Randy, Even if that Frost Free Hydrant was plumbed with a Metallic pipe/tubing, it's wrong... I really don't even want to think about the electric work in your house.. I don't understand your complete dis-regard for Code... To make it simple, Code is the Minimum/Cheapest way it can be done to protect Lives(loved ones & pets too), Structures and Personal Property..the cable is 10/2 and the suggestion to install a sub-panel in the greenhouse seems to be the easiest solution. do you guys think the frost free hydrant i have in the greenhouse would be a suitable ground?
i did all the wiring in my house so i have electrical work experience. how would i use a disconnect box to do this that is different than using a sub-panel? is it wired the same way but the equipment is cheaper?
Take the Good Advice and run a new circuit from the Panel or up the wire & breaker size and set a sub panel in the greenhouse... Keep in mind that you also got some very Bad Advice.. Just because your heater may only draw 23 amps, doesn't mean that you have 7 amps to use...
btw, Use GFI receptacle/s or GFI breaker/s for receptacles in your Greenhouse...
Over 30 years of experience as a Master Electrician...