I have a chance to get some concrete that is 1 foot square, with 4 pieces of 5/8 rebar in it. It would span 7 feet over a drive way to let water under. Any idea what those concrete pieces would carry in weight. There would be 9 of them but the tires would ride on just two of them.
 
/ Concrete strength #2  
How does a 'one foot square' hunk of concrete span 7 feet ?
 
/ Concrete strength #5  
Placement of the rebar will be required to determine strength. Concrete strength is also required as well as maximum aggregate size.
 
/ Concrete strength #6  
Is there any rebar installed transverse in the beam
Unless the concrete Is homemade the strength should be 3000 PSI minimum
Aggregate size does not factor in beam strength
 
/ Concrete strength #7  
Maybe Egon was thinking of rocks being added as fill?? Aggregate size is standardized and should be appropriate for the PSI listed on the bag. We added plastic fiber to bridge abutments we poured.
 
/ Concrete strength #8  
You could recess 3 on each side and pour a 4 inch cement cap to spread the weight over several "beams" . Or something like weight distribution over multiples.
 
/ Concrete strength #9  
It would depend on what the concrete pillars were designed for...horizontal vs vertical load bearing, what is the source of the concrete?
 
/ Concrete strength #10  
I have a chance to get some concrete that is 1 foot square, with 4 pieces of 5/8 rebar in it. It would span 7 feet over a drive way to let water under. Any idea what those concrete pieces would carry in weight. There would be 9 of them but the tires would ride on just two of them.

No enough information provided to make a determination.
 
/ Concrete strength #11  
I would not use it for a beam without a lot more info. See picture of a concrete beam.
 

Attachments

  • concrete beam.jpeg
    concrete beam.jpeg
    93.4 KB · Views: 187
/ Concrete strength #12  
I have a chance to get some concrete that is 1 foot square, with 4 pieces of 5/8 rebar in it. It would span 7 feet over a drive way to let water under. Any idea what those concrete pieces would carry in weight. There would be 9 of them but the tires would ride on just two of them.

NOPE, 4 pieces of longitudinal rebar do not a beam make. There needs to be stirrups to prevent shear cracks from causing a beam failure.
 
/ Concrete strength #16  
Concrete has very poor tensile strength and it's only the rebar that allow such tensile loads, so don't even think of the rebar just strengthening the concrete in this application. It IS the strength. If that was designed as a column, the loading was engineered very differently.
 
/ Concrete strength #17  
Actually if it is actually only a 7' span put them down with some planks on top and you could drive anything over it.
 
/ Concrete strength #18  
Does op know if they have stirrups or just the longitudinal rebar? Who made the columns? What was intended purpose?
 
/ Concrete strength #20  
Concrete has very poor tensile strength and it's only the rebar that allow such tensile loads, so don't even think of the rebar just strengthening the concrete in this application. It IS the strength. If that was designed as a column, the loading was engineered very differently.

Concrete will fail in tension when loaded.
Columns are designed as beam/ columns usually. A combination of compression and bending loads
 

Marketplace Items

2020 ASV RT65 (A60462)
2020 ASV RT65 (A60462)
2023 CATERPILLAR 926M WHEEL LOADER (A62129)
2023 CATERPILLAR...
2022 John Deere 1025R (A53317)
2022 John Deere...
2016 Ford E-450 Passenger Bus (A61568)
2016 Ford E-450...
2021 JOHN DEERE 6145R TRACTOR (A59823)
2021 JOHN DEERE...
2003 Dodge Ram 4x4 Ext. Cab Pickup Truck (A59230)
2003 Dodge Ram 4x4...
 
Top