Too many letters and numbers for me to convert.
Do I understand on the LPG chart that it would use 2.3 gallons per day at 50%? Trying to understand how long my 500 gallon tank might last.
Thanks.
Ok, a few things go into this.
1) your 500 gallon tank has a maximum of 400gallons in it.
2) as the tank gets empty, it cools off and the last portion may not be accessible because it can't boil off. (Better in the summertime, much worse in the winter time.) There are tables to look this up in most manuals.
3) as
@drumminj points out, that is 2.3gal/hr
4) 2.3gal/hr assumes that you don't load it up to full load, in which case, you probably want a smaller generator. Ideally, one that can run 80% load much of the time.
Bottom line: probably not more than four or five days, as little as two and a half, and up to seven or so depending on outside temperatures, and actual loads.
If you anticipate mostly small loads, and occasional large loads, a better solution might be to have batteries that can be recharged by the generator quickly, and run the small house loads for an extended period of time. That's likely to be the most fuel efficient solution.
All the best,
Peter