Is a "earth ground" required for a portable generator? recently bought a generator and it shows one in the manual but I was told by dealer it isn't needed. Is that true?
 
   / Generator Question #2  
According to my electrician, you do not need to use the ground on the generator, as the "plug" from the generator to the house is grounded.

My generator also has a ground "screw" that I dutifully hooked up a ground wire to and stuck in the ground when I used it.

A few months ago, I had the electrician come out and move my generator hookup box and add more circuits to the box that the generator was feeding. He saw my ground wire that I had on the generator and said that it wasn't needed per the above explanation, so I ripped it off and won't use it.
 
   / Generator Question #3  
Grounds can present many tricky situations. Out here in the West where the ground is typically quite dry, a 8 foot rod driven into the ground may have enough resistance that it cannot ground out a 20 amp breaker. The preferred way is a ufer ground, a ground buried in the top 3" of the bottom of a concrete footing. It is typically a piece of 1/2" rebar 20 feet long. Your generator will be grounded when tied to the house ground. In some areas, adding another ground for equipment like a generator can actually create a problem when tied to the house ground. You can develop a differential voltage simply because one ground will be of less resistance then the other. It's one of those areas I am certainly not to sure of as its difficult in real life to ever have this scenario occur and evaluate it. Suffice it to say, if you have a 120V/240V generator, you will need a 4 prong male/female plug/receptacle to adequately transfer power and ground the generator.
 
   / Generator Question #4  
Rat, sorry to be off topic but I cant help but enjoying a good laugh at the "no Vote State". My generator has a spot for a extra ground as well. I had the transfer switches installed by the main breaker box in the basement and the plug in the garage. I can set the generator just outside but under the eaves and plug in. The electrician didn't say any thing about a extra ground so I have never used one. Dave
 
   / Generator Question #5  
I forgot to mention the fact that my generator connects to the house via a 30 amp plug, which is why the electrician said that I did not need the generator's ground.
 
   / Generator Question #6  
When hooked up to your house for emergency power there is no need for a supplemental ground as others have pointed out. But if you are using the generator in a remote location to provide stand alone power for lights, tools, etc. then it would be a good idea to use the ground wire. I bought a copper ground rod and a short length of heavy wire for this purpose.

JackIL
 
   / Generator Question #7  
This is probably outside the usage of most generators. But I have used generators for powering sensitive electronics, with multiple sensors. I had the strangest noise problems that I couldn't track down until we properly grounded all equipment, including generator. Noise problem went away. But for running a drill or saw the ground is probably not needed.
 
   / Generator Question #8  
Ground rods (grounding electrodes) are only required if the generator is a "separately derived system". (For the complete text of sections cited please see the 2002 NEC)

What is a Separately Derived System?

The NEC in Article 100 defines a Separately Derived System as:

A premises wiring system whose power is derived from a battery, from a solar photovoltaic system, or from a generator, transformer, or converter windings, and that has no direct electrical connection , including a solidly connected grounded circuit conductor, to supply conductors originating in another system.

The key to knowing if a generator is a "Separately Derived System" is not the generator, but rather the transfer switch. If the transfer switch does not transfer the neutral (grounded conductor), then the generator has a “solidly connected” grounded circuit conductor and the generator is not a separately derived system.

Bottom line, if connecting to your existing panel thru a transfer switch (that does not transfer the neutral), no ground rod is needed. If generator is sole power source (i.e. job site construction), ground rod is needed.

Here a link for further info --> Generator grounding
 
   / Generator Question #9  
The grounding lug, on the most of the gensets that they are concerned with, have no connection to the neutral. It's just simply a lug on the case. I have purchased, but not yet installed,a 12KW generator. It has an external lug and WILL get a connection to a grounding electrode, if for nothing more than to dissipate transient voltage, i.e. lightning. The NEC® does allow a "supplemental electrode". I'll feel better spending the $10 to install one.

Jerry
 
   / Generator Question #10  
Jerry - I certainly don't have your knowledge and experience, however I have installed a few of these previously and was familiar with the NEC code (about gensets from previous research). BTW - I've seen gensets internally wired both ways - with neutral grounded to the chassis and not. I agree an extra ground wouldn't hurt.
 

Tractor & Equipment Auctions

2010 Ford Edge SE SUV (A51694)
2010 Ford Edge SE...
ATLAS XAS110 COMPRESSOR (A52472)
ATLAS XAS110...
2010 Chevrolet Tahoe SUV (A52377)
2010 Chevrolet...
SKID STEER FORKS (A53843)
SKID STEER FORKS...
Echo SRM2620 Gas Trimmer (A52377)
Echo SRM2620 Gas...
2012 INTERNATIONAL DURASTAR 26FT NON CDL BOX TRUCK (A54313)
2012 INTERNATIONAL...
 
Top