handler and see the bottom of the coil (upflow I assume) and see if it is dirty.
Does your outside unit sit in a position with the sun directly on it? Does your outside unit have stuff growing near it possibly blocking air to it?
Aside from those things drill a small hole in the supply duct just ahead of the coil and see what your discharge air temp is.
These things above are probably not happening if the pressures looked ok, and if they were happening you would probably have a coil freezing up. Also with the blower unit out you should be able to look up through the air handler and see the bottom of the coil (upflow I assume) and see if it is dirty.
Does your outside unit sit in a position with the sun directly on it? Does your outside unit have stuff growing near it possibly blocking air to it?
Aside from those things drill a small hole in the supply duct just ahead of the coil and see what your discharge air temp is.