Gas Backup power didn't back us up!

/ Gas Backup power didn't back us up! #1  

Pilot

Veteran Member
Joined
Nov 20, 2004
Messages
1,224
Location
Oregon
Tractor
JD 770, Yanmar 180D, JD 420 (not running), had a Kubota B6200
We have gas water heater and gas furnace. Lost power for 5 hours a few days ago. Fired up the generator, hooked it up as usual and the furnace fan ran as usual, but the gas in the furnace didn't fire up. And the fan blew cold air. Water heater didn't fire up either. Checked the propane tank & it was at 55%. The way our system has always worked was when we fired up the generator, the furnace fan blew air, the burner came on and all was nice & toasty. The water heater doesn't need electrical power so the gas should heat the water but it didn't.

But when the power came back on both units fired up by themselves and we magically got both warm air and hot water!

What kind of failure could account for both systems to quit, but worked fine when the power came back on?
 
/ Gas Backup power didn't back us up! #2  
Regulator froze up
 
/ Gas Backup power didn't back us up! #4  
Propane generator? If so there may not be enough fuel in tank to run the generator along with everything else, or more likely the regulator isn't adequate.
 
/ Gas Backup power didn't back us up! #5  
It doesn’t explain the hot water if that truly has no electrical connection but our newer high efficiency furnace won’t open the gas valve if the neutral is not grounded (as is the case on most portables).

If determined the cause by the indicator lights on the furnace control board flashing out a code and looking up the code on google.

If the gen and the appliances are both fed from the same propane supply my guess is there was insufficient pressure either from the regulator freezing as the previous port suggests or the tank pressure was too low with the generator running and low ambient temperature.
 
/ Gas Backup power didn't back us up! #6  
You don't really say how the generator is hooked up,,,

The furnace could be operating from two different circuits,,, and possibly you only have one of those on the generator switch over,,,
 
/ Gas Backup power didn't back us up! #7  
We have gas water heater and gas furnace. Lost power for 5 hours a few days ago. Fired up the generator, hooked it up as usual and the furnace fan ran as usual, but the gas in the furnace didn't fire up. And the fan blew cold air. Water heater didn't fire up either. Checked the propane tank & it was at 55%. The way our system has always worked was when we fired up the generator, the furnace fan blew air, the burner came on and all was nice & toasty. The water heater doesn't need electrical power so the gas should heat the water but it didn't.

But when the power came back on both units fired up by themselves and we magically got both warm air and hot water!

What kind of failure could account for both systems to quit, but worked fine when the power came back on?

You said you have a gas water heater and a gas furnace, but you didn't say if they were natural gas, or if they were propane.

You said you have a generator and fired it up and hooked it up usual, but you didn't say if the generator is propane, natural gas, gasoline, or diesel powered. Also, what does hooking up the generator as usual entail?

You said you checked the propane tank and it was 55%, so we know you have propane, but we don't know what all runs on propane.

;)

So....

A little more info would be useful for troubleshooting. :thumbsup:
 
/ Gas Backup power didn't back us up! #8  
So, pull the main breaker, get the generator on-line again and see if the same symptoms appear. If so, then your transfer switch, feed, neutral or ground wiring is the culprit. Furnace fan would probably be 120v. Gas coils from another circuit that's not enabled ?
 
/ Gas Backup power didn't back us up! #10  
Are your pilot lighters on the generator?

Ralph
 
/ Gas Backup power didn't back us up! #11  
if the furnace and water heater are fairly new they probably have hot surface or intermittent ignition systems. Those require a good ground to operate and the correct polarity and good clean power. Without a good clean power they will not ignite. If no ignition the gas valves will not open.
 
/ Gas Backup power didn't back us up!
  • Thread Starter
#12  
if the furnace and water heater are fairly new they probably have hot surface or intermittent ignition systems. Those require a good ground to operate and the correct polarity and good clean power. Without a good clean power they will not ignite. If no ignition the gas valves will not open.

To clarify:
"Regulator froze up" Temp was about 30 degrees. Was windy, but only about 4 or 5 mph. If that was the culprit, why would both furnace & water heater come back on immediately when power came on and continue with no problems? No delay, both started working right away as soon as power came on.

We had lights on & wife cooked dinner on the microwave.

Gas is propane, tank was 55% full.

Cable runs from generator to transfer switch.

Generator is gasoline fueled, rated at 7000 watts. Runs well, freezer, furnace fan, microwave, some lights (LED's).

When power failed lights flashed repeatedly for maybe 30 seconds. Didn't kill computers or anything else.

Thanks to all who replied, I'm hoping for more suggestions.
 
/ Gas Backup power didn't back us up! #13  
To clarify:
"Regulator froze up" Temp was about 30 degrees. Was windy, but only about 4 or 5 mph. If that was the culprit, why would both furnace & water heater come back on immediately when power came on and continue with no problems? No delay, both started working right away as soon as power came on.

We had lights on & wife cooked dinner on the microwave.

Gas is propane, tank was 55% full.

Cable runs from generator to transfer switch.

Generator is gasoline fueled, rated at 7000 watts. Runs well, freezer, furnace fan, microwave, some lights (LED's).

When power failed lights flashed repeatedly for maybe 30 seconds. Didn't kill computers or anything else.

Thanks to all who replied, I'm hoping for more suggestions.

Good info. That kills the theory that the generator is drawing too much propane for the furnace and water heater to work, because the generator doesn't draw any propane at all.

So that probably means it's an electrical issue. Continue troubleshooting from that point.

You also said that this setup has worked in the past, but didn't work this time. That would indicate something has changed electrically, or something has failed electrically.
 
/ Gas Backup power didn't back us up! #14  
I'm going to guess it has to do with your neutral. Generators either have a floating neutral, or a bonded neutral. That is, on the generator outlet, a bonded neutral will be connected to the ground terminal on the outlet. On a floating neutral, it is not. I don't understand the implications or why behind it. I've heard gas furnaces not functioning properly with a floating neutral, and the solution is to make an adapter that bonds the neutral and ground. Some googling may be in order and should help you decide if that is your issue.
 
/ Gas Backup power didn't back us up! #15  
I'll be interested to see if this mystery is solved. Our gas hot water heater doesn't even have an electrical connection.

If the OP's is that way, it seems like something is somehow shutting off the gas supply?
 
/ Gas Backup power didn't back us up! #16  
One word..... Murphy. Why would it work when you really needed it? Sounds like lack of fuel from the limited information, yeah, like the regulator.
 
/ Gas Backup power didn't back us up!
  • Thread Starter
#17  
One word..... Murphy. Why would it work when you really needed it? Sounds like lack of fuel from the limited information, yeah, like the regulator.

What seemed a crackpot answer may be the right answer, the regulator!

Looking online about regulators freezing up it seems that regulators do freeze up. I don't understand the dynamics as the explanation wasn't clear to my 76 year old brain, but if the answer truly is a frozen regulator it seems it is related to gas pressures and evaporative cooling. Anyway a frozen regulator might explain why both systems came back on at the roughly same time the power was restored, if, for example, the furnace started drawing juice allowing the regulator to defrost and the water heater to fire up. I dunno. Maybe someone who knows this stuff can offer a better explanation.

I love TBN!
 
/ Gas Backup power didn't back us up! #18  
Most furnaces and gas water heaters have an ignitor, not a pilot light any more so hence the need for electricity to light them up.
 
/ Gas Backup power didn't back us up! #19  
I'm going to guess it has to do with your neutral. Generators either have a floating neutral, or a bonded neutral. That is, on the generator outlet, a bonded neutral will be connected to the ground terminal on the outlet. On a floating neutral, it is not. I don't understand the implications or why behind it. I've heard gas furnaces not functioning properly with a floating neutral, and the solution is to make an adapter that bonds the neutral and ground. Some googling may be in order and should help you decide if that is your issue.

Regarding generators and neutrals: It comes down to the transfer switch (if you even have one). This determines if the neutral and ground need to be bonded at the genny.
Neutral & ground should only be bonded at one location. This is typically in your main panel. This typically doesn't change when the genny supplies the panel.
I guess 99% of most residential transfer switches do not have a switched neutral, thus the ground and neutral should not be bonded (connected at the genny) or at any adapters or connections between the genny and your electrical panel. Genny connections that don't use a transfer switch, but use a back-feed circuit should also not have their ground and neutral bonded at the genny.

Even if N & G are incorrectly bonded at genny, not sure why furnace and water heater didn't fire. Maybe as JackMurdock noted, ignition controls are sensitive?
Otherwise, did you have all the normal circuits you usually have? (i.e. Or did you only have 1/2 of your normal 120V (i.e. a single leg)? Did you have any 240V loads operate correctly?
 
/ Gas Backup power didn't back us up! #20  
Anyway a frozen regulator might explain why both systems came back on at the roughly same time the power was restored,
if, for example, the furnace started drawing juice allowing the regulator to defrost and the water heater to fire up.

The regulator should be located in an outdoor location,,
sometimes when they "freeze" the regulator will simply continuously vent propane gas to the atmosphere,,,
 

Marketplace Items

2021 UTILITY VS2DX 53x102 T/A DRY VAN TRAILER (A59912)
2021 UTILITY VS2DX...
2009 International 4300 Bucket Truck 55' (A62613)
2009 International...
2017 CAT TL1055 (A60462)
2017 CAT TL1055...
We do NOT accept credit cards as payment. (A64119)
We do NOT accept...
2019 Toro Groundsmaster 7200 72in. Zero Turn Commercial Mower (A61572)
2019 Toro...
2017 Ford Escape 4WD SUV (A61574)
2017 Ford Escape...
 
Top