I know there has been a long thread on this a few years ago, but I still have some confusion. I have a 5hp 240V single phase Franklin submersible well pump with a starter box. It is wird to a 30 amp breaker in my panel. I am trying to determine the minimum size generator to safely run this during outages. I emailed Franklin, and here was their response:
The 5 HP Franklin Electric motor that powers your pump, and I am assuming it is single phase draws 27.5 full load amps and requires a 60 amp breaker or if you have a dual element fuse it should be rated at 30 amps. A consideration when sizing a generator is that upon start up, for less than a second of time, the motor has a locked rotor amp draw of 121.0 that will trip some generators overload.
Here is a picture of the starter box: https://www.dropbox.com/s/tcj22kztihnc29r/WellStarter.JPG
Here is a link to a Franklin guide; page 5 references generator sizing: https://www.dropbox.com/s/9o4dsbzou5hrilc/FranklinSubmersibleMotorGuide2010.pdf
The suggested generator info in the brochure seems way more than the other information would imply. Any help would be appreciated.
The 5 HP Franklin Electric motor that powers your pump, and I am assuming it is single phase draws 27.5 full load amps and requires a 60 amp breaker or if you have a dual element fuse it should be rated at 30 amps. A consideration when sizing a generator is that upon start up, for less than a second of time, the motor has a locked rotor amp draw of 121.0 that will trip some generators overload.
Here is a picture of the starter box: https://www.dropbox.com/s/tcj22kztihnc29r/WellStarter.JPG
Here is a link to a Franklin guide; page 5 references generator sizing: https://www.dropbox.com/s/9o4dsbzou5hrilc/FranklinSubmersibleMotorGuide2010.pdf
The suggested generator info in the brochure seems way more than the other information would imply. Any help would be appreciated.