We're moved into our new house out in the country and I need to get a generator installed. The electrician wired an interconnect to the main panel with a power grid lockout, so I can manually switch the whole panel off the grid and over to the generator, then control individual circuits to tailor my load. The interconnect and lockout is setup with a double pole 100A breaker (so it can run 100A at 240V, or run two 100A legs at 120V).
From the breaker panel, we have a length of 2-2-2-4 aluminum wire run into our crawl space, and spooled up into a loop. Once I decide where to locate the generator outside the foundation, I can route the wire through the foundation where it needs to go and button everything down. There's at least a 70-100 ft run no matter where I go, which will cause about a 5V drop but that's tolerable.
Based on the wiring and breaker, the largest generator I could install would be 24kW, but that's on the ragged edge at full load so I'd probably never be able to run it 100% without tripping the interconnect breaker. So I'm eyeballing diesel generators in the 14kW to 21kW range. I still need to do a final circuit audit to figure what I can and can't run reasonably, and what to prioritize (well pump, fridge, HVAC blower are my top priorities). Trying to get current or power draw specs for the geothermal system to see if it's even within the realm of possibility. I'm definitely keeping an eye on fuel consumption rates too, as I'd like to be able to run for 4 days on a tank if possible.
I want to go diesel since it has (by far) the smallest footprint for the generator and fuel tank for a given run time, and we don't have natural gas out here or a reason to have propane. I'm looking at a 60-100 gallon diesel tank that mounts right under the generator itself.
For those who have installed diesel generators, what did you do for location relative to the house? Code says at least 4 feet from the foundation. I'd like to locate it where noise and exhaust are going to be the least offensive. Can the exhaust be modified to move it farther away or higher?
In addition to running the main wire through the crawl and mounting the generator next to the foundation, I also have a possible option of running the wire from the main panel out through an external wall and then under my driveway to a spot about 50 feet away. We're not pouring the driveway pad for another 2 weeks, so I could have some conduit ready to stick under the forms before they pour.
From the breaker panel, we have a length of 2-2-2-4 aluminum wire run into our crawl space, and spooled up into a loop. Once I decide where to locate the generator outside the foundation, I can route the wire through the foundation where it needs to go and button everything down. There's at least a 70-100 ft run no matter where I go, which will cause about a 5V drop but that's tolerable.
Based on the wiring and breaker, the largest generator I could install would be 24kW, but that's on the ragged edge at full load so I'd probably never be able to run it 100% without tripping the interconnect breaker. So I'm eyeballing diesel generators in the 14kW to 21kW range. I still need to do a final circuit audit to figure what I can and can't run reasonably, and what to prioritize (well pump, fridge, HVAC blower are my top priorities). Trying to get current or power draw specs for the geothermal system to see if it's even within the realm of possibility. I'm definitely keeping an eye on fuel consumption rates too, as I'd like to be able to run for 4 days on a tank if possible.
I want to go diesel since it has (by far) the smallest footprint for the generator and fuel tank for a given run time, and we don't have natural gas out here or a reason to have propane. I'm looking at a 60-100 gallon diesel tank that mounts right under the generator itself.
For those who have installed diesel generators, what did you do for location relative to the house? Code says at least 4 feet from the foundation. I'd like to locate it where noise and exhaust are going to be the least offensive. Can the exhaust be modified to move it farther away or higher?
In addition to running the main wire through the crawl and mounting the generator next to the foundation, I also have a possible option of running the wire from the main panel out through an external wall and then under my driveway to a spot about 50 feet away. We're not pouring the driveway pad for another 2 weeks, so I could have some conduit ready to stick under the forms before they pour.