Generac 15KW generator engine tear down

   / Generac 15KW generator engine tear down #1  

pclausen

Veteran Member
Joined
May 9, 2008
Messages
1,472
Location
Nelson County, VA
Tractor
JD 5085M, Ford 1700, JD GT235
As I'm preparing to install a new 20KW generator at my mothers, I picked up the failed 15KW unit and took it home to tear down the engine in the hopes that I can fix it.

As per the other thread (Which 20KW whole house generator would you choose and why), the Generac tech that came out said the engine passed compression test fine, but that cylinder #1 had a 28% leak down and #2 had 48% leak down. 28% the cut off Generac uses to replace engines under warranty. The tech said the air appears to be escaping from the oil dip stick hole (dip stick removed). So that would likely indicate an issue with the pistons and/or rings.

I started by removing the top and front covers. This whole genset looks very clean:

15kwgenny-10.jpg


Close up showing the model number:

15kwgenny-11.jpg


Here it is after removing the muffler, control board and "firewall":

15kwgenny-12.jpg


Shrouds, intake manifolds and air box removed:

15kwgenny-13.jpg


#1 valve cover removed. Top of valve train looks ok.

15kwgenny-14.jpg


#1 piston:

15kwgenny-17.jpg


#1 cylinder wall. You can still make out the honing marks:

15kwgenny-18.jpg


#2 piston:

15kwgenny-15.jpg


#2 cylinder wall. Again, you can readily make out the honing cross pattern:

15kwgenny-16.jpg


#1 head on left, #2 on right:

15kwgenny-19.jpg


Closeup of #1 exhaust valve. Any idea what that white buildup is?

15kwgenny-20.jpg


#1 exhaust valve stem. Whatever that buildup is, it doesn't look good.

15kwgenny-22.jpg


The head gaskets looked fine. I don't see any obvious signs that the piston rings are shot and causing leak by, yet the leak down test seemed to point in that direction. Could the exhaust valves be the only culprit here?

I'm wondering if I should continue with tearing down the bottom end, or fix the heads first and see if that fixes things?

From what I'm seeing so far, I would say the odds are good that I can get this engine running well again. What do you guys think?
 
Last edited:
   / Generac 15KW generator engine tear down #2  
Rebuild the heads. Looks like a run lean condition. Did it run rough? Seems to be a possible air leak.
Can you give me a close up on the spark plugs?
 
Last edited:
   / Generac 15KW generator engine tear down #3  
Wow- so they let you keep the failed under warranty unit? That is quite a good deal. Worst case scenario is that you could buy a pto gearbox and turn it into a tractor PTO powered unit.

So, what was the issue? Did it simply fail to start when the power went off? Or did it just not have enough horsepower to produce the full 15KW?

The cylinders look nice. I agree that you may be OK with just removing and cleaning up that exhaust valve. Was it using any oil? If not, the black deposits would make me think that it was running a bit rich if it was a gasoline powered engine, but I am not that familiar with natural gas/propane engines.

What weight of oil did you have in it? Maybe you could get by with a thicker weight oil like 20w-50. Thicker oil would slow leakdown and reduce blowby, but would wear the bearings a bit more when starting in really cold weather (and would likely slow the cranking speed).
 
   / Generac 15KW generator engine tear down #4  
Do you mind if I post these photos on another site?

To me it looks like there's an additive in the lpg that the motor doesn't like. You should be able to rebuild those heads for pretty cheap. New guides and seals, valve job and you're golden.
 
   / Generac 15KW generator engine tear down
  • Thread Starter
#5  
Looks like a run lean condition. Did it run rough?
It didn't really appear to be running rough. It was last serviced on 12/6/2011, at which time new plugs were put in.

Can you give me a close up on the spark plugs?
Here you go (#1 plug)

15kwgenny-32.jpg
 
   / Generac 15KW generator engine tear down
  • Thread Starter
#6  
Wow- so they let you keep the failed under warranty unit? That is quite a good deal.
I wish! This 15KW generator was installed in July of 2004, so it is way out of warranty. Instead of having the service company replace the engine to the tune of $2000 with only a 90 day warranty, we decided to instead get a brand new 20kw unit and try to fix this one ourselves.

So, what was the issue? Did it simply fail to start when the power went off? Or did it just not have enough horsepower to produce the full 15KW?
The main issue is that it would burn a quart of oil every 8 hours or so and then shut down. Even with keeping up and adding oil every 8 hours, after running for 3 days straight, it was no longer able to start a 4ton AC unit.

What weight of oil did you have in it?
5W-30 Mobil One synthetic. BUT, when I first refilled it, I used straight 30 weight. Once I read the manual I realized that 5W-30 synthetic should be used. So I drained what little oil was in it, and refilled with Mobil One.

I should also mention that the break-in procedure was not followed. It came factory filled with organic break-in oil. You are supposed to run it for 1 hour at 25% load, then 1 hour at 50%, then 1 hour at 75%, and finally 1 hour at 100% load. Instead, this generator was put into service with the break-in oil in it for the first 3 years of its life. From that point forward, the proper oil was used.

Despite that oversight, the generator had been performing with no issues until this recent Mid Atlantic storm which caused a 5 day power outage, where the generator shut down after 16 hours and then every 8 hours after that due to low oil pressure.
 
Last edited:
   / Generac 15KW generator engine tear down
  • Thread Starter
#7  
Do you mind if I post these photos on another site?
Sure, no problem at all.

To me it looks like there's an additive in the lpg that the motor doesn't like. You should be able to rebuild those heads for pretty cheap. New guides and seals, valve job and you're golden.
I hope its not some additive in the lpg. If that was the case, I would think a lot of generators in my region would suffer from this issue.

I noticed that only the intake valves have seals:

15kwgenny-31.jpg


I don't think the guides are replaceable, at least I don't see a part number for them in the Generac manual.

Here's a close up of the #1 valves after I removed them. It looks like oil deposits on the intake valve.

15kwgenny-30.jpg


So would my best bet be to take the heads and associated parts to a small engine repair shop and have then redo them?
 
   / Generac 15KW generator engine tear down #8  
It didn't really appear to be running rough. It was last serviced on 12/6/2011, at which time new plugs were put in.


Here you go (#1 plug)

15kwgenny-32.jpg

That plug does not look like a cylinder burning a quart of oil in 8 hours. That plug is too new.
 
   / Generac 15KW generator engine tear down
  • Thread Starter
#9  
That plug does not look like a cylinder burning a quart of oil in 8 hours. That plug is too new.
I agree they do look quite new. I'll check w/ the Generac tech. He might have changed them when he did the compression/leak down test. That would mean these plugs only have about 10 minutes of run time on them.
 
   / Generac 15KW generator engine tear down #10  
I'd take the heads to a small engine guy and have him do a valve job on them.. Then put them back on.. Set the intake and exaust to .076mm Set at TDC cold..
Then I would do a oil and filter change useing 5w-30 syn... "we use mobile1" then run the unit for a few hours change it again.. then try a long run.. I'm betting you won't burn any oil.. :)
 

Tractor & Equipment Auctions

Land Honor Skid Steer Hay Accumulator (A50515)
Land Honor Skid...
BANDIT 4680 MOBILE GRINDER (A51242)
BANDIT 4680 MOBILE...
2021 CATERPILLAR 259D3 SKID STEER (A51242)
2021 CATERPILLAR...
2016 John Deere TS Gator Utility Cart (A48082)
2016 John Deere TS...
2018 GENIE GTH-636 TELESCOPIC FORKLIFT (A51242)
2018 GENIE GTH-636...
2018 CATERPILLAR 299D2 SKID STEER (A51242)
2018 CATERPILLAR...
 
Top