Is there EVER a situation where it is legal to run a 10 gauge wire into a 60 amp breaker?
I am not a NEC guru, but intuition would tell me that the answer is ,,,NO!
But, I am guessing, please help!
My heat pump air handler has two breakers on the front panel, they are rated 60 amps (both 220 volt single phase)
The installer wired from the electrical service with 10-2 wire to one of the 60 amp breakers.
(He did use larger wire to the other breaker, I could not find the wire size on that wire.)
Now, maybe, the incoming panel may have a lower rated breaker, which will protect the 10 gauge wire,,
but, if the breaker on the air handler is meaningless, I would assume there would be a disconnect, not a breaker.
The old air handler had fuses, so it had protection, I assume the manufacturer wanted the breakers on the air handler to provide protection?
So, is the 10 gauge wire, in this case, acceptable, or does the installer need to come back, and increase the wire to some size that is rated for 60 amps?
Thank you,,
I am not a NEC guru, but intuition would tell me that the answer is ,,,NO!
But, I am guessing, please help!
My heat pump air handler has two breakers on the front panel, they are rated 60 amps (both 220 volt single phase)
The installer wired from the electrical service with 10-2 wire to one of the 60 amp breakers.
(He did use larger wire to the other breaker, I could not find the wire size on that wire.)
Now, maybe, the incoming panel may have a lower rated breaker, which will protect the 10 gauge wire,,
but, if the breaker on the air handler is meaningless, I would assume there would be a disconnect, not a breaker.
The old air handler had fuses, so it had protection, I assume the manufacturer wanted the breakers on the air handler to provide protection?
So, is the 10 gauge wire, in this case, acceptable, or does the installer need to come back, and increase the wire to some size that is rated for 60 amps?
Thank you,,