NEC: 30" of clearance for electrical subpanel?

   / NEC: 30" of clearance for electrical subpanel? #1  

5030tinkerer

Gold Member
Joined
Dec 27, 2005
Messages
457
Location
Iowa
Tractor
Kubota GL3830/GL5030
I am installing a 100 amp subpanel in my home inside a kitchen pantry (no, nothing will be front of it...). Trouble is, I noticed that code says that I need 30" of side to side working space along with 36" deep of space - the wall where I want to put the subpanel is only 28" long. I am not an artist (and you'll have to ignore the dots - they are placeholders to hopefully help everything line up), but the room looks like:

┌───────┐
│           │
│...........│(subpanel on other side of this wall)
└─ .......─┘

entry ↑

hallway ↓
─────────────────────────

The lower right hand wall stub sticks out about 12" from the wall where the subpanel would be placed. Given that a subpanel user would easily have the required 30" (more like 72") width if you took the hallway width into consideration, am I okay codewise?
 
   / NEC: 30" of clearance for electrical subpanel? #2  
That 30" includes the width of the panel so if the panel is 20" wide then you need 5" on either side. So if your wall is only 28" wide then I would say you would not be in compliance with the NEC.
 

Attachments

  • workingclearances.jpg
    workingclearances.jpg
    20.7 KB · Views: 1,294

Tractor & Equipment Auctions

Pair of New 700/40-225 Alliance Tires with Rims (A55301)
Pair of New...
TEREX RT665 MOBILE CABLE CRANE (A51406)
TEREX RT665 MOBILE...
2020 Westfield MKX 100-83 Auger with Swing Hopper (A55301)
2020 Westfield MKX...
2017 Big Tex 10ET T/A Flatbed Equipment Trailer (A50322)
2017 Big Tex 10ET...
2017 CHALLENGER MT465E TRACTOR (A51406)
2017 CHALLENGER...
Year: 2002 Make: Ford Model: Econoline Vehicle Type: Van Mileage: 156,145 Plate: Body Type: 3 Door (A51694)
Year: 2002 Make...
 
Top