Help with wireing

   / Help with wireing #1  

tile

Bronze Member
Joined
May 28, 2006
Messages
89
Location
Florida
Hi guys.

I need help on running some wire to get power out to my garden.

I have a breaker panel box thats's on the outside of our house in it has the main breaker for the house and the breaker for the well pump & a breaker for the lawn timer.

There are still about 6 spaces left for more breaker's to be installed.

I would like to come off this panel and run the power out to my garden for running two small water pumps ( on a timer ) and any power tools I may need when I work out there.

The garden is about 100' or less for the outdoor panel.

So what size wire would I need and what size breaker would I need.

Was looking and maybe doing like this kind of box in the garden.

# Includes 2 GFI Receptacles
# Two 20 Amp GFI
# 120 Volts
# UL Listed

Thanks for any help

Ron.
 

Attachments

  • 6a744e07-6968-4802-964c-aa0e7331f13c_300.jpg
    6a744e07-6968-4802-964c-aa0e7331f13c_300.jpg
    9.5 KB · Views: 136
   / Help with wireing #2  
Good choice on the GFI that is pretty much a code requirement any more. 10 guage wire would be my first choice for that long of a run. Use underground rated wire even if you put it in a pipe. When you lay the wire go plenty deep so that you don't hit it later on. Take a picture and make a map of where the wire is and how deep. If you sell the place or need someone to come in and do the work then they can use that as well. I used a 25 amp breaker on my breaker box to run my compressor. It ran pretty close to 20 amps and the start surge would trip the breaker at times. If you are using 20 amp receptacles out there then you might use 20 amp breakers. I am not an electrician and familiar with code. Just an electronic geek familiar with Transistors and tubes.
 
   / Help with wireing #3  
12/2 is good for 15 amps, if you going with 20 amps liek you said, it can overheat if you use it for extended periods of time. I go with 10/2 for for effiecent use of power and that long of run for power tools use.
 
   / Help with wireing
  • Thread Starter
#4  
Thanks for the info so far.

I will go with the 10/2 wire.

Also just to make sure I do not burn the house down
I am thinking the black wire gos into the breaker then the white wire to the neutral bus bar
and the ground wire to the ground bus bar.

Or can I put both white and ground to the ground bus bar.

And will 1" gray pvc be to small for the 10/2 wire to be ran into.


Thanks Ron.
 
   / Help with wireing #5  
Two additional questions come to mind--

1) are you supposed to put a disconnect box for this line on the exterior of your house and

2) is the outlet box supposed to be grounded into the earth with a separate ground line of its own?
 
   / Help with wireing
  • Thread Starter
#6  
Two additional questions come to mind--

1) are you supposed to put a disconnect box for this line on the exterior of your house and


I know when we did the pump for our water we had to have a disconnect box at the well.

Ron.
 
   / Help with wireing #7  
If this secondary outside breaker box was installed correctly it should have its own disconnect and dedicated ground rod. If this is the case then Ground and Nuetraul need to be connected to its specified termination possition within this panel.

Ground and Neutral don't start getting important on the location they are terminated until you start adding sub panels.
 
   / Help with wireing #8  
Your outside box would be a 'sub pannel' and the line to this box should be protected from the main pannel by a breaker which actually can serve as the 'disconnect' but, yes, you could add a disconnect switch.
My understanding is that any wire leaving the main pannel and not in a conduit needs to be breaker protected.
Black is power, white is neutral and green or bare wire is ground (like to earth).
Purpose of breakers is to be the weak link and blow/trip before wires melt and cause fire.
Charts will tell you what breaker to use for wire sizes.
Nowdays they bury wires with a caution tape buried slightly above the line so that a digger plucks the tape before hitting the wire thus indicating you are getting close.

Good lick with your project.
 
   / Help with wireing #9  
For that long of a run and since you're going to put it in conduit anyway, you might consider single-conductor 10ga THHN wire and 12ga bare for the ground. Might be a little less expensive than underground 10-2 WG.
 
   / Help with wireing #10  
tile,
I have been in this trade 30+ years. Here's what I'd do if it was my house. I'd use 1" PVC conduit because I want the option to pull it out if something ever happened. Then I'd use either 10/3 w/ground UF cable or 4 separate runs of #10 THWN (THWN is for a wet location) single strand wire. 2 blacks, 1 white and 1 green. The reason for the 2 circuits out there is you have 2 receptacles. Why run them on the same circuit? That's what you'd have if you ran 10/2. I'd run #10 because of the voltage drop issue if you want to run power tools. You said you did. I'd bury it 18-24" deep. Put it on 2 20Amp breakers or 1 2-pole 20Amp breaker. You said you'd be tying it into the breaker panel that has the main breaker for the house, so I'd assume that is the "Service Disconnect" for your electrical service. Connect the wires to the breakers as you mentioned. The white and ground might be able to go to the same buss depending on local codes. Both of them are connected together right there anyway. If you have 2 separate busses then use them appropriately. No disconnect or grounding electrode is needed at the garden power outlet if there is no structure there that has power in it. You can install one of you want, but I personally would not.
 

Tractor & Equipment Auctions

2015 New Holland Boomer 47 4WD Agricultural Utility Tractor (A53421)
2015 New Holland...
2025 IR IRE20 Mini Excavator (A52377)
2025 IR IRE20 Mini...
2015 Infiniti QX60 SUV (A50324)
2015 Infiniti QX60...
2017 Freightliner M2 106 TMA Attenuator Truck (A52377)
2017 Freightliner...
2018 KENWORTH T880 DAYCAB (A53843)
2018 KENWORTH T880...
2013 John Deere 650K Crawler Tractor Dozer (A53421)
2013 John Deere...
 
Top